Jump to content

What Size Main Circuit Breaker For 10Mm Incoming Supply Cables?


GavinK

Recommended Posts

10mm cables supply the distribution board. The board has 8 circuits : 2x32A and 6x16A breakers which are sized correctly. Should the main incoming breaker on the board (and the RCD) be rated 63A or 45A ? Thanks for any help..

Link to comment
Share on other sites

Electau's ratings are at the conservative (safe) end, Bangkok Cables 10mm THW which is commonly used as the overhead feed from meter to house is rated at 70A in air although at an actual 70A it's getting pretty warm.

Things to consider are the actual rating of your meter (15/45?) and the length of the run, as over 50m or so volt drop becomes more important than the actual rating of your cable.

Most of the places I've looked at that have a 15/45 meter have 10mm THW and a 63A incomer.

Link to comment
Share on other sites

15/40 meter. The 10mm cables run from the first board to a second board. The run is c 20 metres. The 1st board is supplied from the meter on 16mm cable. The 10mm cables do not pass through the 1st board - they are spurred off the 16mm cables. Hope this is clear... Its the main breaker on the 2nd board I want to check the size of. Thanks.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.










×
×
  • Create New...