  1. Quick update.. Contractors sending a bloke to fix  performance readout next Friday. The Issan Luv Machine told them I wanted my money back and that they had to come and collect the solar panels.!! True Story.. My approach was different which was I was getting Fizzed off and they will be talking to my Solicitor if not fixed before Songran... Apparently the fix it man is the best in the country and can even make it work of a night time..!!! I wont bother with figures but I am bouncing below the meter read slowly over a few days only to lose it with a cloudy day... Like walking up the stairs and catching the lift back down. Will update as it develops.

    • Haha 1
  2. 8 hours ago, Crossy said:

    I would send the photos to your Contractor backed up with a call from your good lady.

     

    Done already a week ago.. Some things so frustrating to get done here!!! I have been told they will repair. Talks cheap and easy.. I want a time frame from them to complete my warranty issue. That is my next step. Starting to get fissed of with no feedback from installers with where they are up to to rectify my issue. Even if they say 1 month to fix I can live with that. Just want to know what's going on.

     

    8 hours ago, maxpower said:

    the current transformer must have the phase cable passing through the coil and the coil connections arranged to the meter manufacturers diagram. 

     

    I understand what you are saying but my very limited Sparky knowledge of coil connections etc do not comprehend to me. I will have to put my faith in the installers on that one.  

  3. Crossy you detective you. I did not know where the CT reader was connected. Now I can see from my previous photo's. Yes correct installation with arrow showing direction of flow as you say. The blue and white wires coming from the CT are however connected the wrong way around into the Smart reader as you can see in the line diagram and the Photo of Smart Reader. I am so tempted to swap them around and see what happens. 

    6 hours ago, Crossy said:

    Which connections were wrong? The voltage (terminals 3 & 4)

     

    These are the connections I am talking about (5 & 6) in line diagram below.

     

    On 2/24/2021 at 9:36 PM, Thaifish said:

    20210218_124219.jpg

     

     

     

    13 hours ago, Thaifish said:

     

    20210312_090359.jpg

    20210312_080855.jpg

     

  4. Meter read day.. The sad news was that the meter read 54Kwh in the black. So a Bin of 219bht for the month. I was so hoping it would be in the red to see what response/readout would be from PEA. Without accurate performance data (read below) I am guessing my bin for the month would have conservatively been around 4,000bht or around 952kwh consumed.  My Issan Luv Machine spoke with the Meter Reader and from what I heard he was happy the Bin was low for us and said Solar very expensive. We had 2 blackouts from grid power maybe 8hours total. Nothing unusual + a few days where the inverters shut down from over voltage from the grid. Only brief shutdowns maybe 2 hours. I have found that I can maybe change the protection (Over/Under Voltage) settings on the Android phone App that accesses the Inverters. I do not wish to play with these settings however because 1 I do not know what I am doing and 2nd warranty.... Especially at this early stage of installation. 

     

    I have no idea of Solar performance over the month as mentioned in my previous comments. It has been 3 weeks since Installers were notified of the readout issue. The latest is that they know there is a problem and that they are going to send someone up to replace or repair soon (Smart Reader). I'm running low on Jai Yen Yen tablets and have been thumping the drum fellang way with an increasing loudness to hurry up... I found the wiring on the smart meter to be the wrong way around (pictures below) and I am wondering if they have also installed the AMP/Volt clamp the wrong way around also.

     

    I don't doubt the actual installation is performing optimally. The inverters are hot and blinking the correct lights. My Multimeter readings  showing feed back into the grid has been around 22Amp midday with 2 Air conns running on top etc. Of a night time we have been consuming around 25/30Kwh but during the days we have only averaged 15/20Kwh excess back into the meter.

     

    We have had mainly sunny days although Smokey with high cloud coverage. The PV panels are also showing the dirt buildup. They got a wash with rain 2 weeks ago which cleaned them fairly good but I can see now that cleaning is going to be a regular thing.

    20210312_090359.jpg

    20210312_080855.jpg

    • Like 1
  5. 5 hours ago, Crossy said:

    @Thaifish how's it all going?

    Any news on what your graphs actually mean asuming they're correct of course?

    I'm hanging in there trying to to fix my Solar performance readout issue the Thai way. I have learnt beating the drum the fellang way does not work here. There is a definite issue with the readouts which the contractors acknowledge. After two weeks of my Issan Luv Machine sending happy  photos of me pointing at the broken thingy by Line App I am now able to correspond by e-mail. Going by responses the English is not good but they understand the software issue and are in contact with Huawei. Painfully slow but again trying to resolve this the Thai way...  My hand readouts from the Grid Meter which I have kept a log of AM/1200hrs/PM shows that we have basically broken even consumption/production (nearly 4 weeks since installation now). We are only about 30Kwh under last months readout which I was hoping on being better!! From what I can see I believe the System is working to full strength even though I have no reliable data to back it up.

    The Meter reader should be here around the 18th so it will be interesting to see the print out. The Kwh reading should be in the negative so also interesting to see what or if any response comes from PEA about the reading. The Luv machine is not worried. I have made preparation's for a "GO FUND ME PAGE" .

    • Like 1
    • Haha 1
  6. 1 hour ago, Crossy said:

    Just to confuse you 3 wires on big insulators is 3-phase at 25kV or so (it's a delta connection so no neutral)

     

    I think I need to go to 101school learning phases. I will stick to just counting the wires.

     

     Does it have 4 low voltage wires (smaller insulators)? No cannot see.

     

    1 hour ago, Crossy said:

    Definitely time to talk to your contractor

    Phone call and Email sent to contractor this morning. Pointed out my performance readout issues and attached the photos below to compare. The second image readout is over a 24hr period and shows what I would expect to see. I mentioned that I think it is the Chinese Power Sensor unit not giving correct values and that they should install a Huawei Sensor.

    Solar power graph outage 270221.png

    Proper Display Solar readout.png

    • Like 1
  7. 5 hours ago, Crossy said:

    Is that a 3.3km run at 220V or do you have a more local transformer? Such a long run will have a significant resistance which would lead to a large volt-drop on load and a significant volt-rise on export.

    There is a transformer about 300mt up the road with 2 phases coming in (3 wires total...(hope I got my phases correct this time!!) coming in). The supply then branches out to the tapioca and vegetable plantations with about 6km of wiring. Only supplying power to water pumps and the odd light after our Bahn supply.

  8. Before I call it a night I found this Q and A link about Huawei Smart Meters... It shows that Chinese settings for positive are recorded as negative and vise verser. Looking at my read outs it helps me comprehend mush much about chinese method

     

    Link to Q and A.....

     

    Case-Smart Meter Types(Other) Connected to SmartLogger Instance - Huawei Enterprise Support Community

    Smart meter readout.png

  9. So todays production was 23Kwh back into grid as read by PEA meter with solar protection drop outs due to High Voltage from PEA. Solar kept starting up and then would soon drop back out with over voltage again for about 1 hour.

    Graph below showing interruptions ...

     

    Tomorrow its time to phone Contractors with concerns... I will wait until the Issan Luv Machine has her 3rd coffee before we call.. I think it is a full moon tonight... Not a good start...?

    Graph interuptions high voltage 280221.png

    • Haha 1
  10. 5 hours ago, eisfeld said:

    The inverter might have a setting as to the voltage where it will shut off. Those are country specific and if the installer didn't set it to the values for Thailand it might prematurely cut off.

    Another day and had afternoon shut downs due to High Voltage from grid. Last time it was low Voltage. I was never aware how much the Grid voltage changes until now. I saw it it peak at 229Volt before solar shut down on protection mode. I have seen it around 210V at an opposite side of scale. The Bahn is 3.3km  from village up a dirt road mostly... Have had the power drop out 3 times last two months for about 3 to 4hrs each time. Only one drop out effected the village supply. I can usually go and find the breaker which has tripped on our road...    

    • Like 1
  11. 17 minutes ago, Crossy said:

    I'm a bit confused by your Schneider distribution box as that's a 3-phase incoming breaker and it's difficult to see if there's a single-phasing kit installed (it hides on the switched side of the breaker). Need to look at that more closely.

    They did rewire the 2 phases back into 1 phase between the 3 phase breaker and house fuse box. They had to go into town for heavier cabling and joiners and I watched them join connections.

  12. 2 hours ago, Crossy said:

     

    Any indication just how low the supply went?

    No idea! I was only aware of brown out when I checked the alarm records. House appliances where not effected. There are only two grid wires running past Bahn..  Live and Neutral.. The two phases we have 2 Live 2 Neutral coming to Bahn are feeding of them so cant change setup... Blackouts/brown outs not uncommon here.  

  13. 9 hours ago, Crossy said:

    You shouldn't be able to change anything on the DDSU unit other than the RS-485 address. I wouldn't mess with it.

     

    I included the English manual with my earlier post but it probably isn't really going to help.

    Do you think it might be what is causing the incorrect values being displayed on my readouts.. I'm going to hit the installers up Monday with the erroneous readouts.. Thankfully my Issan Luv machine can see the errors also.. I am wondering if because they did not install an original Huawei power sensor the software is not recognizing the DDSU666-H Smart meter they installed.???? I have spotted your link on the Solar carport thread  with the readouts and I am envious with the info you see. Hope you do not mind have copied here below your link...

     

     

    "Local Energy Consumption" plot to ThingSpeak channel https://thingspeak.com/channels/991448

  14. 1 hour ago, Crossy said:
    1 hour ago, Crossy said:

    The DDSU666-H is the "Smart Power Sensor" which interfaces the current transformer hanging off your incoming supply in the Schneider box and your inverters. It's this that's generating your usage/export/import data.

     

    One assumes that the manuals for all your devices are in a pile of documentation somewhere.

    data:image/gif;base64,R0lGODlhAQABAPABAP///wAAACH5BAEKAAAALAAAAAABAAEAAAICRAEAOw==

     

     

    Ok got it. The one fitted is a Chinese model not a Huawei brand. Chinglish manual included. If the sensor is generating the data then maybe this is what is causing the unusual production/consumption readouts? It looks like you can change the values if I am reading it correctly?? Is that possible?? If so then I will get onto the installers to fix..

     

  15. There is a smart meter wired in as earlier questioned. In the schematics of wiring I think there are 2 but I watched the installers remove 1 during initial start up. There is a scrolling readout with active energy IMP/EXP and Active Power which I do not comprehend??? Not sure which side of power input it is coming from....ie PV or Grid?? The other readouts are basic Amp, Watt, Freq to me which I understand

    Smart meter Solar.jpg

×
×