A 9,000 BTU A/C will draw around 900 Watts (about 4 Amps) when the compressor is running.

 

No problem load wise adding it to a lightly loaded outlet circuit if it's wired in 2.5mm2, put a plug on it and you're good to go.

 

You shouldn't have a breaker over 20A on 2.5 so it would be wise to swap that 25A out.

 

If it's practical I would still run a dedicated circuit but it's not essential.

  • Like 1
Link to comment
Share on other sites

On 9/9/2018 at 11:05 PM, Crossy said:

A 9,000 BTU A/C will draw around 900 Watts (about 4 Amps) when the compressor is running.

 

No problem load wise adding it to a lightly loaded outlet circuit if it's wired in 2.5mm2, put a plug on it and you're good to go.

 

You shouldn't have a breaker over 20A on 2.5 so it would be wise to swap that 25A out.

 

If it's practical I would still run a dedicated circuit but it's not essential.

HI, Thanks for that. I have the option of a dedicated circuit but its 4mm on 25 or 32 amp breaker, but I wanted to try and use this for electrical heater 6KW (multi) elsewhere. So if I can just come of the dedicated fridge circuit with no ill affects and I just have to swap out the breaker, I would prefer this.

 

On a side note, I noticed that the other Ac unit I have, 15k btu, has live + neutral to the consumer, but no earth. Ive managed to change everything else but this I have not as I have to remodel this room and will be getting it taken down shortly. When I go to put it back where should the earth go? is there a point on the inside unit? I did get a static or electrical shock from the compressor when it was on, so should i just earth this with a ground stake into the earth outside also?

 

Thank you again for your help

 

Regards

Link to comment
Share on other sites

You could swap the breaker but it's not necessary.  Over-current will not be an issue as you described and either will trip on short circuit immediately.

 

The AC installers I have had just ignore the ground or drill a hole in the concrete and jam the ground wire in.  It's probably nothing to worry about but if you do run a ground there should be an identified ground screw on the chassis somewhere.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.









×
×
  • Create New...