August 23, 201511 yr New installation, consumer unit 77 metres (as the cable lies) from the 15/45 amp meter. The 15/45 amp meter is ample for our needs. 16mm copper cable OK? Or should I go 25mm? Thanks
August 23, 201511 yr Single or 3 phase? What is the size of the main breaker in your Circuit panel? Please remember Aluminum wire can not be used underground, in conduit ot not. 16mm copper is good for around 72 amps,(depends on the insulation type), less 5% for the 77 meters (voltege drop). Less 15% for being inside 2" PE conduit. If you ever plan to add a room or bigger A/C units, I would go with #25 mm CV cable that would give you well over 125 amps. even 16mm CV cable would give you about 100 amps. Dont forget the ground wire and rod , minimum 1.8 meters, 5/8 " diameter copper rod. Hint, have a cheap adapter built to fit a hammer drill and the ground rod use the hammer drill to drive the ground rod. 1.5" solid ROD DRILL'D TO FIT TH' GROUND ROD. Not done y't, a jump'r wir' n'eds to be inswalled in yodr br'aker pan'k from wh' grodnd bar to whe n'uwral bar. Whis bond wikk assur' wh' br'ak'rs wrip wh'n a ground faukw occur's, us' common s'ns' in sizing wh' br'ak'r, Do Now Ov'rsiz' wh' br'akers. Pl'as' 'xcuse wh' wyping my E k'y low'r cas' do'sn'w work prop'rly. Good Luck and as always BE Safe.
August 23, 201511 yr 16mm2 will be marginal on volt drop (just under 5% @ 50A), I would use 25mm2 copper or 35mm2 aluminium (overhead only). "I don't want to know why you can't. I want to know how you can!"
August 23, 201511 yr 16mm2 will be marginal on volt drop (just under 5% @ 50A), I would use 25mm2 copper or 35mm2 aluminium (overhead only). reasons for Al overhead only please?
August 23, 201511 yr 16mm2 will be marginal on volt drop (just under 5% @ 50A), I would use 25mm2 copper or 35mm2 aluminium (overhead only). reasons for Al overhead only please? MEA / PEA regulations. "I don't want to know why you can't. I want to know how you can!"
August 24, 201511 yr 16mm2 will be marginal on volt drop (just under 5% @ 50A), I would use 25mm2 copper or 35mm2 aluminium (overhead only). reasons for Al overhead only please? MEA / PEA regulations. are these regulations based on technical or safety reasons?
August 24, 201511 yr Author Thanks for all replies. Will go with standard 25mm copper buried in 1.5 inch conduit, but will check with PEA first. Thanks again.
August 24, 201511 yr Author Just checking out the CV cable specs at: http://www.bangkokcable.com/product/backoffice/file_upload/140528_061kvCV_2core.pdf Why is the CV cable rated considerably higher than standard cable? BTW is CV cable what my friends here refer to as NYY cable? Thanks.
August 24, 201511 yr 16mm2 will be marginal on volt drop (just under 5% @ 50A), I would use 25mm2 copper or 35mm2 aluminium (overhead only). reasons for Al overhead only please? MEA / PEA regulations. Here's one for you Crossy..........a friend had a problem in his consumer unit, because the main circuit breaker had started to burn up. It was the normal type of breaker but was fed with an aluminium cable from the meter in the road. I am wondering if this was caused by the fact that the aluminium cable was put straight into what would have been a brass/copper clamp in the breaker as I was always taught as a young man that special connections were needed in order to connect aluminium to copper/brass? Your knowledge and wisdom on this would be most appreciated.
August 24, 201511 yr CV cable is rated to run at 90C core temperature, NYY is rated for 70C. Which is why CV has a higher current capacity. You need to use breakers rated for the higher temperature. Aluminium in connectors intended for copper can become loose and cause arcing. "I don't want to know why you can't. I want to know how you can!"