Are those METAL poles?  Are these poles the property owner put up to carry the incomer mains power lines to the house?

 

Are there any other metered homes nearby?  Do any of their poles (usually cement) have a wire (bare or encased) running from the top of every third pole down into the ground or to a metal strap that goes into the ground?

Posted
Are those METAL poles?  Are these poles the property owner put up to carry the incomer mains power lines to the house?
 
Are there any other metered homes nearby?  Do any of their poles (usually cement) have a wire (bare or encased) running from the top of every third pole down into the ground or to a metal strap that goes into the ground?


Metal poles installed by PEA.
Is this what your talking about ?
IMG_5909.JPGIMG_5910.JPG


Sent from my iPhone using Tapatalk
Posted
Amazing Thailand.
 
...and the second part of my question?


Concrete poles but it's midnight so can't look [emoji4]


Sent from my iPhone using Tapatalk
Posted
Amazing Thailand.
 
...and the second part of my question?


Is that not the tether your talking about ?
It's on the fourth pole?


Sent from my iPhone using Tapatalk
Posted

The 'wire' in your photo has no electrical connection, so is likely a repurposed electrical wire being used as guy-wire (to oppose the pull of the weight of the wires being carried at 90 degrees).  That the wire doesn't have a ceramic isolator is its own problem.

 

The MEN (Multiple Earthed Neutral) protocol used in Thailand will typically, on every third power pole, make a wired connection between the overhead NEUTRAL wire (seen commonly as a bare wire) and actual Earth Ground, via internal rebar or wire in the cement pole or running a wire or metal strap down the pole and directly into the ground.

 

Two major reasons for MEN implementation in Thailand are probably Lightning Protection and keeping the Neutral Float Current potential as close to the same as Earth potential for maximum safety.

 

The reason I posted about the steel metal poles is I don't believe PEA do MEN connections on poles used to long-carry electrical service to an individual house.

 

MEN implementation on the City or Village poles will look something like this:

 

MEN.jpg.97283a51693ad713c72836343cc9f0d5.jpg

 

* Images stolen from Internet. Blue highlights are mine.

 

 

You also might find these and other ThaiVisa Electrical Forum topic discussions on 'MEN' or Safe-T-Cut 'RCD' (Residual Current Device) of interest:

 

IMPORTANT INFORMATION for new electrical supplies. Building a home, read this!

Started by Crossy, March 28

 

How to make your Thai Electrical system safe
Started by Forkinhades, January 2, 2014

Posted

Ok getting info over load now pardon the pun.

So let me get this straight.

If we don't have MEN then that black wire stays out of the board?

If we do then it goes in ?

As it stands u guys don't see and RCB so we need to add one whether there is MEN or not?

It also needs a ground bar driven into the ground irrespective of what is installed ?

Am I right or way off ?

 

 

Sent from my iPhone using Tapatalk

 

Posted
Just now, irlguy1 said:

Ok getting info over load now pardon the pun.
So let me get this straight.
If we don't have MEN then that black wire stays out of the board?
If we do then it goes in ?
As it stands I guys don't see and RCB so we need to add one whether there is MEN or not?
It also needs a ground bar driven into the ground irrespective of what is installed ?
Am I right or way off ?

 

Pretty much spot on.

 

Electrical safety is nothing to be sneezed at, you can't see it but it is quite capable of killing you even after being just fine for many years.

Posted
 

Pretty much spot on.

 

Electrical safety is nothing to be sneezed at, you can't see it but it is quite capable of killing you even after being just fine for many years.

 

IMG_5971.thumb.JPG.e8c4d310bf97ee726c8303841162cf9b.JPGIMG_5970.thumb.JPG.6b6f5fa7e154dffaf49f311698f620ee.JPGIMG_5969.thumb.JPG.3bc2fa01252ecac8840e047c9600ede2.JPG

 

Tethers or MEN?

 

The ground bar was fitted yesterday I just saw it now.

 

 

 

Sent from my iPhone using Tapatalk

Posted

 

 

 

 

Typically, pole GUY or TETHER wires are *NOT* used as Electrical Ground devices.

Electrical Earth-Grounds and Lightning Grounds need to be as SHORT and STRAIGHT to ground as possible. 

 

 

The power pole image you posted is carrying -both- HIGH VOLTAGE Power Distribution Lines (3 wires at very top) feeding many transformers, and 230v~ MAINS ELECTRICAL Power Distribution Lines (4 wires at mid position) connecting a local Power Transformer (not pictured) to many metered homes in the area.

 

The 'bare' wire at the very top on this power pole is used as lightning protection.  

I can't see the wire connections on the 4 mid positions well enough to see if the top wire (typically the Neutral) is connected to a wire running to an Earth-Ground in support of MEN (Multiple Earthed Neutral). 

 

It would be easier to tell if MEN is implemented on the shorter concrete poles nearby (as seen in the background) as these carry only 230v~ MAINS ELECTRICAL. Finding an electrical connection from the Neutral Wire to the cement pole's internal metalwork or a strap running directly down to a earth ground strap would be more evident.

 

So look at the poles only carrying the 230v~ service wires and look for an bond connection from a bare Neutral Wire to Wires or metalwork sticking out the very top of the cement pole, or connected to a cable running down the pole and attached to a heavy metal strap at the bottom of the pole.

 

Anatomy of a power pole:

Power Pole

 

 

 

In this second image (stolen from another ThaiVisa forum post) you'll see a bare cable tying the Power Transformer NEUTRAL cable and going both UP to connect to the Neutral Power Distribution Line (not in pictured) and DOWN to be bonded to an earth ground strap very near where the pole goes into the ground (also not in picture).

 

post-249019-0-81615200-1463452456_thumb.

Posted

Various images of 4 poles out on main road near his house.
Can u decipher anything from this spaghetti junction?
IMG_5996.JPGIMG_5997.JPGIMG_5998.JPGIMG_5999.JPGIMG_6001.JPGIMG_6002.JPGIMG_6003.JPGIMG_6004.JPGIMG_6005.JPG

Is dad from a MAN area ? [emoji848][emoji13]


Sent from my iPhone using Tapatalk

Posted

Yes I can.....you're not listening to some very helpful and credible people who have given you advice. You've just taken chappy photos.
Advice: as one who started out like you, and who gained the displeasure of the electrical forum moderator......lift your game.
If you accept their advice, you need to do some internet research as well.

Sent from my SM-J700F using Tapatalk

Posted
Yes I can.....you're not listening to some very helpful and credible people who have given you advice. You've just taken chappy photos.
Advice: as one who started out like you, and who gained the displeasure of the electrical forum moderator......lift your game.
If you accept their advice, you need to do some internet research as well.

Sent from my SM-J700F using Tapatalk





No need to be rude. It's not like I can climb the pole and that's the best my camera gets.
It's on the back of their advice that I am out in 40 degree sun looking at poles so please less of the attitude.
To the ones that are being helpful I thank you sincerely.
I have done plenty of research and that's why I am asking in here because "research" in Thailand is as useful as a chocolate hammer. It varies from user to user and it seems in here at least people "the helpful ones" know what they are talking about.


Sent from my iPhone using Tapatalk
Posted

I'm not being rude, but talking straight as one who didn't have much of a clue before. 40 degree is nothing, come join me in the bottom of my swimming pool hole, in the Lao side of Isaan as I prepare for the walls to be poured.

'pussy' I say, but respectfully.

And by 'chocolate hammer' do you mean 'ti**s on a bore hog' ? [emoji41]

 

Sent from my SM-J700F using Thailand Forum - Thaivisa mobile app

 

 

 

 

 

 

Posted
13 hours ago, RichCor said:

 

post-249019-0-81615200-1463452456_thumb.

 

What you're looking for is something like the bare wire snaking down the pole in RichCor's post, it should go to a rod buried in the ground at the bottom.

 

If you see that, then try to see what's going on at the other end of it, it should be linking to the (usually bare) neutral.

 

@carlyai the ones I find useless are on nuns.

 

Posted
 
What you're looking for is something like the bare wire snaking down the pole in RichCor's post, it should go to a rod buried in the ground at the bottom.
 
If you see that, then try to see what's going on at the other end of it, it should be linking to the (usually bare) neutral.
 
[mention=207577]carlyai[/mention] the ones I find useless are on nuns.
 



Ah ok [emoji4]

Simple explanation thanks.
No
Not seen anything like that on any poles [emoji23]


Sent from my iPhone using Tapatalk
Posted

So, to sum up. No MAN so leave out the wire from my original comment.
Install rcbo or breaker

Change from 63 to 50 amp.

Rod is already buried so at least that's right.

Do I get a prize or am I still in the dog house?


Sent from my iPhone using Tapatalk

Posted
1 minute ago, irlguy1 said:

So, to sum up. No MAN so leave out the wire from my original comment.
Install rcbo or breaker

Change from 63 to 50 amp.

Rod is already buried so at least that's right.

Do I get a prize or am I still in the dog house?


Sent from my iPhone using Tapatalk

Dog house I'm afraid.  It's "MEN" not "MAN".  And don't forget to connect/clamp the biggest wire you have from the CU ground bar to the rod.

Posted
3 minutes ago, irlguy1 said:

So, to sum up. No MAN so leave out the wire from my original comment.
Install rcbo or breaker

Change from 63 to 50 amp.

Rod is already buried so at least that's right.

Do I get a prize or am I still in the dog house?

 

Yup, all OK :smile:

 

BUT.

 

If this is a new supply or meter upgrade you may need a PEA inspection. The inspector may want to see the link in place. If so put it in

Spoiler

, and when he's gone remove it again

.

 

 

Posted
Dog house I'm afraid.  It's "MEN" not "MAN".  And don't forget to connect/clamp the biggest wire you have from the CU ground bar to the rod.



Every 3rd pole would be men
I don't even have one so it's singular [emoji23][emoji23][emoji23]


Sent from my iPhone using Tapatalk
Posted

Having Electrical Poles with both Street Lamps and Dead Vines on them doesn't make it very easy to self-verify if MEN is being implemented  :-(

 

I'd suggest you have someone contact the local PEA/MEA directly and inquire.

 

While it may not seem important, it does change the way the CU / Breaker Box needs to be wired for maximum safety features to function properly.

 

 

Oh, so have you decided to ADD an additional RCD (Residual Current Device) ahead of the CU / Breaker Box,  or are you planning to replace the internal MAIN BREAKER with a combo MAIN BREAKER/RCD,  or put individual RCBO (Residual Current Breaker w/Overcurrent protection) on select circuits?

Posted
Having Electrical Poles with both Street Lamps and Dead Vines on them doesn't make it very easy to self-verify if MEN is being implemented  :-(
 
I'd suggest you have someone contact the local PEA/MEA directly and inquire.
 
While it may not seem important, it does change the way the CU / Breaker Box needs to be wired for maximum safety features to function properly.
 
 
Oh, so have you decided to ADD an additional RCD (Residual Current Device) ahead of the CU / Breaker Box,  or are you planning to replace the internal MAIN BREAKER with a combo MAIN BREAKER/RCD,  or put individual RCBO (Residual Current Breaker w/Overcurrent protection) on select circuits?


Adding an RCD [emoji106]
Gonna call PEA just to be sure.
Incidentally will they understand MEN or is it a different acronym in Thai ?


Sent from my iPhone using Tapatalk
Posted
6 hours ago, irlguy1 said:

Adding an RCD emoji106.png
Gonna call PEA just to be sure.
Incidentally will they understand MEN or is it a different acronym in Thai ?

 

 

You may need to call it "Multiple Earthed Neutral".

 

Posted

Ok if I may bother u guys again.

I have googled this and can't really find a proper answer.

 

A mate of mine is looking to build a home in Thailand and has just bought his plot and after everything was done he realised that the supply to the area is 3 phase. He says they don't have single phase and is freaking out as he is wondering how that effects his house build?

Can he just convert or what's the deal?

Thanks again guys

 

 

Sent from my iPhone using Tapatalk

 

Posted
8 minutes ago, irlguy1 said:

A mate of mine is looking to build a home in Thailand and has just bought his plot and after everything was done he realised that the supply to the area is 3 phase. He says they don't have single phase and us freaking out as he is wondering how that effects his house build?
Can he just convert or what's the deal?
Thanks again guys

 

Luckily (most of) Thailand is 3-phase, 4-wire (4 wires on the pole outside). No issue to treat it as three separate single-phase installations.

 

If he can get away with a 15/45 single-phase supply the PEA will happily give him just that, from one phase and neutral. This is exactly what everyone on single-phase supplies has.

 

EDIT Even if he's in one of the few areas that are 3-phase, 3-wire he can still have a single-phase supply no issue whatever. Is your friend perchance from the US where single and 3-phase supplies are very different?

 

EDIT-2 Or is he looking at the big 25kV poles with no 220V, if this is the case he may need a transformer, no issue (other than cost).

 

Suggest he talks to the supply authority in his area, he needs to anyway to get supply.

 

Posted
 
Luckily (most of) Thailand is 3-phase, 4-wire (4 wires on the pole outside). No issue to treat it as three separate single-phase installations.
 
If he can get away with a 15/45 single-phase supply the PEA will happily give him just that, from one phase and neutral. This is exactly what everyone on single-phase supplies has.
 
EDIT Even if he's in one of the few areas that are 3-phase, 3-wire he can still have a single-phase supply no issue whatever. Is your friend perchance from the US where single and 3-phase supplies are very different?
 
EDIT-2 Or is he looking at the big 25kV poles with no 220V, if this is the case he may need a transformer, no issue (other than cost).
 
Suggest he talks to the supply authority in his area, he needs to anyway to get supply.
 



Apparently the local villagers chipped in and bought a transformer further up but he doesn't want to buy one himself and have every bugger connecting to it as you know they will.

Any idea what a transformer would cost ?
Is it normal for them to stick in a big pole and expect the locals to be able to pay for the transformer?


Sent from my iPhone using Tapatalk

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.




×
×
  • Create New...