So i have 2 inverter each with Dc SPD And Ac SPD. My plan was to connect 2 Dc SPD And 2 Ac SPD To same dedicated ground pole just outside the wall( 3meters away). Any reasons to not?

 

Pink

Posted

I doubt there would be any issue using a common rod if the SPDs are close together physically.

 

Our DC and AC SPDs share the car port metalwork as a common grounding point. The car port does have a rod too, but the metalwork alone actually tests better than the rod! But the rod is required to be "to code".

  • Thanks 1
Posted
15 minutes ago, Crossy said:

I doubt there would be any issue using a common rod if the SPDs are close together physically.

 

Our DC and AC SPDs share the car port metalwork as a common grounding point. The car port does have a rod too, but the metalwork alone actually tests better than the rod! But the rod is required to be "to code".

Thanks Crossy.