I have a 180m overhead cable run and PEA recommend 95 mm. I would like touse 70 mm but am loathe to against their advice.

If you are going for a 30/100 meter then the 95mm2 is the cable to use, if you are going with a 15/45 then you could get away with 70mm2 but there'd be no spare capacity for a meter upgrade.

A better (cheaper) solution now you're going overhead would be to go for 120mm2 Aluminium, much cheaper and significantly less of a magnet for copper thieves.With a cable that size there is no way it will fit in the meter or consumer unit so your contractor will have to splice on a 25mm2 copper pigtail at each end (don't let him trim strands).

Run the idea of Al cable past PEA and see what they say.

Thanks Crossy.

Posted

First . What is your proposed max demand in amps? 100A, 45A etc.

1.5km is a very long run for a LV distribution spur line. Far more economical is to have the transformer as close as practical to your property boundry, or the PEA may permit it on your property and locate it as close as practicable to the proposed mainswitch board. this way you will have short route length for the LV consumers mains.

Dependant on your max demand you it may be advantageous to you from an economic perspective ( ie cost) to install a 3 phase 4 wire supply in lieu of a 2 wire single phase one.

Smaller conductors mean less cost per metre for your consumers mains.

On the downside you will have to pay for the capital cost of the HV line extension and transformer.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...