Earthing Second (Spurred) Consumer Unit

Featured Replies

I have 2 consumer units. 1st consumer unit is upstairs. From the Double Pole Switch there is a spur off the live and neutral running to supply a second CU downstairs. 1st CU appears to be earthed (although I can't find the earthing rod). 2nd CU has no earth spike. To earth this 2nd CU is it just a matter of running cable from the 2nd CU to a new earthing rod ? Should I use 4mm or 6mm cable ? Thanks.

You can add a rod to the second CU no problem. Ensure that all circuits are protected by an RCD since this is now a TT system.

Do NOT add a MEN (N-E) link to the second CU, if your original CU has a link between E and N then you would be better extending this MEN system to the second CU by running an earth between them.

Use 6mm cable to your rod.

"I don't want to know why you can't. I want to know how you can!"

  • Author

Thanks for the advice.

Both CU's have only Circuit Breakers. Can these CB's simply be swapped with an RCD in each CU or is it a matter of replacing both CU's with Split Service CU's ?

You need to replace the incoming breaker with an RCBO, that provides both over current and earth leakage protection.

A cheaper option if you have space is to simply add an RCD immediately after the incoming breaker in each board.

"I don't want to know why you can't. I want to know how you can!"

  • 2 months later...
  • Author

Crossy, you say to 'ensure that all circuits are protected by an RCDs' - do you really mean ALL circuits should be protected ? I'm wondering about nuisance tripping and whether it would be ok to set-up both CU's to be split-load CUs ? Thanks again.

You should at least protect any circuits with Class-1 fixed appliances (water heaters) and all outlets with RCDs.

Nothing to stop you using split load CUs with RCBOs on things like the freezer.

"I don't want to know why you can't. I want to know how you can!"

Appears is not good enough, visually check the main earth and connection first (and test). If this is OK you can run a 4 or 6 sqmm earthing conductor from the first switchboard to the next DB. This is connected to the earthbar. There must be no connection between the neutral and earth in the second DB if the MEN system is used, ie an N-E bond at the main switchboard.

If you are using the TT system you can run another main earth and electrode from the second DB if you wish but you should bond them together (equipotential bonding). Easier to run an earth between the two switchboards.

RCD protection. TT systems. All circuits.

RCD protection TN-C-S (MEN). All socket outlets, all lighting points. Permanently connected equipment on a risk assessment basis. All permanently connected equipment with exposed conductive material must be earthed.

  • Author

Appears is not good enough

Quite right. When I got to the end of the earth cable I discovered that someone had 'forgotten' to attach an earth rod, leaving the end of the cable just buried in the soil. That was quickly fixed.

There is no MEN link on either DB.

Running an earth conductor from the 1st DB to the 2nd would mean going through ceilings, walls and a concrete floor, something I'd like to avoid if possible, at least until the next round of decorating. Is there any safety benefit of doing this vs a TT system ?

The L&N connecting the DB's have been there for several years - unfortunately they forgot to earth either DB. So I'm trying to fix that. Both DB's can be RCD/RCBO protected - I'm prepared to replace both DB's to accommodate them. I should also mention that there are 2 showers each with their own earth rod. Attached diagram shows the current set-up. Other than the missing RCD protection, would there be any other concerns with this that I should consider ?

Thanks for all the help and advice.

CU.pdf

Appears is not good enough

Quite right. When I got to the end of the earth cable I discovered that someone had 'forgotten' to attach an earth rod, leaving the end of the cable just buried in the soil. That was quickly fixed.

There is no MEN link on either DB.

Running an earth conductor from the 1st DB to the 2nd would mean going through ceilings, walls and a concrete floor, something I'd like to avoid if possible, at least until the next round of decorating. Is there any safety benefit of doing this vs a TT system ?

The L&N connecting the DB's have been there for several years - unfortunately they forgot to earth either DB. So I'm trying to fix that. Both DB's can be RCD/RCBO protected - I'm prepared to replace both DB's to accommodate them. I should also mention that there are 2 showers each with their own earth rod. Attached diagram shows the current set-up. Other than the missing RCD protection, would there be any other concerns with this that I should consider ?

Thanks for all the help and advice.

coffee1.gif

Appears is not good enough

Quite right. When I got to the end of the earth cable I discovered that someone had 'forgotten' to attach an earth rod, leaving the end of the cable just buried in the soil. That was quickly fixed.

There is no MEN link on either DB.

Running an earth conductor from the 1st DB to the 2nd would mean going through ceilings, walls and a concrete floor, something I'd like to avoid if possible, at least until the next round of decorating. Is there any safety benefit of doing this vs a TT system ?

The L&N connecting the DB's have been there for several years - unfortunately they forgot to earth either DB. So I'm trying to fix that. Both DB's can be RCD/RCBO protected - I'm prepared to replace both DB's to accommodate them. I should also mention that there are 2 showers each with their own earth rod. Attached diagram shows the current set-up. Other than the missing RCD protection, would there be any other concerns with this that I should consider ?

Thanks for all the help and advice.

What I meant to say was interupted coffee1.gif

What I mean to say before was I thought is was 10mm cable from earth bar to rod and 4mm to equipment.?

  • Author

There's probably a typo in .pdf but it's not the cable size I'm asking about now (yes, 10mm to the rod).

If at all possible you should link your grounds together, either inside or at the rods.

This will reduce the possibility of shock between the two grounds during a fault and will also reduce the overall resistance to ground which can never be a bad thing.

"I don't want to know why you can't. I want to know how you can!"

  • 2 weeks later...

Wouldn't it be better to disconnect the independent earths of the showers and run them to the earth bar in the consumer unit ?

Create an account or sign in to comment

Recently Browsing 0

  • No registered users viewing this page.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.