Earthing Second (Spurred) Consumer Unit


Recommended Posts

Posted

I have 2 consumer units. 1st consumer unit is upstairs. From the Double Pole Switch there is a spur off the live and neutral running to supply a second CU downstairs. 1st CU appears to be earthed (although I can't find the earthing rod). 2nd CU has no earth spike. To earth this 2nd CU is it just a matter of running cable from the 2nd CU to a new earthing rod ? Should I use 4mm or 6mm cable ? Thanks.

Posted

You can add a rod to the second CU no problem. Ensure that all circuits are protected by an RCD since this is now a TT system.

Do NOT add a MEN (N-E) link to the second CU, if your original CU has a link between E and N then you would be better extending this MEN system to the second CU by running an earth between them.

Use 6mm cable to your rod.

Posted (edited)

Thanks for the advice.

Both CU's have only Circuit Breakers. Can these CB's simply be swapped with an RCD in each CU or is it a matter of replacing both CU's with Split Service CU's ?

Edited by regedit
Posted

You need to replace the incoming breaker with an RCBO, that provides both over current and earth leakage protection.

A cheaper option if you have space is to simply add an RCD immediately after the incoming breaker in each board.

  • 2 months later...
Posted

Crossy, you say to 'ensure that all circuits are protected by an RCDs' - do you really mean ALL circuits should be protected ? I'm wondering about nuisance tripping and whether it would be ok to set-up both CU's to be split-load CUs ? Thanks again.

Posted

You should at least protect any circuits with Class-1 fixed appliances (water heaters) and all outlets with RCDs.

Nothing to stop you using split load CUs with RCBOs on things like the freezer.

Posted

Appears is not good enough, visually check the main earth and connection first (and test). If this is OK you can run a 4 or 6 sqmm earthing conductor from the first switchboard to the next DB. This is connected to the earthbar. There must be no connection between the neutral and earth in the second DB if the MEN system is used, ie an N-E bond at the main switchboard.

If you are using the TT system you can run another main earth and electrode from the second DB if you wish but you should bond them together (equipotential bonding). Easier to run an earth between the two switchboards.

RCD protection. TT systems. All circuits.

RCD protection TN-C-S (MEN). All socket outlets, all lighting points. Permanently connected equipment on a risk assessment basis. All permanently connected equipment with exposed conductive material must be earthed.

Posted

Appears is not good enough

Quite right. When I got to the end of the earth cable I discovered that someone had 'forgotten' to attach an earth rod, leaving the end of the cable just buried in the soil. That was quickly fixed.

There is no MEN link on either DB.

Running an earth conductor from the 1st DB to the 2nd would mean going through ceilings, walls and a concrete floor, something I'd like to avoid if possible, at least until the next round of decorating. Is there any safety benefit of doing this vs a TT system ?

The L&N connecting the DB's have been there for several years - unfortunately they forgot to earth either DB. So I'm trying to fix that. Both DB's can be RCD/RCBO protected - I'm prepared to replace both DB's to accommodate them. I should also mention that there are 2 showers each with their own earth rod. Attached diagram shows the current set-up. Other than the missing RCD protection, would there be any other concerns with this that I should consider ?

Thanks for all the help and advice.

CU.pdf

Posted

Appears is not good enough

Quite right. When I got to the end of the earth cable I discovered that someone had 'forgotten' to attach an earth rod, leaving the end of the cable just buried in the soil. That was quickly fixed.

There is no MEN link on either DB.

Running an earth conductor from the 1st DB to the 2nd would mean going through ceilings, walls and a concrete floor, something I'd like to avoid if possible, at least until the next round of decorating. Is there any safety benefit of doing this vs a TT system ?

The L&N connecting the DB's have been there for several years - unfortunately they forgot to earth either DB. So I'm trying to fix that. Both DB's can be RCD/RCBO protected - I'm prepared to replace both DB's to accommodate them. I should also mention that there are 2 showers each with their own earth rod. Attached diagram shows the current set-up. Other than the missing RCD protection, would there be any other concerns with this that I should consider ?

Thanks for all the help and advice.

coffee1.gif

Posted

Appears is not good enough

Quite right. When I got to the end of the earth cable I discovered that someone had 'forgotten' to attach an earth rod, leaving the end of the cable just buried in the soil. That was quickly fixed.

There is no MEN link on either DB.

Running an earth conductor from the 1st DB to the 2nd would mean going through ceilings, walls and a concrete floor, something I'd like to avoid if possible, at least until the next round of decorating. Is there any safety benefit of doing this vs a TT system ?

The L&N connecting the DB's have been there for several years - unfortunately they forgot to earth either DB. So I'm trying to fix that. Both DB's can be RCD/RCBO protected - I'm prepared to replace both DB's to accommodate them. I should also mention that there are 2 showers each with their own earth rod. Attached diagram shows the current set-up. Other than the missing RCD protection, would there be any other concerns with this that I should consider ?

Thanks for all the help and advice.

What I meant to say was interupted coffee1.gif

What I mean to say before was I thought is was 10mm cable from earth bar to rod and 4mm to equipment.?

Posted

If at all possible you should link your grounds together, either inside or at the rods.

This will reduce the possibility of shock between the two grounds during a fault and will also reduce the overall resistance to ground which can never be a bad thing.

  • 2 weeks later...
Posted (edited)

Wouldn't it be better to disconnect the independent earths of the showers and run them to the earth bar in the consumer unit ?

Edited by GavinK
Posted

Indeed it would ^^^. Unfortunately some installations make it difficult or impossible to do this in a neat manner.

  • Like 1

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...