45A at 220V is 9900 Watts.

We have two 7kW water heaters and 4 aircons on a 15/45, running both heaters and all the A/C (total 22kW) will open the incoming 50A breaker (it's pulling about 100A), but in reality we rarely go anywhere near the limit.

To our OP, 7kW (31A) shouldn't be an issue.

Posted

And the next question is... When you are running that new big draw heater at max what is your voltage drop? Depending on the distribution system in your area the voltage drop could be big. If so, be sure to turn of you fancy new air con units and other motor loads when you shower. Except for the poor overheating water pump of course....

Posted

Nothing wrong with going with the biggest size heater your service allows. I would recommend it actually, I found my 6000W undersized at the peak of some cool seasons. But it would be a good idea to crank on a few of your biggest loads and perform a voltage check at a receptacle. Often in the evening at my place with two A/C units running and half the lights on I could be floating between 195 - 200 V. This will nose dive if I now crank on the biggest water heater. So I now have a routine of turning off all motor loads possible before showering..... until the PEA shows up at my doorstep to save me.....been waiting a couple years now.

Posted

Thanks for the contributions. I picked up a 4.5 kw heater on special today, and the MIL will be getting the old 3.5, which is the largest that her meter will allow.

Is she insured. w00t.gif ...................................laugh.png
Posted

It is not practical if renting, but a big boiler electric hot water system (need hot water plumbing) only draws typically at max about 2000W when it is on, so for some people this is actually a good solution.

Or put in 3 Phase and triple what you get.

  • 3 weeks later...
Posted

Voltage drop and the size of the consumers mains are the important factors. Your voltage on load should not be less than 198VAC max. this is 10% below the nominal 220. the smaller the heater in kW the better, make sure you have good water pressure. A 20A heater is ample for showers, temp set at 60C max.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...