I am building  a garage/ workshop it will have is own  CU  I oder a 3P +N RCBO from aliexpress but they send me  a 3P RCBO can I use this one

or better to oder  a new?  shold  I use the same earth rod from the house or fit  a new it is about  15 meters between  them?

Posted

Some experts will visit shortly, but I recently built the same sort of thing about 30m from the house. I treated it as a new installation as (mine only single phase), the underground power feed is from the incoming mains. So I did put an earth rod from the new garage CU.
I haven't looked up the RCBO 3P + N, but I presume it open circuits the N as well on a trip. If this is the case I'm not sure why you require it on a garage installation.

Sent from my SM-J700F using Tapatalk

Posted

OK, that's a 3-P RCBO intended for operation of balanced 3-phase loads with no neutral (motors and the like).

 

I do not believe it is suitable for the application you intend where there will be significant neutral currents.

 

Time to open a dispute with the supplier I think if they definitely sold it as 3P+N.

Posted

I just went to the Aliexpress website. https://www.aliexpress.com/wholesale?ltype=wholesale&d=y&origin=y&isViewCP=y&catId=0&initiative_id=SB_20170222185203&SearchText=3P+%2BN+RCBO&blanktest=0&tc=af, and it seems that some of the RCBOs advertised  as 3P+N gave a neutral connection and some don't!  The picture of the EFET one looks exactly like the one you have and is obviously missing the neutral but is advertised as 3P+N, the picture of the DELIXI advertised as 3P+N has the neutral connection.  Both advertised as 3P+N. Doesn't surprise me!

Posted

Don't let your option to open a dispute expire.

 

I've seen this ploy from a couple of Chinese sellers, low value stuff so they hope you'll not bother opening a dispute.

 

Item in question was a pack of 10 football adaptors. Only one arrived.

"Sorry, sorry, we'll send you the rest"

Some time later, after I'd let the dispute time out, another one adaptor arrived :(

 

So I have two adaptors for the price of 10 (they were really cheap mind).

 

Posted

I haven't had too much trouble with the sellers on Aliexpress, but always keep the dispute date in mind.  However, Lazada customer service is totally useless.  I order a lot through Lazada and the majority of the time they perform  and deliver before the committed date, but when I have a problem and have to contact customer service they have to be the worst.  Getting a refund for non delivery takes a month of Sundays!:sorry: off topic!

Posted

Just to say... I have ordered a lot from Lazada and the one time I had issue it was resolved by their customer service immediately.  They refunded the price and I sent back the defective item.  

Posted

Probably silly question, but how can you have a 3 phase RCBO without a neutral? What inbalance causes it to trip?

Sent from my SM-J700F using Tapatalk

Posted
23 minutes ago, Arjen said:

I think Crossy gives the answer here? "operation of balanced 3-phase loads"  So an inbalance between the phases will make it trip?

 

Nearly. A simple phase imbalance won't trip a 3-phase 3-wire RCD/RCBO (with no neutral the phase voltages will go awry).

 

The RCD device performs a phasor addition of the three phase currents, this should result in zero. If it does not the difference must be going somewhere (through you) and the device operates.

 

The 3-P+N unit does the same sums on the 3 phase plus the neutral (still looking for zero).

 

Posted

I always wondered about the operating principle of the RCBO...am I right in presuming that it's the same as a differential protection relay in an HV/MV installation?...a low voltage version of detecting ground faults...

 

 

Posted
 
Nearly. A simple phase imbalance won't trip a 3-phase 3-wire RCD/RCBO (with no neutral the phase voltages will go awry).
 
The RCD device performs a phasor addition of the three phase currents, this should result in zero. If it does not the difference must be going somewhere (through you) and the device operates.
 
The 3-P+N unit does the same sums on the 3 phase plus the neutral (still looking for zero).
 

Ahhh, forgotten my 3 phase stuff. Thanks for the response effort.

Sent from my SM-J700F using Tapatalk

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...