We have what appears to be the standard low level service on our small Bangkok shophouse, 15-45 amps. Is the 45 amps the limit on this service?

There is a 63 amp rated Safe T Cut device that I take to be a combined breaker tripped by excess current (64 amps?) and also by leakage showing up as unequal current between hot and neutral.

What is likely to happen with an overload of say 50-60 amps? (Say from a water heater and a couple of aircons and say some kitchen stuff).

Does the meter blow, or is there typically some fuse on the company side of the circuit? I'm assuming a 63 amp breaker trips at 63 amps, but I'm no expert.

Swelters.

By the way, the Thaivisa stuff on electricity is invaluable, I jus didn't see the answer to this elementary question.

Hi Ron.

The maximum continuous load on your meter is 45A, however meters are very robust so even a fairly significant overload won't do any damage.

It depends on the actual device characteristics, but the 63A breaker will open in about 5 minutes at 50% overload (not 64A) so it won't even notice your 50-60A load.

IMHO you'll be just fine, you're unlikely to have all the loads on at once anyway :)

That said you should do a maximum-demand calculation to be sure.

"I don't want to know why you can't. I want to know how you can!"

If your meter size is 45A you most likely have 50A consumers mains, but one should verify this. A service fuse or protective device may not be installed. Your mains will accept short sustained overloads providing there is no undue temp rise. If your consumers mains are larger 63A will provide the protection you require.

You should carry out an MD calculation or calculate your MD by assessment, ie: the max sustained load over any 15minute period. the second option is the best.

Create an account or sign in to comment

Recently Browsing 0

  • No registered users viewing this page.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.