wayned Posted June 11, 2016 Share Posted June 11, 2016 I just bought a new Arc welder (input capacity 15.2 KVA, 35% duty cycle). I will splice into the overhead power lines coming into the building and install a separate breaker and plug for the unit about a 10 meter run to the new breaker. My calculations indicate that the wire size should be 16MM2 copper, but the manual indicates 10MM2 copper is acceptable. Which is correct? If 10MM2 copper is okay I shpould be able to get away with 16MM2 aluminum which I already have and could save some money! Link to comment Share on other sites More sharing options...
Crossy Posted June 11, 2016 Share Posted June 11, 2016 10mm2 Cu will be fine on a current rating basis taking into account the duty cycle, volt drop over 15m will be about 2% 16mm2 Al will be fine. I'm assuming the welder and supply is single-phase, what size meter do you have? Link to comment Share on other sites More sharing options...
wayned Posted June 11, 2016 Author Share Posted June 11, 2016 Thanks. Meter size is 15/45. I have another welder, heavy and not portable, hooked up to it in another building with no problems. That one is installed using 25MM2AL that I had leftover when I built the house.. I'll never use both at the same time. Link to comment Share on other sites More sharing options...
hgma Posted June 11, 2016 Share Posted June 11, 2016 Only added suggestion i can make if you want to transport the welding machine from its place adding length to the supply wire....be sure NOT to coil the feeding ac wires..........causing spool effect and overheating supply lines!! Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now