April 18, 20179 yr SafeT-Cut Tripping -Not sure what to do with this problem. It has just started this week, after nothing in particular, no changes to anything. My house is wired via a 63A Safe-T-Cut box, the mains come in direct from the road (no breaker). The box is about 12 -14 years old and I am wondering if the box could be on its way out. Symptoms are as follows; The trip is set at 25mA and has been like this for years with no issues, suddenly this week the trip has been cutting off the power and I cannot find a reason. If you take a look at the photos, the output from the Safe-T-Cut goes into the main breaker (far left ) on the Square D box, this is a 60Amp / 10KA rating. From the 60 Amp in the square D, the power is fed to the individual breakers from 1 -12 (12 is spare). When the Safe T Cut trips, I can turn off all of the 1-12 breakers AND the 60A Breaker and yet for about 1-2 minutes, the Safe-T-Cut will keep tripping with nothing else switched on? Once the Safe-T-Cut can be reset, then I can power everything up and it works fine, I have reduced the trip to 15mA to see if there is one particular circuit that is more sensitive, nothing happens. I then run it at 5mA and again nothing trips (This is running one breaker on at a time to see if I can identify maybe one particular circuit that is leaky) I cannot get any decent results using 5 or 15mA using more than 5 or 6 breakers as eventually any combination can cause it to trip. So, we set it back to 25mA and it might run for a day or two or even three but it will go and trip again, reset and all is fine. Any ideas where to start looking? I can't understand why the Safe-T-Cut would trip when the main 60A breaker has been opened as there is only power as far as the Square D breaker. Any ideas thanks?
April 18, 20179 yr If it's tripping with the main CU breaker open then suspect the Safe-T-Cut Does it trip on "direct"? Do verify the supply polarity L is L, N is N it's possible that this has changed without your knowledge, any work done on the supply recently? "I don't want to know why you can't. I want to know how you can!"
April 18, 20179 yr Author 7 minutes ago, Crossy said: If it's tripping with the main CU breaker open then suspect the Safe-T-Cut Does it trip on "direct"? Do verify the supply polarity L is L, N is N it's possible that this has changed without your knowledge, any work done on the supply recently? Sorry, I don't understand what you mean about tripping on direct? I assumed Direct prevented it from tripping. (Safe-T-Cut) - Does the Safe-T-Cut still trip out on Direct?? None of the breakers actually trip at all. What do you suggest? Maybe run it for a couple of days on direct and see if a breaker trips? Thanks And yes, L is still L and N is still N! Edited April 18, 20179 yr by Formaleins
April 18, 20179 yr Setting "direct" (theoretically) disables the earth-leakage part of the Safe-T-Cut, if it still trips on direct then strongly suspect the beast. The problem is that, without the proper test gear, the only way to verify if it is the Safe-T-Cut is to replace it. "I don't want to know why you can't. I want to know how you can!"
April 18, 20179 yr Author 2 minutes ago, Crossy said: Setting "direct" (theoretically) disables the earth-leakage part of the Safe-T-Cut, if it still trips on direct then strongly suspect the beast. Thanks a lot! I will give that a try - just out of curiosity, if it does not trip on direct but still trips on the leakage settings (5-25mA) when all the breakers off, where would you begin to look? Thanks!
April 18, 20179 yr 7 minutes ago, Formaleins said: Thanks a lot! I will give that a try - just out of curiosity, if it does not trip on direct but still trips on the leakage settings (5-25mA) when all the breakers off, where would you begin to look? Thanks! Without a proper RCD ramp-tester it's time for a new Safe-T-Cut I'm afraid EDIT It's just possible there's a nick in the tails between the Safe-T-Cut and the Square-D box, worth pulling the lot off if possible for a look. Pop the lid of the Safe-T-Cut, may be some wildlife within. "I don't want to know why you can't. I want to know how you can!"
April 18, 20179 yr QUESTION: Why is there a NEUTRAL<>GROUND bridge link in this CU (with a Safe-T-Cut upstream) And have you verified the earth-ground rod is still in good condition (hasn't been eaten away by corrosion)? ...also, gotta love the misuse of green/yellow-strip on circuit #3 and #5 breakers.
April 18, 20179 yr ...unless the Green/yellow-strip wire attached to the NEUTRAL BAR is a third misuse of that color of wire. Still trying to see why they used RED/BLACK combination on a single-phase CU. Confusing.
April 18, 20179 yr 6 hours ago, RichCor said: ...unless the Green/yellow-strip wire attached to the NEUTRAL BAR is a third misuse of that color of wire. Still trying to see why they used RED/BLACK combination on a single-phase CU. Confusing. Indeed, I was thinking a N-E fault, but that would clear when the main CU breaker was opened. Last hope is wildlife in the Safe-T-Cut box or iffy tails to the CU. "I don't want to know why you can't. I want to know how you can!"
April 18, 20179 yr Probably should replace the Safe-T-Cut anyway, as it has a Direct setting. Should buy a new one without a Direct setting. The reason is that if something happens, and switching the Safe-T-Cut to Direct fixes the problem, then it would probably be left there. Sent from my SM-J700F using Tapatalk