Jump to content

Recommended Posts

Posted

RCBO (residual currant circuit breakers ) yes is the best way to go but expensive one can cost as much as one RCD its a Rolls Royce job. Incidentally if you don't know RCBOs are circuit breakers with RCD built into them so every circuit has its own RCD on it so if the circuit trips because of earth fault then you don't loose all the installation just that circuit and you leave the main switch there or in your case the double pole circuit breaker. I would think that maybe you may have problems getting RCBO in Thailand because of the cost. Thai like everything done on the cheap so nobody would buy them plus the fact some of them probably don't know what they are. Supply and demand.  

Posted

@blookhead57 VERY IMPORTANT

 

You can not apply UK standards here. There is no DNO fuse in a Thai domestic installation, the front end MUST be an MCB, MCCB (in 3-phase installations) or RCBO. A simple Main Switch or RCD like we would use in the UK is not suitable as there will then be no over-current protection for the incoming supply. A short in the CU will result in an event of an explosive nature, not to mention what would happen to the poor 50A meter.

 

This document (225 Baht) https://eitstandard.com/มาตรฐานการติดตั้งทางไฟ-2/ and the others in it's family will tell you all you need to know about Thai electrical installation. Failing that AS3000 (Aussie standard) is close enough for domestic work.

 

In our OP's CU the earth bar is indeed connected to the incoming neutral so all is well. The Thai implementation of MEN (PME) requires a local earth rod at least 1.8m long (not sure what an "earth steak" is), which is something our OP needs to verify.

 

Schneider / Square-D plug-in 2-pole RCBOs which will directly replace the incomer are available here, I have the catalog somewhere but try a forum search.

 

 

Posted (edited)
2 hours ago, Crossy said:

@blookhead57 VERY IMPORTANT

 

You can not apply UK standards here. There is no DNO fuse in a Thai domestic installation, the front end MUST be an MCB, MCCB (in 3-phase installations) or RCBO. A simple Main Switch or RCD like we would use in the UK is not suitable as there will then be no over-current protection for the incoming supply. A short in the CU will result in an event of an explosive nature, not to mention what would happen to the poor 50A meter.

 

This document (225 Baht) https://eitstandard.com/มาตรฐานการติดตั้งทางไฟ-2/ and the others in it's family will tell you all you need to know about Thai electrical installation. Failing that AS3000 (Aussie standard) is close enough for domestic work.

 

In our OP's CU the earth bar is indeed connected to the incoming neutral so all is well. The Thai implementation of MEN (PME) requires a local earth rod at least 1.8m long (not sure what an "earth steak" is), which is something our OP needs to verify.

 

Schneider / Square-D plug-in 2-pole RCBOs which will directly replace the incomer are available here, I have the catalog somewhere but try

 

 

Ok an earth steak is the same as a earth rod (English term) incidentally what's a DNO fuse? Ok this Gent then cant remove the main switch circuit breaker he will have to fit an external RCD. I don't think you can get a double pole 63A RCCBO plug in breaker. 

Edited by blookhead57
Posted
31 minutes ago, blookhead57 said:

Ok an earth steak is the same as a earth rod (English term) incidentally what's a DNO fuse? Ok this Gent then cant remove the main switch circuit breaker he will have to fit an external RCD

I was being facetious, the word is "stake".

 

Anyway, the DNO (Distribution Network Operator  https://en.wikipedia.org/wiki/Distribution_network_operator ) fuse is the 80A (or so) BS88 fuse that is found in the service head where the supply enters the property. Thailand does not have these, over current protection for the supply is provided by the MCB in the CU.

 

Our OP CAN replace the current 2-pole MCB (overload only) with a 2-pole RCBO (earth leakage plus overload), he cannot replace it with an RCD (earth leakage only).

 

One of these, yes I know that's a 50A unit, but since he's likely on a 15/45 meter that's actually the right one. ;-

 

EDIT Here's the 63A one https://www.lazada.co.th/2p-rcbo-63a-34schneider34-77047448.html still shows the picture of the 50A.

 

Untitled-1.jpg

 

Lazada have them https://www.lazada.co.th/2-50-rcbo-2p50a-30ma-10kaschneidersquare-d-23017589.html

 

Posted
11 minutes ago, Crossy said:

I was being facetious, the word is "stake".

 

Anyway, the DNO (Distribution Network Operator  https://en.wikipedia.org/wiki/Distribution_network_operator ) fuse is the 80A (or so) BS88 fuse that is found in the service head where the supply enters the property. Thailand does not have these, over current protection for the supply is provided by the MCB in the CU.

 

Our OP CAN replace the current 2-pole MCB (overload only) with a 2-pole RCBO (earth leakage plus overload), he cannot replace it with an RCD (earth leakage only).

 

One of these, yes I know that's a 50A unit, but since he's likely on a 15/45 meter that's actually the right one. ;-

 

EDIT Here's the 63A one https://www.lazada.co.th/2p-rcbo-63a-34schneider34-77047448.html still shows the picture of the 50A.

 

Untitled-1.jpg

 

Lazada have them https://www.lazada.co.th/2-50-rcbo-2p50a-30ma-10kaschneidersquare-d-23017589.html

 

ok very good this is what this gent needs I noticed its only 10KA I hope his not near the transformer where it might have short circuit potential of more than 10,000 amps. Incidentally I use to be dyslexic but I couldn't spell it LOL.

Posted

Yeah, 10kA should be fine. We are only 150m from the village transformer our PFC is 500A (source impedance is around 0.5 ohms). 

 

Yes, we get pretty bad voltage droop on load, hence my thread on installing an AVR.

 

As a southpaw I too suffer from word blindness (although it's much better now than it was at school), can be an issue as an engineer.

Posted
4 minutes ago, Crossy said:

Yeah, 10kA should be fine. We are only 150m from the village transformer our PFC is 500A (source impedance is around 0.5 ohms). 

 

Yes, we get pretty bad voltage droop on load, hence my thread on installing an AVR.

 

As a southpaw I too suffer from word blindness (although it's much better now than it was at school), can be an issue as an engineer.

a lot of intelligent people are dyslexic

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...