Daikin aircon error codes - Split aircon daikin indoor unit blinking on start up


Recommended Posts

Posted

Hello,

One of the aircons just died at the wrong timing :-)

I was looking for error codes and found this in case you are interested:

DAIKIN error codes:

AO Indoor Error of external protection device
A1 Indoor PCB defect
A3 Indoor Malfunction of drain Level control system
A5 Indoor Freeze-up prevention
A6 Indoor Fan motor lock, Overload
A7 Indoor Malfunction of swing motor flap
A9 Indoor Malfunction of EEV
AF Indoor Drain level above limit (clogging)
AJ Indoor Malfunction of capacity set device
C3 Indoor Malfunction of drain thermistor
C4 Indoor Malfunction of liquid pipe thermistor
C5 Indoor Malfunction of gas pipe thermistor
C7 Indoor Lower louvre limit switch/motor
C9 Indoor Malfunction of air thermistor
CC Indoor Malfunction of moisture sensor
CA Indoor Malfunction of discharge air thermistor
CJ Indoor Malfunction of remote control thermistor
CE Indoor Malfunction of radiant heat sensor
E0 Outdoor Activation of outdoor safety device
E1 Outdoor PCB defect
E3 Outdoor Activation of high pressure switch
E4 Outdoor Activation of low pressure switch
E5 Outdoor Activation of compressor over heat protection
E5 Outdoor Compressor motor lock
E6 Outdoor Compressor start up error
E6 Outdoor Standard compressor lock/overcurrent
E7 Outdoor Fan motor lock, Overload
E8 Outdoor Inverter input overcurrent
E9 Outdoor Malfunction of EEV
EA Outdoor Four way valve defective.
F3 Outdoor Abnormal discharge pipe temperature
F6 Outdoor Refrigerant overcharged
FC Outdoor Low pressure drop.
H3 Outdoor High pressure switch defect
H4 Outdoor Low pressure switch defect
H6 Outdoor Compressor motor position detection sensor error
H7 Outdoor Fan motor position detection sensor error
H8 Outdoor Current transformer error
H9 Outdoor Malfunction of air thermistor
J1 Outdoor Malfunction of pressure sensor
J2 Outdoor Current sensor malfunction
J3 Outdoor Malfunction of discharge pipe thermistor
J4 Outdoor Low pressure saturation thermistor
J5 Outdoor Malfunction of suction pipe thermistor
J6 Outdoor Malfunction of heat exchanger thermistor
J7 Outdoor Malfunction of heat exchanger liquid thermistor
J8 Outdoor Malfunction of liquid pipe thermistor
J9 Outdoor Malfunction of gas pipe thermistor
JA Outdoor Malfunction of discharge pipe pressure sensor
JC Outdoor Malfunction of suction pipe pressure sensor
JH Outdoor Malfunction of oil temperature sensor
L0 Outdoor Malfunction of inverter
L3 Outdoor Electronic component box overheat
L4 Outdoor Inverter cooling defect
L5 Outdoor Comp motor ground fault, Short circuit
L6 Outdoor Compressor motor grounding/short circuit
L7 Outdoor Total input overcurrent
L8 Outdoor Comp overload, Motor disconnected
L9 Outdoor Compressor lock
LA Outdoor Power unit malfunction
LC Outdoor Transmission between inverter & outdoor
P1 Outdoor Inverter over ripple
P3 Outdoor Thermistor abnormality
P4 Outdoor Power unit humidity sensor malfunction
PJ Outdoor Failure of capacity set resistor
U0 System Shortage of refrigerant or EEV failure
U1 System Negative phase, Open phase
U2 System Power supply insufficient
U3 System Wiring check operation not executed
U3 System Mismatch of indoor and outdoor units (Split only)
U4 System Transmission between indoor units
U5 System Transmission to remote controller
U6 System Malfunction transmission outdoor to BP unit
U7 System Transmission between outdoor units
U7 Outdoor Malfunction between outdoor boards(RMX/RX RK)
U8 System Transmission between master & slave R/C
U9 System Transmission error between indoor to outdoor
UA System Excessive number of fancoils
UC System Address duplication of central controllers
UE System Transmission error between indoor & central
UF System Refrigeration system not set/wiring - piping
UF System Terminals 1 and 3 crossed (Split/Skyair)

If your DAIKIN remote controller comes with a "test" button, use it. Otherwise press the Temperature UP,
Temperature DOWN and the MODE buttons all at the same time. I repeat, all 3 buttons at the same time.

You will see 00 on the remote controller. The first "0" will be blinking.

Stand facing the particular air conditioner you wanted to test.

Now press the Temperature UP button, "0" will become "A" and the air conditioner will respond with either a single
beep or double beep.

Carry on pressing the Temperature UP button and listen to the beeping sound, stop when you hear a double beep.
For example: it is now showing "C0".

Now press the MODE button, the second "0" will be blinking.
Now press the Temperature UP button, "0" will become "1" and the air conditioner will respond with either a double
beep or a continuous beep.

The continuous beep is the error code. For example "C4", it means it is a faulty liquid pipe thermistor.

Posted

Now a question, do you know a guy who checked your inverter Daikin aircon ?

I don't want to call random somchai who will know nothing about inverter and just walk to dirt my expensive wooden floor !

Thank you.

PS: I get this error: E7 Outdoor Fan motor lock, Overload

Posted

Now a question, do you know a guy who checked your inverter Daikin aircon ?

I don't want to call random somchai who will know nothing about inverter and just walk to dirt my expensive wooden floor !

Thank you.

PS: I get this error: E7 Outdoor Fan motor lock, Overload

Thanks for posting those Daikin A/C error codes!! (Hopefully Daikin's build quality will make them a rarely used)

Depending on your location, I would buy and get service from a Daikin dealer - A reputable electrical shop at the very least.

Posted

Daikin dealers are not better than one of the few guys with a brain that we can find in this country.

Without looking at the error code he instantly found that the outdoor unit fan was dead.

Now trying to find one before SONGKRAN !

Do you know if there is any aircon parts shop as there are cars parts shops ?

Thanks.

Posted

Daikin dealers are not better than one of the few guys with a brain that we can find in this country.

Without looking at the error code he instantly found that the outdoor unit fan was dead.

Now trying to find one before SONGKRAN !

Do you know if there is any aircon parts shop as there are cars parts shops ?

Thanks.

You haven't said where you are, but this thread could be helpful http://www.thaivisa.com/forum/topic/667384-airconditioner-technicians/

Also.... in Pattaya

post-62323-0-97481800-1460227689_thumb.p

Posted

Thank you, but how stupid can be someone to have closed this thread ? No chance to ask who were the Daikin technicians involved.

What I found that can be useful:

jbrain

I bought my aircons from the wholesale that supplies all the parts to the technicians, since they were by far the cheapest at that time. They carry all brands and are located 3 shop houses before Fascino pharmacy on Nua road, next to Giffarine.

Questions:

Is it the only place around Pattaya to buy aircon parts ?

Can we repair an outdoor unit fan or do we have to change it ? Buy it second hand is ok ?

My problem is not the price but availability within 2 days.

Thanks.

Daikin dealers are not better than one of the few guys with a brain that we can find in this country.

Without looking at the error code he instantly found that the outdoor unit fan was dead.

Now trying to find one before SONGKRAN !

Do you know if there is any aircon parts shop as there are cars parts shops ?

Thanks.

You haven't said where you are, but this thread could be helpful http://www.thaivisa.com/forum/topic/667384-airconditioner-technicians/

Also.... in Pattaya

attachicon.gifAirconditioner_Technicians_-_Pattaya_Forum_-_Thailand_Forum_-_2016-04-10_01.41.26.png

Posted

We just had the same problem with a Mitsu air-con, took them a week to order and install a new outdoor fan motor, it was caused by a surge in the power supply, cost for replacement being fitted was 3,000 Baht.

Posted

Thank you, but how do they know that there was a surge ? They can just guess ? Any motor car die suddenly and does not need a surge.

We just had the same problem with a Mitsu air-con, took them a week to order and install a new outdoor fan motor, it was caused by a surge in the power supply, cost for replacement being fitted was 3,000 Baht.

Posted

Thank you, but how do they know that there was a surge ? They can just guess ? Any motor car die suddenly and does not need a surge.

We just had the same problem with a Mitsu air-con, took them a week to order and install a new outdoor fan motor, it was caused by a surge in the power supply, cost for replacement being fitted was 3,000 Baht.

The surge was my diagnosis! we had a brief power cut, then the power came on and went off again about three times in quick succesion - then stayed off for about an hour, obviously they were having trouble resetting power, after that the air-con didn't work! Thankfully we only had the one air-con running at that time.

Posted

I get this all the time when there is a power cut or big voltage spike.

Switch off at the mains fuse for a couple of minutes. Switch back on and problem is usually fixed, if not repeat.

Works every time for me.

Posted

Thank you !

It usually works, you are right, but not this time !

Do you know why it usually works actually ? Weird that cutting the power helps the aircon to restart ?

I was so sure to repair it myself thanks to T-cut, but this time I lost face :-)

I get this all the time when there is a power cut or big voltage spike.

Switch off at the mains fuse for a couple of minutes. Switch back on and problem is usually fixed, if not repeat.

Works every time for me.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...