Consumer Unit problems


carlyai

Recommended Posts

I have a Schneider Easy Pact 100 A 25 KA outside load centre or Consumer Unit.
While looking for a phase not working problem (another thread), I poked around resulting in the phase returning with intermittent arcing under the knurled Allen screw. I tried to tighten the screw, but the female thread in the black bakelite CU must be stripped as the Allen screw will not tighten.
 
Question 1.
Do you know if I can just replace the black bakelite/plastic, or do I need to buy another CU?
 
While having a close look at the CU, I noticed that more than one Allen screw connection to the 60A breaker appears to have been arcing as well. I also noticed that the right hand, and middle black bakelite seems to have been melting.
The 3 phase breaker in the CU is 60A and has never tripped.
Question 2.
If the CU is 100A per phase unit, why does the bakelite appear to have melted on the middle and RHS Allen keys side? Is it because of the proximity to the bacelite high resistance joints created by the stripped Allen screws female threads?
 
If I have to replace the black bacelite, I can probably do it myself as the 60 A breaker will be left in circuit. If I need to buy a new CU I think it's a job for my electrician. He was the one who installed the CU in the first place.
 
20180217_113423.jpg.33f2a7aea331bdbbbd4cf7a42196d93b.jpg20180217_113447.jpg.16c93ae08e6d5d454569feb52ee797ee.jpg20180217_113509.jpg.a4005bb5ad9d3cf25ea944c85d39d633.jpg20180217_113519.jpg.f3adc96cf7dadc9c6b4490f6affb2bd0.jpg
 
Sent from my SM-J700F using Tapatalk
 
 


Link to comment
Share on other sites

Seems like a loose connection causing the arcing. If you can get the Allen screws out, then your good to go, if that's where the thread has gone.

Sent from my SM-N950F using Thailand Forum - Thaivisa mobile app


So you think it's the male Allen key thread, not the part it screws into? Good thought, thanks, will take a look.

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

So you think it's the male Allen key thread, not the part it screws into? Good thought, thanks, will take a look.

Sent from my SM-J700F using Tapatalk

Having a better look, and the Allen screws do screw into a bus. 20180217_131545.jpg

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Ah I can see what you mean now. If the female thread has gone, then I fear that you are screwed. No pun intended.
I would try spring washer and a washer. Which should be standard on that piece of kit.

Sent from my SM-N950F using Thailand Forum - Thaivisa mobile app


Seems I'm screwed. It's the female part.20180217_134432.jpg

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Another possibility is to tap a larger bolt on.

Sent from my SM-N950F using Thailand Forum - Thaivisa mobile app


I thought of that, not too sure if Global House etc have thread taps and a selection of Allen screws.
The best option I think.
Trouble is I can't take the Allen screw with me, so will have to try the Muan Thai Outlet in Roiet first, this is where I bought the CU.
I can nearly hear the reply...' we can sell you a new CU but don't have the Allen screws.'
I did notice a big flash from the HR joint when I reconnected everything and the house pump (300 W) and the aquifer pump (700 W ) both kicked in together. What would the start up current be, approx. 15A?
Seeing SWMBO is huffing and puffing at the moment, tomorrow might be a good time for a Roiet road trip.
There's a downside in living in Isaan without an Isaan house. Everytime there is an electrical issue, or pump or water or pool cleaning issue, and SWMBO gets wind of it she gets huffy with ' what am I going to do if you die? No one's going to be able to fix the place.'

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Have a look for these self-drilling screws, not the regular self-tapper type, these have real threads. Take care on the length, things could get "interesting" if a too long screw touches something it shouldn't

 

20180217_154051.jpg

  • Like 1
Link to comment
Share on other sites

Seems I'm screwed. It's the female part.20180217_134432.jpg.1c170b48201b120fa74555583c20b7ab.jpg

Sent from my SM-J700F using Tapatalk

There is an excuse for a spring washer on the Allen screws. I put another spring and flat one on the RHS one, seemed to fix it, but I can't get the middle one out it just spins. It does have a lose and tight spot, so screwed it to the tight spot.
If I can't find a tap and correct Allen screw, I suppose I could get a bigger screw and cross thread it in. Nah, I couldn't do that...[emoji848]

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Have a look for these self-drilling screws, not the regular self-tapper type, these have real threads. Take care on the length, things could get "interesting" if a too long screw touches something it shouldn't
 
20180217_154051.thumb.jpg.cc146f0b3e96efa9c39131f6d8385d11.jpg
Thanks, like thinking I think.

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

What size key are you using? Then you can determine what size screw you have. https://www.metricmcc.com/catalog/Ch1/1-32.pdf

 

The problem then becomes finding the next size up in imperial to get close. Or simply go up one size metric. Buy a tap set and... Looks like there is enough meat!

Edited by VocalNeal
Link to comment
Share on other sites

Can you not get a terminal driver on the middle one, and keep pressure on to lift it off as you turn?
 
Sent from my SM-N950F using Thailand Forum - Thaivisa mobile app
 
 
 
 
I tried with a flat screwdriver lifting and some bullnose pliers pulling, but no go. Didn't try too hard as I need a connection until I fix it.

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Another question while you're all bored and got nothing to do...
Crossy I notice that you installed large analogue meters for your Amps and Volts near your stabalisers. Look good. Any reason you didn't use the digital voltamps meters?

Also, I need to monitor the voltage and current on the 3 phases at my CU, but not sure how I'd do it with the CU I have. I don't wish to wire anything to the feed from the meter, I want to work on the other side of the 60A breaker with it off. Or would a different style CU, with the same dimensions be easier to wire up?


Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

What size key are you using? Then you can determine what size screw you have. https://www.metricmcc.com/catalog/Ch1/1-32.pdf
 
The problem then becomes finding the next size up in imperial to get close. Or simply go up one size metric. Buy a tap set and... Looks like there is enough meat!
Thanks VocalNeal, big help, I'll check it out.

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

16 minutes ago, carlyai said:

Crossy I notice that you installed large analogue meters for your Amps and Volts near your stabalisers. Look good. Any reason you didn't use the digital voltamps meters?

Actually we now have multiple digital beasties too (read Volts, Amps, Watts and energy consumed), set up for incoming supply (along with the analog meters), AVR output and genset output.

 

Analog meters are great for "a quick glance to verify all is well" (this is why aircraft instruments are still analog look-alike, the pilot sees all the needles horizontal when all is well, anything off horizontal or bouncing around means trouble) they also react more quickly than digitals, handy if you have lights flickering.

 

20180217_162726.jpg

 

Wifey doesn't moan (at least not verbally) just lets her crazy farang do what he wishes.

 

  • Like 1
Link to comment
Share on other sites

Thanks VocalNeal, big help, I'll check it out.

Sent from my SM-J700F using Tapatalk

The key size is 4mm, this seems to correspond to the screw threaded part diameter size. So I'll try for a 5mm Allen screw or 5mm roofing screw.

Also a tap set. I suppose there are good and bad tap sets at Global House?

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

25 minutes ago, carlyai said:

Also a tap set. I suppose there are good and bad tap sets at Global House?

Even the cheap Chinese carp should be OK in your bus-bars, the "metal" isn't exactly tough even in the big-name stuff.

Link to comment
Share on other sites

Usual it is copper. A very "elastic" material to make thread. When you go for M5,  you should drill 4.2mm. (M6 5mm) But you can try without drilling. The easy available hand taps are marked. with one ring is the first one, with two rings is the second one, and without rings is the third one. The rings are usual placed on the end from the tap, close to the square. When you can find a machine tap, that is even better. They cut easier.
 
If available apply some WD40 or (better) engine oil on the tap.
 
Arjen.
 
 
Hi Arjen. Sorry I don't understand. Are you saying the taps are made of copper, or the material to tap into?
It's a long time since I was trainee/apprentice, but I thought the taps were made if steel. I also don't understand about the rings.

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Thinking about installing the analogue voltage and current meters, I could probably install another metal CU box near the first one. Then take out the 3 links between the main breaker and the bus bars. Then run 3 cables from the out side of the main 60 A breaker to the new box and current meters and back to the bus bars. Take the volts meters of the corresponding Amp meter and other side to neutral.
Not much room.
Probably have to make the wires come up vertically from and to where I remove the links from the 60 A breaker to the buses.
Only other way may be to have individual digital current/voltage/energy meters in the house consumer unit, the garage/aquaponics/ pool pump CU and the back aquifer CU.
That would be 3 meters in the house CU and 1 each in the other CUs.
Probably be safer, as red ants tend to periodically invade the outside consumer unit.
Any thoughts?
@Crossy have you a reference for those digital volts/amps/energy meters?
20180217_131611.jpg

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

36 minutes ago, carlyai said:

@Crossy have you a reference for those digital volts/amps/energy meters?

 

These are the ones in the photo https://www.aliexpress.com/item/Digital-LCD-Blue-backlight-AC80-260V-100A-volt-amp-meter-with-Transformer-coil-voltage-current-power/32340279544.html

 

HTB1R28pQFXXXXbvXFXXq6xXFXXXz.jpg

 

Dead easy to install, just slip the current transformer onto the bus (hopefully it will fit) or incoming cable and hook the voltage sense to L and N. They do make a 3-phase version for a more compact installation.

 

EDIT Looking at your board I suspect you will be slipping the CTs on the incoming supply.

 

 

 

 

Link to comment
Share on other sites

 
These are the ones in the photo https://www.aliexpress.com/item/Digital-LCD-Blue-backlight-AC80-260V-100A-volt-amp-meter-with-Transformer-coil-voltage-current-power/32340279544.html
 
HTB1R28pQFXXXXbvXFXXq6xXFXXXz.jpg.b833d6a8c7b19bd31e9044467584b434.jpg
 
Dead easy to install, just slip the current transformer onto the bus (hopefully it will fit) or incoming cable and hook the voltage sense to L and N. They do make a 3-phase version for a more compact installation.
 
EDIT Looking at your board I suspect you will be slipping the CTs on the incoming supply.
 
 
 
 
Yes on the incoming cable into the 60 A breaker, seems the way. Didn't know it would be so easy.
I'll look up a 3 phase distribution board, see what they have on offer. Meters should be pre wired.

As another aside... looks like all the Allen type screws are arcing between the excuse for a spring washer and the busbars. I changed the back pumps to the LHS phase, blue, the one that didn't seem to be arcing, and when the back pumps kicked in it looked for a second that someone was arc welding around the spring washer. Fissing and poppying then silence. Must have welded a good connection as I couldn't get it to do it again.
Maybe that's a fault with those CUs?
I'll check out other units when I get to Roiet.
I'm obeying again, so all is OK. [emoji6]

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

The material to tap into is from copper. It does not look red, as it is plated with Sn. Hand taps (the set what cmes in three pieces) are usual from HSS steel. Machine taps (only one needed) ar much harder then HSS.
 
The rings....5a89330f911e5_20180218_1500251.thumb.jpg.493a49b0562fb5fa353e18eda6562d6c.jpg
 
The lowest one has one ring, it is the first tap, the middle one has two rings, it is the second one. The one most on top has no rings, it is the last (third) one.
 
Hope this helps!
 
Arjen.
 
 
OK, thanks, got it.

Sent from my SM-J700F using Tapatalk

Link to comment
Share on other sites

Something you may wish to think about, if indeed it applies these days, and it may save you going through all of this trouble............ when bakelite or something like it's equivalent, overheats and has already had some arcing near it/around it, then it changes from being an insulator to a (part) conductor!!

Saw this many times and once this material became subject to arcing, it was always advisable to change it completely because overheating and further arcing, if not a complete burnout would occur.

Something to possibly consider?

  • Like 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.










×
×
  • Create New...