We have a long relatively narrow lounge, about 9m by 4m so 36m2.

 

Currently it doesn't have any A/C and with plenty of through ventilation it's quite comfortable for me with just fans. It only gets sun through the windows early and late, the windows are well shaded during most of the day.

 

We have family coming from the UK early next year so I think adding aircon to this room will make them more comfortable when watching the telly.

 

Conventional Thai wisdom of 6-700 BTU per m2 gives us 21,000 - 25,000 BTU required.

 

So, considering the shape of the lounge would having one large unit or two smaller ones be the way to go?

 

Link to comment
Share on other sites

Thanks so far chaps.

 

We are limited as to where we can put the indoor units there's space about 6m along one long wall and again at maybe 2m of the same wall. the end walls are non-starters.

 

Also there's only space for one outdoor unit on the ledge constructed for same so we would need a stacking arrangement for two units.

 

My current thinking is two non-inverter units, our power can be a little "lumpy" so I'd like to keep things simple. We could run one unit alone in the cooler weather, also we get some redundancy if there's a failure.

 

Link to comment
Share on other sites

12 minutes ago, Issanman said:

I have a Panasonic 18K inverter cooling a 56sqm room and it works just fine.

None of the walls of this room are exposed to direct sunlight, however.

I have a slightly larger Hitachi inverter in a very slightly smaller area and that also works fine. One entire wall is glass and gets a little direct sun at some times of day.

I suppose my set up might struggle if I wanted the room at 19 degrees, but I have it set constantly at 27, with one ceiling fan on slow, and it's all good.

 

I would never buy another aircon that was not an inverter.

  • Like 1
Link to comment
Share on other sites

Generally speaking an 18k btu (5kw) inverter wall hung split system should be adequate.

I would consider the installation placement if I were you, it would be preferable to install the indoor on an exterior wall in a back to back configuration with the outdoor condensing unit.

Installation can rack up the purchase price if you have long internal and external runs, I would not recommend installing the indoor unit on an internal wall for various reasons.

 

Link to comment
Share on other sites

2 hours ago, TheMysteriousMrTesla said:

Conventional Thai wisdom of 6-700 BTU per m2 gives us 21,000 - 25,000 BTU required.

I have found that 500 BTU per m2 is plenty, I also prefer AC + fan as then you can be comfortable with a higher room temperature and not have such a large temperature differential to the outside.

 

so what I would do is put in 1 AC of maybe 12,000 BTU. That lets you decide if it's enough and if not add a second.

 

Do not forget that oversized AC is much worse than correctly sized or even slightly undersized ones because an oversized AC will not be able to reduce the humidity anywhere nearly as well as a smaller unit and it's the Thai humidity that makes new arrivals uncomfortable.

Link to comment
Share on other sites

Suggest you install two aircons. I also have a long room 9m x 4m. Originally the supplier installed one large 18,000Btu/hr Air Con at one end of the room and it was difficult to keep the far end of the room cool, whilst the end with the air con was too cold. My monthly bill, which included 3 other air cons in the bedrooms was B8,000+. I replace this aircon with two 13,000Btu/hr aircons at opposite ends of the room lounge end and the other working office end. This mean that I only need to run one air con during the day at the office end and the other when watching TV. The result has been a B3,000 reduction in my monthly bill down to B4-5,000/month for the whole house.

Link to comment
Share on other sites

2 hours ago, bankruatsteve said:

FWI:  I cool a 3.5 x 10 meter living area indirectly through my bedroom (leaving the door and shutters open).  This is with a 12K Daikin.  With ceiling fans to move the air it is very comfortable even when HOT.

   Same with me.....   That's all I use when in Thailand and Cambodia.   Windows open in my apartment, and fans on..   I never even turn the A/C on...   never use it.   

   Oh...wait.. the 12k Daikin is an A/C unit you have turned on ? ? 

Edited by Catoni
correction
Link to comment
Share on other sites

Seems a big expense for the sake of a few guest needing to watch the tv.

Lose the tv and encourahe outdoor sitting.

The weather is perfect for outdoor living, I havr not sat inside my house for three years! 

 

However, I agree with Stww and would go for one unit and see how it performs.

 

Link to comment
Share on other sites

I have quite large open lounge area, maybe half as big again as your area OP, it has two air-cons fitted both inverters, one of 12,000 and the other of 8,000.  I never need the two on at the same time.  The 12,000 is more than adequate to cool the room sufficiently.  I never did take heed of the recommended size of air-cons , as they are inevitably overblown by many BTU and seem to want to turn the tropics into the arctic, at great expense. As an aside, my UK visitors seem very happy just to have air con in the early evening and to sleep. 

  • Like 1
Link to comment
Share on other sites

2 minutes ago, eyecatcher said:

Seems a big expense for the sake of a few guest needing to watch the tv.

Lose the tv and encourahe outdoor sitting.

The weather is perfect for outdoor living, I havr not sat inside my house for three years! 

 

However, I agree with Stww and would go for one unit and see how it performs.

 

Won't the lady of the house let you in?  Been there mate  !! ???? 

  • Haha 1
Link to comment
Share on other sites

16 minutes ago, Catoni said:

   Same with me.....   That's all I use when in Thailand and Cambodia.   Windows open in my apartment, and fans on..   I never even turn the A/C on...   never use it.   

   Oh...wait.. the 12k Daikin is an A/C unit you have turned on ? ? 

Yah, 12K BTU Daikin "inverter" set to 25C.  My house is very well insulated and just a couple hours of morning sun on that room.  I usually don't even turn on the AC until about 10am, if then.

Link to comment
Share on other sites

7 minutes ago, Pilotman said:

As an aside, my UK visitors seem very happy just to have air con in the early evening and to sleep. 

Yeah, I think that this is going to be the operation mode, we have a large shaded outdoor area and they ought to be doing tourist stuff during the day anyway.

 

Unfortunately, once it gets dark the mozzies are out in force so the lounge needs to be closed up after being open all day so we need something to keep the temperature sensible (26-28C).

 

I'm tending towards something around 18,000 BTU possibly inverter towards the TV end. Fans can move the cold air around if needed.

 

Link to comment
Share on other sites

My lounge room is about 5m wide by 8m deep and i've just got an 18k BTU Samsung unit and it works well.

 

But it is well insulated as it has a floor above, below and townhouses on each side. When installing PowerBuy made me sign a document stating that if it's not cool enough I cannot return it as the BTU math didn't work out for them lol.

Link to comment
Share on other sites

13 minutes ago, MarleyMarl said:

My lounge room is about 5m wide by 8m deep and i've just got an 18k BTU Samsung unit and it works well.

 

But it is well insulated as it has a floor above, below and townhouses on each side. When installing PowerBuy made me sign a document stating that if it's not cool enough I cannot return it as the BTU math didn't work out for them lol.

 

Interesting. I wonder why their heat load calcs didn't work out. Possibly it is requested for all their installs to avoid having to legally accept returns or upgrades. A 40sqm room is adequately served by a 5kw (18k btu) unit. Most likely they were concerned about the throw from the indoor unit not reaching the farthest area of the room.

 

 

Link to comment
Share on other sites

All I can add is don't listen to the Daikin shop salesman, we put 2 x 24000 split ceiling units in our L shaped lounge, roughly 68m2 on his advice and one unit keeps the whole area cool in the hottest months. The formula he used must have been around 700BTU per m2. I guess we have a backup which we have not needed in 7 years.

I see there is supposedly a 30-40% saving when I googled Inverter airconditioners, is it worth replacing my older airconditioners? Anyone experience a worthwhile saving doing this?

Link to comment
Share on other sites

Maybe an option is to install one large capacity evaporate with 2 smaller size outdoor compressor units, when cooling requirements are low only 1 compressor will run, an obviously when cooling requirements are high both compressors will run, I know these units are available in Oz in the Daikin brand, maybe not available here, any half decent air con shop would or should know of there availability. 

Link to comment
Share on other sites

7 hours ago, TheMysteriousMrTesla said:

So, considering the shape of the lounge would having one large unit or two smaller ones be the way to go?

I would install two smaller, about half sized, units if it was my lounge...????

Link to comment
Share on other sites

Calculating the unit size is a little bit more detailed than just 600btu/m2

I am a tad more analytical with it, so that a top floor room needs lets say 300 extra to a gf. Then you can make a similar deduction if you have adjoining neighbours each side, then add for south facing windows. Then there is ceiling height which affects the volume, 3m is a standard but if you have 4m to cool its another add......

Do you have roof insulation.....

 

So yes rounded up 600/700btu/m2 may be the working average. but if you live in a greenhouse thats not going to work

Edited by eyecatcher
Link to comment
Share on other sites

1 hour ago, stevkob said:

I wonder why their heat load calcs didn't work out.

Shops here assume that you want icicles forming inside your living room. So they calculate accordingly. They said that my air-con was underpowered also and they were completely wrong for my needs.

Link to comment
Share on other sites

1 hour ago, Rawairat said:

I see there is supposedly a 30-40% saving when I googled Inverter airconditioners, is it worth replacing my older airconditioners? Anyone experience a worthwhile saving doing this?

I switched to an inverter and my saving was well over 50% on the total bill. Not sure how much was to do with the inverter and how much because the old air-con was very old.

 

How old are your existing air-cons?

Link to comment
Share on other sites

Agree that most salesmen oversize your needs. I have a poorly insulated, west facing bedroom/lounge of about 24 sq. metres. Only ever have air on afternoons and evenings, and nights except cold season.  One aircon enough, 11,000 BTU and set at 27 degrees C.

 

No mass deaths in UK's heat wave this summer, which i was present for and it was uncomfortable at night without a fan. So no need to spoil the guests. I'm sure they would be happy for one reasonable aircon in the lounge and some fans to mix it up if needed. Sleeping more of an issue.

Link to comment
Share on other sites

6 hours ago, sometimewoodworker said:

so what I would do is put in 1 AC of maybe 12,000 BTU. That lets you decide if it's enough and if not add a second.

My thoughts also, more or less what we have done with a secondary living room, keeps the humidity down and with a fan more than comfortable.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.











×
×
  • Create New...