Pink7 Posted February 16, 2022 Author Share Posted February 16, 2022 Thanks for the follow up Muhendis, Do you get your setup to priority between sun, battery, and utility supply power same way as with all in one? Pink Link to comment Share on other sites More sharing options...
Muhendis Posted February 16, 2022 Share Posted February 16, 2022 38 minutes ago, Pink7 said: Thanks for the follow up Muhendis, Do you get your setup to priority between sun, battery, and utility supply power same way as with all in one? Pink Yes. Priority is solar 1st and utility 2nd. The down side is that it takes a second to switch over so I have to have my computer on a UPS. The good thing about this way of doing things is that the utility supply allows me to run my rice mill which would be a bit of a challenge for the solar inverter. Switching over is simply a case of disconnecting the inverter output at its MCB and letting the ATS do its thing. There is also a manual override switch on the ATS which allows umm, well, manual operation of the switch. Useful if the internal switch motor were ever to stop working. Link to comment Share on other sites More sharing options...
BritManToo Posted February 16, 2022 Share Posted February 16, 2022 11 minutes ago, Muhendis said: Yes. Priority is solar 1st and utility 2nd. The down side is that it takes a second to switch over so I have to have my computer on a UPS. Your answer should be NO. As the 'all in one' switch themselves with no interruption of power, and your computers work continuously. Link to comment Share on other sites More sharing options...
Muhendis Posted February 16, 2022 Share Posted February 16, 2022 9 minutes ago, BritManToo said: Your answer should be NO. As the 'all in one' switch themselves with no interruption of power, and your computers work continuously. All-in-one inverter units do indeed switch themselves and, as far as the consumer is concerned, it is a seamless changeover. However the discussion is about the use of my ATS and how its priority was arranged. I should point out that, as mentioned earlier, my setup does not use an all-in-one inverter but instead uses individual elements so the ATS is quite a necessary part of the installation. My inverter does not have any mains input facility. 1 Link to comment Share on other sites More sharing options...
Pink7 Posted March 6, 2022 Author Share Posted March 6, 2022 On 2/14/2022 at 1:16 PM, Crossy said: Here in sunny Thailand you can guesstimate your realistic solar output by:- Installed capacity x 0.5 x 6 hours = Energy Generated. Solving for Installed Capacity = Energy Generated / (6 x 0.5). We have Sofar inverters, but they aren't particularly cheap either. When you calculate panels vs inverter would you limit panels to capacity listed on the panels even you just expect 50%? Pink Link to comment Share on other sites More sharing options...
Popular Post Crossy Posted March 6, 2022 Popular Post Share Posted March 6, 2022 12 hours ago, Pink7 said: When you calculate panels vs inverter would you limit panels to capacity listed on the panels even you just expect 50%? Your inverter manual will tell you the maximum amount of PV per string input. You should not exceed this. Your inverter will have a maximum PV input voltage. The sum of your series panel open-circuit voltages (Voc) MUST NOT exceed the inverter maximum PV input voltage. Ignore this at your peril!!! The inverter will also have a maximum string current, the sum of your parallel panel short-circuit currents (Isc) should not exceed this value. Whilst most inverters and charge controllers will try to protect themselves against over volt/current they don't always succeed and the exit of the magic-smoke ensues ???? NOTE Over-panelling an inverter or charge controller is permissable under certain circumstances, but generally stick within the numbers in the manual and you won't fry anything. 3 Link to comment Share on other sites More sharing options...
Popular Post Muhendis Posted March 6, 2022 Popular Post Share Posted March 6, 2022 1 hour ago, Pink7 said: When you calculate panels vs inverter would you limit panels to capacity listed on the panels even you just expect 50%? Pink This advisory is something I posted some time ago. I think you'll find it quite relevant. 3 Link to comment Share on other sites More sharing options...
BritManToo Posted March 6, 2022 Share Posted March 6, 2022 (edited) 2 hours ago, Pink7 said: When you calculate panels vs inverter would you limit panels to capacity listed on the panels even you just expect 50%? Pink See what your panels actually produce, fit the real numbers to your inverter numbers. My GTI said max PV max OC 45V, 1000w. My panels said max OC 46V, 320w ............. but actually produced 46V at under 200W. 5 panels in parallel @ 320w worked perfectly for 2 years ............. (they never reached more than 800w) A local Thai builder saw my setup, copied me without asking, 2 panels in series = 90V puff of smoke and burning smell. Edited March 6, 2022 by BritManToo 2 Link to comment Share on other sites More sharing options...
Pink7 Posted March 15, 2022 Author Share Posted March 15, 2022 Now i research a plan for 2 x 5500kv inverters in parallel: So if i set up a single line (all serial) to each inverter, and a battery pack to each inverter. So how to combine 2 x outgoing power from the inverters to House breakers box? Is there a good way to add a option for grid power to direct to breaker box if wanted or needed? Pink This will give a possibility for a step by step plan where i try out with one inverter and half of the panels first Link to comment Share on other sites More sharing options...
Crossy Posted March 15, 2022 Share Posted March 15, 2022 Just now, Pink7 said: So how to combine 2 x outgoing power from the inverters to House breakers box? Is there a good way to add a option for grid power to direct to breaker box if wanted or needed? Task A. is to ensure your inverters are actually able to run in parallel. Grid-tie will naturally parallel but off-grid or off-grid hybrids need to know about each other. If they are off-grid hybrids they will have a grid input, grid goes there. Inverter output goes to the house breaker box. The inverter instructions should show you how to add a bypass switch. It's usual for all the inverters to share a battery pack (or packs in parallel). Why not start a thread and post what you intend doing there? 1 Link to comment Share on other sites More sharing options...
Pink7 Posted March 15, 2022 Author Share Posted March 15, 2022 (edited) 4 hours ago, Crossy said: If they are off-grid hybrids they will have a grid input, grid goes there. Inverter output goes to the house breaker box. The inverter instructions should show you how to add a bypass switch. Something like this? https://www.lazada.co.th/products/3-knife-switch-2p-3p-32a-63a-100a-i2047964700-s6660382746.html? Im going slow on this so im still not sure what to choose. And i need to know what i need etc before ask any here to help wire the AC cables from grid etc etc. But new tread coming for sure when im start ordering. Regarding If they are off-grid hybrids they will have a grid input, grid goes there. Inverter output goes to the house breaker box. The inverter instructions should show you how to add a bypass switch: the 2 inverter outputs connected together or output 1 goes to inverter 2 then output 2 goes to house breaker box? Right now its 2 x powmr 5.5kva ( parallel version) vs the 11kva Mppsolar. 4 hours ago, Crossy said: Edited March 15, 2022 by Pink7 Link to comment Share on other sites More sharing options...
Pink7 Posted March 15, 2022 Author Share Posted March 15, 2022 (edited) https://powmr.com/manuals/PowMr-Manuals-Solar-Inverter-Charger-48V-220V-80A-POW-HVM5.5K-48V.pdf page 40 I see outgoing ac connected to same wire as i expected, so what i try to ask what i should use to combine this 2 ac sources to 1? Pink Edited March 15, 2022 by Pink7 Link to comment Share on other sites More sharing options...
Pink7 Posted August 6, 2022 Author Share Posted August 6, 2022 If a inverter have max 500VDC what value on the solar panel is used to calculate the vdc? Pink Link to comment Share on other sites More sharing options...
Popular Post Muhendis Posted August 6, 2022 Popular Post Share Posted August 6, 2022 1 hour ago, Pink7 said: If a inverter have max 500VDC what value on the solar panel is used to calculate the vdc? Pink If the 500v inverter input relates to the solar panel input (which it probably does) then the maximum number of solar panels per string would be the sum of the open circuit voltages (Voc) of each panel not exceeding 500VDC. In the example label shown, that would be 500VDC/45Voc = 11.11. That's 11 panels in a string. 2 1 Link to comment Share on other sites More sharing options...
Pink7 Posted August 7, 2022 Author Share Posted August 7, 2022 (edited) I was plan to buy panels today then i just find a post in another tread about water heaters and all in one inverter not really a good match. I have 2 x 4500w showers.. So maybe then options is a grid tie inverter? or maybe the low frequency 48V 10Kw diy i post before then with a extra ATS to grid power? Pink Edited August 7, 2022 by Pink7 Link to comment Share on other sites More sharing options...
Muhendis Posted August 7, 2022 Share Posted August 7, 2022 (edited) 1 hour ago, Pink7 said: I was plan to buy panels today then i just find a post in another tread about water heaters and all in one inverter not really a good match. I have 2 x 4500w showers.. So maybe then options is a grid tie inverter? or maybe the low frequency 48V 10Kw diy i post before then with a extra ATS to grid power? Pink Have you considered paralleling three units of 4 or 5 kilowatt inverters? That will give you all the power you need. Also since you are talking off grid you will have batteries. If the day is a bit cloudy and you need more power than the panels can supply, the batteries will take up the slack so to speak. You might also spend some time to make up a chart of power consumption against clock time then develop a few house rules about what is allowed to run and when. Grid power is a relatively bottomless pit in terms of power availability but solar power needs to have it's limitations fully understood and maybe worked around. Edited August 7, 2022 by Muhendis 1 Link to comment Share on other sites More sharing options...
Pink7 Posted August 7, 2022 Author Share Posted August 7, 2022 20 minutes ago, Muhendis said: Have you considered paralleling three units of 4 or 5 kilowatt inverters? That will give you all the power you need. Also since you are talking off grid you will have batteries. If the day is a bit cloudy and you need more power than the panels can supply, the batteries will take up the slack so to speak. You might also spend some time to make up a chart of power consumption against clock time then develop a few house rules about what is allowed to run and when. Grid power is a relatively bottomless pit in terms of power availability but solar power needs to have it's limitations fully understood and maybe worked around. Yes i have think about 2 and also 3 inverters in parallel. And also the 11kw from Taiwan. Then i kind of end up with a plan where i can do this in steps without to large as first solar project: Start with a 5kv inverter and 4kw panels or so as step 1. The 5kv inverter could be the powmr 5.5kw ready for parallel and wifi. Then step to ad batteries. Then if or when want or need ad more inverters/panels/batteries. Pink Link to comment Share on other sites More sharing options...
Popular Post BritManToo Posted August 7, 2022 Popular Post Share Posted August 7, 2022 3 minutes ago, Pink7 said: Yes i have think about 2 and also 3 inverters in parallel. And also the 11kw from Taiwan. Then i kind of end up with a plan where i can do this in steps without to large as first solar project: Start with a 5kv inverter and 4kw panels or so as step 1. The 5kv inverter could be the powmr 5.5kw ready for parallel and wifi. Then step to ad batteries. Then if or when want or need ad more inverters/panels/batteries. Pink Problem being getting extra inverters to match your first one. They seem to change specs every 6 months, and the new ones won't connect to the old ones. 3 Link to comment Share on other sites More sharing options...
Pink7 Posted August 7, 2022 Author Share Posted August 7, 2022 2 minutes ago, BritManToo said: Problem being getting extra inverters to match your first one. They seem to change specs every 6 months, and the new ones won't connect to the old ones. Ok thats for sure a issue. Pink 1 Link to comment Share on other sites More sharing options...
Popular Post Crossy Posted August 7, 2022 Popular Post Share Posted August 7, 2022 Yeah, I've noted many times that it's best to get all your prospective inverters at once. 3 Link to comment Share on other sites More sharing options...
Pink7 Posted August 7, 2022 Author Share Posted August 7, 2022 46 minutes ago, Muhendis said: Grid power is a relatively bottomless pit in terms of power availability but solar power needs to have it's limitations fully understood and maybe worked around. In Europe now there is power issues and also crazy prices on electric power ..I dont know what the chances for same issue here..but for me it was just another good reason to try get this project rolling. Even in the cold north Europe where im from they have waiting times of 6months + to get solar installed, so in this climate solar should be on every roofs. Pink Link to comment Share on other sites More sharing options...
Popular Post Muhendis Posted August 7, 2022 Popular Post Share Posted August 7, 2022 1 hour ago, Pink7 said: In Europe now there is power issues and also crazy prices on electric power ..I dont know what the chances for same issue here..but for me it was just another good reason to try get this project rolling. Even in the cold north Europe where im from they have waiting times of 6months + to get solar installed, so in this climate solar should be on every roofs. Pink On every roof indeed. My idea which is probably same as everyone else, is that all small communities of say 500 households should be independently solarised and connected to each other into a mini grid. 1 2 Link to comment Share on other sites More sharing options...
Pink7 Posted August 8, 2022 Author Share Posted August 8, 2022 Panels ordered today so now i started a new tread for the project here Pink 2 Link to comment Share on other sites More sharing options...
Crossy Posted August 8, 2022 Share Posted August 8, 2022 1 hour ago, Pink7 said: Panels ordered today so now i started a new tread for the project here Pink Let's continue over in the new thread. Link to comment Share on other sites More sharing options...