7 minutes ago, Crossy said:

U mean 3-phase inverters etc?

 

When it comes to 3-phase in Thailand my advice is always "treat it as 3 x single-phase installations" be it automatic voltage regulators or solar inverters.

 

The single most common failure on the 3-phase network here is loss of one phase.

 

A 3-phase AVR or GTI will trip out and you will get zero, if it's 3 x single-phase units two of them will continue to operate.

 

 

Isn't 3* usually what PEA would install.

 

I hope so.

 

 

 

Posted
6 minutes ago, MrJ2U said:

Isn't 3* usually what PEA would install.

I hope so.

 

Only if you ask for it.

 

Thailand LV distribution is 3-phase 4-wire, a normal single-phase supply (which >90% of us have) comes from one phase plus the neutral.

 

Of course, if you have a big place and can't get enough energy from a single-phase supply then request a 3-phase meter and supply. But once past your main breaker still treat it as if its 3 x single-phase supplies.

 

@carlyai What are you actually trying to do?

Posted
5 minutes ago, Crossy said:

 

Only if you ask for it.

 

Thailand LV distribution is 3-phase 4-wire, a normal single-phase supply (which >90% of us have) comes from one phase plus the neutral.

 

Of course, if you have a big place and can't get enough energy from a single-phase supply then request a 3-phase meter and supply. But once past your main breaker still treat it as if its 3 x single-phase supplies.

 

@carlyai What are you actually trying to do?

I was curious.

 

I had 3 phase installed.

 

We've got a pool, 4 refrigerators, 8 air-conditioners. Numerous small appliances.

 

I just assumed they would have put in 3 phase.

 

I didn't realize there's different 3 phase types.

 

 

They put in some new terminals/transformers in the village last week.

I'll take a picture, perhaps I can message you and you might know what it is?

 

It's great we haven't had the power go out since! 

 

  • Like 1
Posted
3 hours ago, Crossy said:

 

Only if you ask for it.

 

Thailand LV distribution is 3-phase 4-wire, a normal single-phase supply (which >90% of us have) comes from one phase plus the neutral.

 

Of course, if you have a big place and can't get enough energy from a single-phase supply then request a 3-phase meter and supply. But once past your main breaker still treat it as if its 3 x single-phase supplies.

 

@carlyai What are you actually trying to do?

I thought I saw someone here who installed 3 phase solar. 

I thought it was red007 but think I'm mistaken.

I understand your comments before about seperate in vetters for each phase.

I hope to start the 3 phase solar project next year after I move my aquaponics.

So mainly was looking for threads of 3 phase installations.

 

Posted
3 minutes ago, carlyai said:

I thought I saw someone here who installed 3 phase solar. 

I thought it was red007 but think I'm mistaken.

I understand your comments before about seperate in vetters for each phase.

I hope to start the 3 phase solar project next year after I move my aquaponics.

So mainly was looking for threads of 3 phase installations.

 

 

Got it.

 

I don't recall a member installing 3-phase solar ???? 

  • Thanks 1
  • 2 weeks later...
Posted

Hi there

 

not DIY, but done by an installer:

Huawei SUM2000-5KTL-M1 5.0Kw, 3 Phase inverter and totally 14 Jinko PV panels 470W, no battery as yet, cost was slightly below 200 KTHB all in.

Running with 0 export most of the time. It is still slightly hazy but we are getting close to 5 kW at the moment.

 

I would have to agree that 3 x 1-phase inverters might have been better due to 1 phase dropping out frequently. At the time of decision I did not think about this possibility but I guess it would have made the setup more expensive and complicated.

 

  • Like 1
Posted
17 minutes ago, a340bangla1 said:

Hi there

 

not DIY, but done by an installer:

Huawei SUM2000-5KTL-M1 5.0Kw, 3 Phase inverter and totally 14 Jinko PV panels 470W, no battery as yet, cost was slightly below 200 KTHB all in.

Running with 0 export most of the time. It is still slightly hazy but we are getting close to 5 kW at the moment.

 

I would have to agree that 3 x 1-phase inverters might have been better due to 1 phase dropping out frequently. At the time of decision I did not think about this possibility but I guess it would have made the setup more expensive and complicated.

 

Hi, yes I'm looking at 3 hybrid inverters (with toroid transformer), cost about B35000 each.

[My Thai Solar friend who was just visiting said 'make sure the inverters have toroid transformers']. I haven't Googled it yet. ????

Posted
44 minutes ago, carlyai said:

Hi, yes I'm looking at 3 hybrid inverters (with toroid transformer), cost about B35000 each.

[My Thai Solar friend who was just visiting said 'make sure the inverters have toroid transformers']. I haven't Googled it yet. ????

Toroid ? Is that a dirty word ? ????

 

I saw them install circular transformers around the 3 phases which I assumed to be current transformers.

 

The 3-phase Huawei inverter (5 kW) was about B30'000

Posted
2 hours ago, a340bangla1 said:

Hi there

 

not DIY, but done by an installer:

Huawei SUM2000-5KTL-M1 5.0Kw, 3 Phase inverter and totally 14 Jinko PV panels 470W, no battery as yet, cost was slightly below 200 KTHB all in.

Running with 0 export most of the time. It is still slightly hazy but we are getting close to 5 kW at the moment.

 

I would have to agree that 3 x 1-phase inverters might have been better due to 1 phase dropping out frequently. At the time of decision I did not think about this possibility but I guess it would have made the setup more expensive and complicated.

 

"no battery as yet"

 

Just a heads-up......  I seem to remember another forum member who has had a Huawei inverter installed discovered after the fact that Huawei some how tie you into using only their batteries, which then turned out to be a very expensive option.  Hope I'm wrong for your sake.

  • Like 1
  • Thanks 1
Posted
1 hour ago, 007 RED said:

"no battery as yet"

 

Just a heads-up......  I seem to remember another forum member who has had a Huawei inverter installed discovered after the fact that Huawei some how tie you into using only their batteries, which then turned out to be a very expensive option.  Hope I'm wrong for your sake.

I have no plans for batteries at the moment but I might consult my installer to find out if there is such a restriction.

Posted
1 hour ago, a340bangla1 said:

My supplier confirmed this morning that "at this moment" only Huawei batteries can be connected

That's my understanding also from the contractor who did my installation.

  • Like 2

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...