Well today one of my daughters informed me that she received an electric shock from the railings on top of the outside wall, on the side of our (rented)house!! Anyway whilst questioning the wife about this and her saying "Chinese lady say because of rain, ok now" :blink: the other daughter has grabbed a different section of the railings and has indeed received an electric shock clamping her hand to the rail.After prising her off and getting the odd job man out with his voltmeter the said railings were indeed 220v.

Now according to the odd job man the problem came from a neighbours old outside light which somehow has caused the railings on top of our wall to become live. Anyway he (the neighbour) has cut the cable beneath the switch and the rails are no longer live.

Can someone explain/guess how this has happened ?

here are some pics to help

post-3823-0-87358900-1305456017_thumb.jp the old switch

post-3823-0-54981500-1305456520_thumb.jp the hole near the wall where the old fitting was

post-3823-0-51035100-1305456251_thumb.jp the wall and railings from neighbors side, just above the fitting hole

post-3823-0-92865600-1305456194_thumb.jp same from our side

How did this make our railings live and can I be sure that we are now safe ?

One good thing is my daughters now fully understand the power of electricity.

Link to comment
Share on other sites

Pictures don't tell anything. My guess, might have tried to add a "earth" or Ground" and tapped one of the 220V terminals instead of the ground terminal on the switch.

Very poor electricians here.

Link to comment
Share on other sites

ok will try again.

That round hole in photo 2 is at the foot/base of our wall post in photo 3 and is supposedly where an old light (?)fitting was that was operated by the switch in photo 1.This somehow made the railings atop our wall live ???

Edited by parryhandy
Link to comment
Share on other sites

I suspect that the railings are in contact with (or welded to) the re-bar inside the wall.

A pound to a penny that the re-bar is exposed (or near the surface) inside the hole where the old light resided.

Poor housekeeping when the fitting was removed left a live wire exposed.

Getting wet from the rain provided a current path from said live to the re-bar.

QED.

Link to comment
Share on other sites

I suspect that the railings are in contact with (or welded to) the re-bar inside the wall.

A pound to a penny that the re-bar is exposed (or near the surface) inside the hole where the old light resided.

Poor housekeeping when the fitting was removed left a live wire exposed.

Getting wet from the rain provided a current path from said live to the re-bar.

QED.

One would agree with you here, light circuit wiring not terminated in an approved manner. An RCD on the lighting circuit would have isolated the supply.

Link to comment
Share on other sites

I suspect that the railings are in contact with (or welded to) the re-bar inside the wall.

A pound to a penny that the re-bar is exposed (or near the surface) inside the hole where the old light resided.

Poor housekeeping when the fitting was removed left a live wire exposed.

Getting wet from the rain provided a current path from said live to the re-bar.

QED.

This makes sense and is pretty much what the wife said, but why does the current not travel to earth through the rain and out of interest would it have been costing the neighbour money i.e. causing his meter to spin.

Link to comment
Share on other sites

I suspect that the railings are in contact with (or welded to) the re-bar inside the wall.

A pound to a penny that the re-bar is exposed (or near the surface) inside the hole where the old light resided.

Poor housekeeping when the fitting was removed left a live wire exposed.

Getting wet from the rain provided a current path from said live to the re-bar.

QED.

This makes sense and is pretty much what the wife said, but why does the current not travel to earth through the rain and out of interest would it have been costing the neighbour money i.e. causing his meter to spin.

Leakage current only due to moisture. It takes about 10watts @ 220volts to operate (cause the disc to rotate) of a kWh meter.

Edited by electau
Link to comment
Share on other sites

You should buy a lottery ticket while you luck holds, 2 kids and 2 seperate life threatening situations. Give them both a big hug as well and be thankful it is still possible.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.




×
×
  • Create New...