Jump to content

Recommended Posts

With your reference to power boards or power strips the polarity is normally in Thailand looking at the socket outlet in a clockwise direction is E, N, L. This complies with Thai Industrial Standards and the NEC standard.

Yes, the earth terminal may not have a earth conductor connected at the terminal. They often have only a 2 pin plug top and 2 core lead.

In all cases if a switch is fitted as an integral part of the power board it must operate in the L conductor.

IEC, British standards and AS3112 the polarity is E, L, N. In this case the standard requires that the power board is fitted with a 3 core lead and 3 pin plug top, with the earth conductor connected to the earth terminal.

You do not rewire power boards, you replace them.

Reversal of polarity at a socket outlet is not a safety issue providing the L conductor is switched.

Removing the plug top from the socket outlet complies with the switching requirement (in Thailand).

Link to comment
Share on other sites

Oh man, Crossy, you, of all people, left the country while your house was being wired? I had you pegged as the electrical god. Now you've sunk to expert, but mortal!

As for rewiring a electrical strip to correct polarity and connecting a ground, of course you can. Why not? Anybody that knows how and can solder is perfectly capable of doing this -- and doing it better than they could do it at the factory, apparently. I do a lot of rewiring of things here. Sometimes its because rats have chewed up the original wires. Sometimes it's the only alternative. The plug strips I rewired had a three pin plug and a three hole receptacle, but only a two core lead, which is what I replaced. A bit of a scam, those things.

I also have a 110V Makita lithium ion battery, model DC18RA, that I converted to 220V for use in LOS. I am not sure why, but the 110V version can be had for $30-40, while the 220V version goes for $100+. I converted two of them and the conversion took about a nickel's worth of electronic parts. Since the plug is designed to assure correct polarity, I always make sure it gets it. Has worked great through hundreds of recharges over three years.

Not knowing what the Thai standard is, being American, I have wired everything to the NEC standard, so I got lucky with the Thai standard. Funny, the British standard is different. Hmmm, they drive on the wrong side of the road, too. (-:

Link to comment
Share on other sites

With your reference to power boards or power strips the polarity is normally in Thailand looking at the socket outlet in a clockwise direction is E, N, L. This complies with Thai Industrial Standards and the NEC standard.

Yes, the earth terminal may not have a earth conductor connected at the terminal. They often have only a 2 pin plug top and 2 core lead.

In all cases if a switch is fitted as an integral part of the power board it must operate in the L conductor.

IEC, British standards and AS3112 the polarity is E, L, N. In this case the standard requires that the power board is fitted with a 3 core lead and 3 pin plug top, with the earth conductor connected to the earth terminal.

You do not rewire power boards, you replace them.

Reversal of polarity at a socket outlet is not a safety issue providing the L conductor is switched.

Removing the plug top from the socket outlet complies with the switching requirement (in Thailand).

Thanks...good info.

Most of the 3 wire/plug power strips I've seen/bought in Thailand come wired/marked IAW with the British Standards/AS3112 as mentioned above...most have been made in China. That is, when looking at a power strip outlet with the E at 12 o'clock, the L is at 3 o'clock and the N at 9 o'clock. However, most of the 3 wire/plug wall outlets I've bought are marked with the E at 12, L at 9 and N at 3 o'clock. But the Safe-T-Cut GFCI/RCD wall outlets were wired E at 12, L at 3, and N at 9 o'clock.

I opened up most of the power strips to install/replace MOV surge protection across all three lines for three modes of surge protection....and in many cases if I wanted to rewire the L & N polarity it would not have been an easy or quick job especially if I wanted to keep the circuit breaker/fuse & switch in the high/hot side of the line for safety purposes. And in some cases it really wasn't possible to rewire if I wanted to keep the fuse and switch in the high side of the line...and even ensure the high/hot side went to the fuse holder rear connector. It's important to power to a switch/fuse/breaker in the high/hot side of the line to ensure power can be killed or force the CB/fuse to blow if there is an internal short/fault on a device which allows current flow via Earth versus Neutral (assuming you have a 3 wire setup)...with a fault to Earth but the CB/fuse/switch being in the Neutral line the item could remain powered up with current flow from Earth to Hot/Live..plus also making the case of the item a shocking hazard.

For "polarity" purposes I really don't worry if the L & N are reversed since the three slot outlets almost always (let's say 80 to 90% of the time) have a two prong device being plugged into the strip (i.e., no Earth 3rd wire)...and whether the strip's L & N connections are wired correctly/in accordance with standard XYZ when plugging in a two prong/non polarized/non earthed plug which I can plug in two different ways with a mere 180 degree rotation (i.e., flip polarity) is the predominate plug on devices like TVs, stereos, DVD, TV set-top boxes, modem/routers, rice cookers, microwaves, fans, electric shavers, electric hair clippers, and many-many other devices....for these devices the L & N polarity on a power strip or wall outlet is really a non-issue. And then most of our two wire plug in devices now days are contained within plastic/non-conductive cases which greatly reduces the chance of an internal Hot to equipment case fault causing a shocking hazard....plus most of these devices will not have an external fuse holder (or CB) to potentially cause a shocking hazard if wired incorrectly (i.e., Hot wire not wired to rear of fuse connector) when removing a fuse with the device still plugged in.

With so many different electrical standards in the world for building wiring and equipment wiring it's almost like we don't really have "a standard." Throw in all the two wire devices we have in our home and work place today, it's almost like having a Earth wire or even being concerned about polarization is becoming a non-issue. But with that being said, whenever possible to have a 3 wire connection "with that Safety Important Earth wire" it's definitely the safe way to go....and I definitely try to wire my home in accordance with as "few" electrical standards as possible/safe. My goal is to ensure an Earth wire whenever possible (but most devices now days as mentioned above come without an earth wire--just two wire...and also ensure I standardize my wall outlets L & N polarity even if my two wire devices could care less about polarity).

Edited by Pib
Link to comment
Share on other sites

Oh man, Crossy, you, of all people, left the country while your house was being wired? I had you pegged as the electrical god. Now you've sunk to expert, but mortal!

Not knowing what the Thai standard is, being American, I have wired everything to the NEC standard, so I got lucky with the Thai standard. Funny, the British standard is different. Hmmm, they drive on the wrong side of the road, too. (-:

Sheer bad luck that was, but earning money is quite high on my list of important activities. The problem was chiefly that our initial sparks, whilst pretty good, was a piss-head and got his 'brother' to run the cables. Brother is not a sparks and decided that rather than running a single piece from DB to outlet he took the easy option of running about 4 bits per run, his joints were carp even using the 'foolproof' Wago connectors I gave him.

The Thai standard is broadly based on the NEC, you hit pay-dirt there :)

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.








×
×
  • Create New...
""