Jump to content

Recommended Posts

Posted

In many places in South east Asia, the electricity is unreliable. Many places have generators, so I am always concerned about a spike / surge.

My home country has 3 pin plugs and powerpoints.

Generally, Thailand appliances use 2 pin plugs and have 2 pin powerpoints.

I have been plugging the electonic devices I have bought with me into a 3 pin surge protector, and then plugging that into an adapter with 2 pins and then plugging the adapter into the powerpoint. A LED lights up showing the surge protector operating.

Is this a waste of time, or does this still give me some surge protection? I have received some conflicting opinions about it.

For my laptop, I am using a Belkin surge protector. See the link.

http://www.belkin.com/au/F5C791-C6/p/P-F5C791-C6/

The box it came in says it works "in any country." It comes in a 3 pin or 2 pin, depending on the laptop company and the charger they use.

I bought a 3 pin. Will this product still work "in any country" when Belkin would be aware there are many countries that only have 2 pin powerpoints?

I know it can't hurt to use the thing anyway, but thought I would consult members of the forum.

I am on the road a lot, so please don't mention a UPS, but I am open to any other suggestions that will ensure my electonic devices don't get fried. :)

Posted

OK guys, a 3-pin arrestor plugged into a 2-pin outlet will provide some protection (L-N surges), better than nothing.

Things will of course work better if you have a 3-pin outlet or connect the ground pin to a grounded point.

  • Like 2
Posted

OK guys, a 3-pin arrestor plugged into a 2-pin outlet will provide some protection (L-N surges), better than nothing.

Things will of course work better if you have a 3-pin outlet or connect the ground pin to a grounded point.

Yes thats right. I just changed all the outlets in my house to 3 pin. The surge protector i linked is 3 pin with a 2 pin plug for the outlet and in the specs it lists the protection provided. But i guess gerry123 was too "dim" to read the specs.

Posted

If the surge protector is not grounded, it shows a red light, a green one, if grounded.... (at least on mine, two types ... one is Belkin)

My way around this was to plug in a two pin line from source, to a three pin outlet, (electrical stores have) I ran a ground line from the three pin outlet, to a copper ground pipe out side...

It's not really difficult to do (as long as not in a highrise! )

Posted

You say you brought 3 pin equipment from your home country, if that was the UK,

you should realize that the L -N poles are reversed here,a 3 pin socket here

has L on the left and N on the right.so a 3 pin plug with fuse will not be protected

as the fuse will be on the N side. I don't know which side is normal in the rest of

Europe or U.S..A.

regards worgeordie

Posted

OK guys, a 3-pin arrestor plugged into a 2-pin outlet will provide some protection (L-N surges), better than nothing.

Things will of course work better if you have a 3-pin outlet or connect the ground pin to a grounded point.

In layman's terms, can you tell me what type of surge this would protect against, and what type of surge it offers no protection against?

I don't expect a small surge protector to protect against a lightening strike, but was hoping for some protection when the main power goes off, the generator kicks in, and then the main power comes back on, and the generator goes off.

Would a small surge protector, like the one in my link, offer protection in this case?

Posted

If the surge protector is not grounded, it shows a red light, a green one, if grounded.... (at least on mine, two types ... one is Belkin)

My way around this was to plug in a two pin line from source, to a three pin outlet, (electrical stores have) I ran a ground line from the three pin outlet, to a copper ground pipe out side...

It's not really difficult to do (as long as not in a highrise! )

I know some surge protectors have 2 LED lights. A red and a green.

The one I maily use to charge phone, camera and music player just has one small red LED which lights up in a 3 pin powerpoint in my home country, and also in a 2 pin powerpoint in South East Asia.

My chargers still charge, but with no third pin here, is this offering me any protection?

Posted

I think it really depends on the type of problems you're likely to experience.

Direct lightning strike to the power line?

Indirect lightning strike to the power line?

Increased voltage?

Voltage spikes?

Decreased voltage?

Brown-outs?

Drop-outs?

Out of spec current?

A surge protector is really only protective to large momentary voltage spikes. All the other issues that can impair or destroy your electronics ... not gonna do a thing.

Better to take a look at UPS and Power Conditioners.

And if your equipment is not only designed to 'clamp' high voltage, but also 'shunt' it to grount ... and the ground isn't there. Then that protection isn't going to be effective either.

I really liked to refer people to articles like the one at TheWireCutter.com that partially explains how surge protections work:

How surge protectors work

To understand the tests we did, you need to know a little about how surge protectors work. Fortunately, they’re simple.

Surge protectors rely mainly on devices called metal-oxide varistors, or MOVs. A MOV works sort of like a runaway truck ramp on a mountain pass. Just as the ramp routes the truck off the highway so it can’t do any harm, then slows the truck to a stop, an MOV routes surges and spikes off the main electrical line then dissipates their energy so it can’t harm whatever’s plugged into the surge protector.

A MOV is connected across two conductors of an AC line. Below a certain voltage, the MOV doesn’t conduct electricity. Above a certain voltage, it conducts, effectively “shorting out” the surge so it can’t damage the components connected to the surge protector. A voltage surge that exceeds the capacity of the MOV will cause it to short completely. Like a paper clip plugged across a wall outlet, the shorted MOV instantly blows open (think July 4th). To minimize the fireworks potential, there’s usually a fuse in series (in line) with the MOV. It is designed to blow before the fireworks begin. Unfortunately, when the fuse goes, the MOV is also removed from the circuit and you have no surge protection at all.

MOVs are rated in joules. The joule is a measure of quantity, not level. Where a volt is like the force behind a boxer’s punch, a joule is like the damage done to his opponent by the punch. It’s the total amount of delivered energy, whereas a volt is a momentary measure of energy intensity. Just like punches, the effects of joules add up. The rating of an MOV—or a surge protector with a joule rating—indicates the total energy it can absorb from electrical spikes and surges before failure. So 100 1-joule spikes will wear out an MOV the same as a single 100-joule spike.

If this is giving you the idea that surge protectors don’t last forever, you’re catching on. The more MOVs employed, and the higher the joule rating on the MOVs, the longer the surge protector will continue to function.

I don't expect a small and cheap device to protect my electronics from a seriously major overload like a lightening strike.

As I said in the other post, just when the main power goes off and a generator kicks in, and then when the main power comes back on, and the generator turns off.

I know a UPS is good, but I do not want to carry one of these around with me because I am on the road a lot.

Posted (edited)

OK guys, a 3-pin arrestor plugged into a 2-pin outlet will provide some protection (L-N surges), better than nothing.

Things will of course work better if you have a 3-pin outlet or connect the ground pin to a grounded point.

In layman's terms, can you tell me what type of surge this would protect against, and what type of surge it offers no protection against?

I don't expect a small surge protector to protect against a lightening strike, but was hoping for some protection when the main power goes off, the generator kicks in, and then the main power comes back on, and the generator goes off.

Would a small surge protector, like the one in my link, offer protection in this case?

I am using one similar to the one i linked and so far (3 years ) no problems. Yes its not earthed. Dont charge your devises during storms.

We have a generator cut in 3 to 6 times every day.

Edited by stat088
Posted

As mentioned above the Metal Oxide Varistor (MOV) is the primary protection device in surge protectors although some may have some other components also. But at the minimum, the MOV is the device providing the bulk of protection. If your surge protector has "one" MOV installed and it happens to be installed across Line to Ground, well, if it's plugged into a two hole outlet (i.e., no ground) you will have no protection because the Ground is not connected.. If the MOV was installed across the Line to Neutral then you have one line mode protection whether plug into a 3 or 2 hole outlet.

I have modified all the surge protector strips I've bought to include a MOV across the Line to Neutral, Line to Ground, and Neutral to Ground to provide protection in all three modes which surges can ride in on. Now when I took the strips apart to do my modification, I found some had their one each MOV installed from from Line to Ground and some Line to Neutral.

Posted

OK guys, a 3-pin arrestor plugged into a 2-pin outlet will provide some protection (L-N surges), better than nothing.

Things will of course work better if you have a 3-pin outlet or connect the ground pin to a grounded point.

In layman's terms, can you tell me what type of surge this would protect against, and what type of surge it offers no protection against?

I don't expect a small surge protector to protect against a lightening strike, but was hoping for some protection when the main power goes off, the generator kicks in, and then the main power comes back on, and the generator goes off.

Would a small surge protector, like the one in my link, offer protection in this case?

I am using one similar to the one i linked and so far (3 years ) no problems. Yes its not earthed. Dont charge your devises during storms.

We have a generator cut in 3 to 6 times every day.

I've never had a surge burn one of these out, but that could be because I have never had a surge. :)

I don't charge anything during a storm.

When the generator cuts in, and then the mains electricity turns back on, this is when I fear a spike the most.

Posted

As mentioned above the Metal Oxide Varistor (MOV) is the primary protection device in surge protectors although some may have some other components also. But at the minimum, the MOV is the device providing the bulk of protection. If your surge protector has "one" MOV installed and it happens to be installed across Line to Ground, well, if it's plugged into a two hole outlet (i.e., no ground) you will have no protection because the Ground is not connected.. If the MOV was installed across the Line to Neutral then you have one line mode protection whether plug into a 3 or 2 hole outlet.

I have modified all the surge protector strips I've bought to include a MOV across the Line to Neutral, Line to Ground, and Neutral to Ground to provide protection in all three modes which surges can ride in on. Now when I took the strips apart to do my modification, I found some had their one each MOV installed from from Line to Ground and some Line to Neutral.

If I was to buy a surge protector in Thailand, like one of the power boards with surge protection, and this only has a 2 pin plug, would that mean it must have the MOV from Line to Neutral, and offer at least some protection rather than possibly no protection?

Posted

If I was to buy a surge protector in Thailand, like one of the power boards with surge protection, and this only has a 2 pin plug, would that mean it must have the MOV from Line to Neutral, and offer at least some protection rather than possibly no protection?

Correct.

Posted

If I was to buy a surge protector in Thailand, like one of the power boards with surge protection, and this only has a 2 pin plug, would that mean it must have the MOV from Line to Neutral, and offer at least some protection rather than possibly no protection?

Correct.

Thanks.

I'll go and buy one here. I thought a surge protector bought in my home country would be better quality and more reliable. I paid a bit for the Belkin laptop surge protector because it did say "works in any country." I guess that means the little LED lights up, and that's about it. :)

Posted

That Belkin unit due to its price and connected equipment warranty will certainly have 3 MOVs, with no ground it will provide L-N protection just like one of the cheapies, no need to get anything further.

Switching spikes are unlikely to be of sufficient magnitude to damage modern kit, so the transfer to/from genset shouldn't be a worry.

Posted (edited)

That Belkin unit due to its price and connected equipment warranty will certainly have 3 MOVs, with no ground it will provide L-N protection just like one of the cheapies, no need to get anything further.

Switching spikes are unlikely to be of sufficient magnitude to damage modern kit, so the transfer to/from genset shouldn't be a worry.

Thanks.

Whenever the power goes off, I have a few seconds before the generator starts up. I run to the powerpoints and disconnect everything. smile.png I thought the generator could send a spike down the line on it's initial start up.

The Belkin is slim and lite. It's good for traveling. Anyway, some coverage is better then none. I'll continue to use the surge protectors I have.

Edited by KhunHeineken
Posted

Funny, I just took apart one of those local, "heavy duty looking" extension cords on a roll up/wheel-type chassis, due to ant infestation. Opened the fuse recepticle to find there was no fuse inside! Once I got the chassis open, saw there was a 1/4" red wire off the back of the fuse recepticle, connected to......... nothing. sad.png

Posted

Funny, I just took apart one of those local, "heavy duty looking" extension cords on a roll up/wheel-type chassis, due to ant infestation. Opened the fuse recepticle to find there was no fuse inside! Once I got the chassis open, saw there was a 1/4" red wire off the back of the fuse recepticle, connected to......... nothing. sad.png

Is this something you previously purchased 'New' from a reputable retailer?

The QC in those Chinese sweat shops isn't what it used to be. You should complain.

Posted

Don't worry about the spikes, Enron today in bkk suffering brown outs and I live behind a feeder. And whatever the fault was it was sinking enough juice to have the neon indicator lights on a powerstrip go dark and still allow a floor fan to run. Everything else dropped off instantly due to serious underv. This will burn out so many things much more effectively than surges.

Posted

Funny, I just took apart one of those local, "heavy duty looking" extension cords on a roll up/wheel-type chassis, due to ant infestation. Opened the fuse recepticle to find there was no fuse inside! Once I got the chassis open, saw there was a 1/4" red wire off the back of the fuse recepticle, connected to......... nothing. sad.png

As an alternate to the fuse, just put a "Safety First" sticker on it and continue to use it as that what a Thai company would probably do. In fact look close and you should be able to find a faded sticker on it somewhere.

Posted

Funny, I just took apart one of those local, "heavy duty looking" extension cords on a roll up/wheel-type chassis, due to ant infestation. Opened the fuse recepticle to find there was no fuse inside! Once I got the chassis open, saw there was a 1/4" red wire off the back of the fuse recepticle, connected to......... nothing. sad.png

As an alternate to the fuse, just put a "Safety First" sticker on it and continue to use it as that what a Thai company would probably do. In fact look close and you should be able to find a faded sticker on it somewhere.

No Hab Stick-uh. Wear amulet, no probrum.

I did, however, get the ants out of the switch housing so it's back in business as the outdoor patio extension near the rain gutter downspout where I plug in my submersible, 2-pin fish pond pump....which came from the same reputable retailer. tongue.png

Posted

Many years ago I was discussing 'Surge Protection' with an avionics engineer.

He told me I would not believe how 'Bad' UK mains electrical supply was.

Some months later we where at a UK aircraft manufacturer where he had been quite senior before changing jobs.

He took me into a Hanger and spoke to a mate of his, Show John the mains supply on an Oscilloscope if you would.

Nice sinusoidal wave, OK now enlarge, Spikes, monsters and thats from a well moderated system.

I bought a Surge Protector as soon as possible and still use it here, but as this thread has suggested I am wasting my time.

john

Posted

Sure when you enlarge the line/sine wave you can see all types of low level noise/garbage (a couple of volts maybe) continuously riding the line...you could probably see that in most any country...and it can be worst in some areas of the country (especially around airports) than others and varies throughout the day and night. But it's those BIG surges/spikes of several hundred (or more) volts for a few micro/milliseconds that occasionally come along due to lightning, large motors turning on/off, arc welding activity, etc., is what zaps stuff.

Posted

Funny, I just took apart one of those local, "heavy duty looking" extension cords on a roll up/wheel-type chassis, due to ant infestation. Opened the fuse recepticle to find there was no fuse inside! Once I got the chassis open, saw there was a 1/4" red wire off the back of the fuse recepticle, connected to......... nothing. sad.png

I have no formal training in the electrical industry, so pardon my ignorance, but I thought the fuse was overload protection. That is, if you put too many appliances on the power board, like a big fridge, a cooker, a fan etc and PULL more than about 2000w, it would blow the fuse to protect wiring in the house heating up and possibly causing a fire.

I didn't think these fuses offered protection for a surge that was PUSHED down the line.

Does the fuse also work in reverse, and offers surge protection?

Posted

Don't worry about the spikes, Enron today in bkk suffering brown outs and I live behind a feeder. And whatever the fault was it was sinking enough juice to have the neon indicator lights on a powerstrip go dark and still allow a floor fan to run. Everything else dropped off instantly due to serious underv. This will burn out so many things much more effectively than surges.

I didn't know the lack of the right amount of electricity can do damage. I thought the appliance would just stop working.

How does fading electric burn out electronics and appliances?

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...