Electrical Problem

Featured Replies

Hi everyone, would there be an electrician on here from either Australia , New Zealand, UK etc? I have a question about an air conditioner my fiancee had installed while I was in oz. The a/c is split system, the motor/compressor is outside near the garden. I returned home here in Chiang Mai, yesterday, and while watering the garden and admiring the work my fiancee had done when I leaned on the a/con unit and got a slight electric shock. I wasn't sure whether it was electricity stored from my body so I touched it again. Sure enough, I got another boot. I had wet feet and was standing on the wet ground, My fiancee said she had various workers here doing an extension on the house and thinks the sparky was not registered. My question is, what can I do to the unit to stop the electric shock? Do I need another electrician or can I put an earth strap somewhere or whatever needs doing to stop it.

Cheers.

Is the house power supply grounded correctly ( meaning the breakers etc ... )  ??  were copper hods installed and connect to the box ?  Sounds like the AC compressor just requires an additional grounding.

  • Author

I couldn't say whether its grounded correctly or not. what is/are a copper hods? I thought the a/c just needs an earth put somewhere, but Im no electrician. I know in oz the houses have an earth wire staked into the ground.

11 minutes ago, RZ Supra said:

earth wire staked into the ground.

No different here.

Copper rods or zinc-plated "spears" are available at the hardware stores.

Mostly quite hidden, needs a good search.

Use a 1 meter long type.

 

38575388.jpg

  • Author

Ah, ok. Do I just wire it to the metal unit then stake it to the ground or is there an earth connector, in the wiring box in the unit, that I connect it to?

46 minutes ago, RZ Supra said:

Ah, ok. Do I just wire it to the metal unit then stake it to the ground or is there an earth connector, in the wiring box in the unit, that I connect it to?

There is an earth connection in the outdoor unit which sadly Thai AC installers rarely use.

 

Having a decent ground is not only for your personal safety but is essential in the surge suppression and filter circuits of many inverter units.

  • Author

Ok, thanks everyone who replied. I will be off to Homepro for a copper rod and other bits tomorrow.

Cheers.

 

It's actually a copper-plated steel rod.  Solid copper would be way too soft to pound into the ground (not to mention expensive).  You'll need at least a baby sledge hammer too.  An ordinary hammer will get you half-way down at best.

All good stuff above.

 

But our OP would be wise to check the rest of the house wiring for correct grounding, particularly any water heaters. That tingle could be rather larger when you're in the shower and wet.

 

Also look for an RCD/RCBO, essential protection from electric shock.

 

Don't know what you have? Post some photos.

 

"I don't want to know why you can't. I want to know how you can!"

15 hours ago, RZ Supra said:

Ok, thanks everyone who replied. I will be off to Homepro for a copper rod and other bits tomorrow.

Cheers.

 

Don't forget that if you put the rod into earth that is bone dry, or that can get bone dry, then it will be ineffective. Earth rods should be in permanently damp soil to work well.

 

My recommendation is at least 1 ½ to 2 metres.

  • Author

Hi everyone, thanks for all of your feedback. I bought a 5/16(8mm) x 6ft(1.8mt) solid copper rod plus a copper clamp and (copper?) bolt and 2.5mm square earth cable. I managed to belt the rod about 2/3rds the way into the ground ( 4ft or 1.2mt ) with a very small hammer that came in a cheap tool kit. I then wired, all 4 a/c units, with the 2.5mm cable and bolted the 4 wires to the rod. I noticed that only 1 a/c unit was giving me an electrical shock when I was playing with the cable. I can now touch that a/c unit, with wet feet and ground, and not get a boot from it. I feel much better now knowing I can leave the little lady, while I go back to oz to work, at home and not get electrocuted. I am guessing 2.5mm cable is sufficient in size? Thanks to all of you for your advise. It's the first time I needed to ask a question on here, no doubt it won't be the last. Cheers.

You might want to take off enough of the skins on the AC unit giving you the buzz to check for ant/gecko infestation.  That could be causing the tingle and could eventually take out a relay and/or PCB.  So far I have had to replace 3 relays on my conventional AC's due to ants.

  • Author

Oh, Thanks for that. something else I didn't need to know. haha. I have managed to smash the the rod in the ground further. now it's down 5ft. I hope that totally fixes any problems. I'd sent pics but my iPhone doesn't want to communicate with my MacBook. haha. absolutely stoked with the help here. My next project is to fix the water leak somewhere in the mains line. The housing estate we live in is about 5 years old and now we have problems with the mains pressure. and leakage.????

14 hours ago, RZ Supra said:

My next project is to fix the water leak somewhere in the mains line.

 

Water leaks are always fun.

 

The DIY forum is here  https://forum.thaivisa.com/forum/124-diy-housing-forum/ for when it all goes wrong.

 

Good luck!

 

"I don't want to know why you can't. I want to know how you can!"

Create an account or sign in to comment

Recently Browsing 0

  • No registered users viewing this page.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.