Have good municipal water supply that feeds the ground floor tank.

 

Mitsubishi pump pumps water from ground floor tank to roof tank. 

 

Float valves in both the ground floor and roof tanks control the water levels.

 

The issue is that when the roof tank is full, the ground floor pump shuts off and on for almost an hour until the float valve settles down and flow stops completely. It looks like it used to have an electric control, but is in not operational and (apparently) incomplete.

 

The problem is that I do not want to get on the roof to repair or replace the electric control. 

 

The plan is to install an on-delay relay and contactor to control the pump such that it (the pump) will only come on once an hour. 

 

Anyone think of a reason this would not work or why it might be a bad idea?

 

 

 

 

Posted

OP, get the guys from the local pump shop, they will work out the solution, get up on the roof etc, all for a couple of hundred baht. 

It sound like either adjustments to the float or the pump.

Posted

A pump delay timer would work if the demand from roof tank will allow it. I would add override switch to the timer and start with 30 minutes then increase if required. This will only work if the pressure switch never cuts the pump when ball valve is fully open.

 

Another method would be adding additional pressure storage at the pump to increase time between cycles as ball valve closes.

 

Constant pressure control is another method but not straightforward modification on a regular house pump.

Posted
10 hours ago, Fruit Trader said:

A pump delay timer would work if the demand from roof tank will allow it. I would add override switch to the timer and start with 30 minutes then increase if required. This will only work if the pressure switch never cuts the pump when ball valve is fully open.

 

Another method would be adding additional pressure storage at the pump to increase time between cycles as ball valve closes.

 

Constant pressure control is another method but not straightforward modification on a regular house pump.

3

 

The roof tank lasts us two days, so that should not be an issue.

 

I did plan to add an override.

 

Not sure what you mean by: "This will only work if the pressure switch never cuts the pump when ball valve is fully open."

 

There is no pressurized storage now, beyond what is in the pipe from the pump to the tank. I'm not clear how adding a pressure tank would help, unless it had an air bladder of some kind.

 

I think constant pressure might be cost prohibitive. 

 

Thanks for the help.

 

 

 

Posted
13 hours ago, Peterw42 said:

OP, get the guys from the local pump shop, they will work out the solution, get up on the roof etc, all for a couple of hundred baht. 

It sound like either adjustments to the float or the pump.

Thanks, but I've had three guys out, one said nothing was wrong, one said I needed to repipe (still waiting for the quote) and the last said I need an electrician.

Posted
19 minutes ago, Yellowtail said:

Not sure what you mean by: "This will only work if the pressure switch never cuts the pump when ball valve is fully open."

I assume the timer will prevent the pump from starting again after the pressure switch stops the pump. It would be undesirable if this happened before the tank filled to the start of ball valve closing.

 

19 minutes ago, Yellowtail said:

There is no pressurized storage now, beyond what is in the pipe from the pump to the tank. I'm not clear how adding a pressure tank would help, unless it had an air bladder of some kind.

So you are running a pump and pressure switch without any pressure vessel. By adding additional pressure storage like a 20L bladder tank, the pump would cycle less as ball valve started to close.

 

You do not say what kind of pump arrangement you are using to send water to a roof above five floors.

Posted
18 hours ago, Fruit Trader said:

I assume the timer will prevent the pump from starting again after the pressure switch stops the pump. It would be undesirable if this happened before the tank filled to the start of ball valve closing.

 

Almost. The timer will prevent the pump from starting for a period after the pressure switch comes back on.

 

18 hours ago, Fruit Trader said:

So you are running a pump and pressure switch without any pressure vessel. By adding additional pressure storage like a 20L bladder tank, the pump would cycle less as ball valve started to close.

 

You do not say what kind of pump arrangement you are using to send water to a roof above five floors.

1

That is correct, although I assume the pump has an integral pressure vessel. 

 

The bladder tank would be full of air, correct? I can see how that could work. I think I can try this with a length of pipe.

 

The pump is a Mitsu EP-355Q5, and it will pump 750l to the roof in 20-30 minutes. The WP type might be better given it has a bladder but the EP is less than 2 years old and I would rather not replace it. Long term I want to do a full repipe.

 

 

Posted
1 hour ago, Yellowtail said:

The pump is a Mitsu EP-355Q5, and it will pump 750l to the roof in 20-30 minutes. The WP type might be better given it has a bladder but the EP is less than 2 years old and I would rather not replace it. Long term I want to do a full repipe.

The EP has an integrated pressure vessel with a bladder. The WP series has no bladder, it sits on the pressure vessel and needs bleeding occasionally. The EP is designed for things like an instant hot water shower  

Posted
3 minutes ago, sometimewoodworker said:

The EP has an integrated pressure vessel with a bladder. The WP series has no bladder, it sits on the pressure vessel and needs bleeding occasionally. The EP is designed for things like an instant hot water shower  

But the WP would have a much greater volume of air to compress than the EP, yes?

Posted

I may be missing something here, but why have a roof tank? why not just connect the pump to the outlet from the roof tank, your still pumping the same volume of water.

Posted
2 minutes ago, CGW said:

I may be missing something here, but why have a roof tank? why not just connect the pump to the outlet from the roof tank, your still pumping the same volume of water.

A bigger reserve of water and we still have water in the event the power or pump goes out.

Posted
34 minutes ago, CGW said:

I may be missing something here, but why have a roof tank? 

Yes you are. There a often power cuts sometimes several hours long with a roof tank you can still have a shower or use the toilets and wash up any time. The water can also be cut from time to time so with 7,500 litres at low level and 1,000 in the roof we would be OK for a couple of months (one water cut was about 5 weeks)

 

Though with my system I have a small cheap pump that fills the high level tank if the village water pressure is too low. Then I have a pump in the roof to pressurise the water system.

 

if you have a constant power and water supply things are different but TIT.

Posted
2 hours ago, Yellowtail said:

The pump is a Mitsu EP-355Q5, and it will pump 750l to the roof in 20-30 minutes. The WP type might be better given it has a bladder but the EP is less than 2 years old and I would rather not replace it. Long term I want to do a full repipe.

The EP-355Q5 series is in the compact range which is likely to include flow and pressure control.

 

If fitted, the electronic module has a reed switch flow sensor along with input from the pressure switch. You will need to decide the best place to introduce time delay as the module will be looking for flow when pressure switch calls the pump on.

Posted
3 minutes ago, Fruit Trader said:

The EP-355Q5 series is in the compact range which is likely to include flow and pressure control.

 

If fitted, the electronic module has a reed switch flow sensor along with input from the pressure switch. You will need to decide the best place to introduce time delay as the module will be looking for flow when pressure switch calls the pump on.

 

I'm thinking I'd put the on-delay (and contactor) between the pressure switch and the pump motor. 

Posted
7 minutes ago, Yellowtail said:

 

I'm thinking I'd put the on-delay (and contactor) between the pressure switch and the pump motor. 

You will need to check the control voltage because the pressure switch is connected to the electronic circuit (if fitted). Its not the conventional pressure switch controls motor direct.

Posted
26 minutes ago, sometimewoodworker said:

if you have a constant power and water supply things are different but TIT.

OK, though seems like overkill to me, if experiencing so many power cuts why not get a generator, our water supply is good, so lucky there.

Posted
2 minutes ago, CGW said:

OK, though seems like overkill to me, if experiencing so many power cuts why not get a generator, our water supply is good, so lucky there.

Why bother with a generator (on going maintenance and cost smell and noise)?

 

The design of the house allows for things to continue when the power goes out (one time cost in the building) We currently have several power cuts most weeks often a couple on one day varying from a minute or two to a recent one that was 5 or 6 hours long. 

 

Maybe when all the other more important things have been done and paid for we may get round to installing one, it isn't a priority now.

  • Like 1
Posted
1 hour ago, Fruit Trader said:

You will need to check the control voltage because the pressure switch is connected to the electronic circuit (if fitted). Its not the conventional pressure switch controls motor direct.

Should I not be able to use a 230VAC relay and contactor to interrupt the line wire going into the motor?

 

 

Posted
1 hour ago, Yellowtail said:

Should I not be able to use a 230VAC relay and contactor to interrupt the line wire going into the motor?

 

 

Yes thats no problem but where will you feed the delay timer from?  

I ask because the electronic module will most likely drop its output if there is no flow because timer is holding pump off.

Posted
1 minute ago, Fruit Trader said:

Yes thats no problem but where will you feed the delay timer from?  

From the line wire going to the motor. 

 

When the pump control turns on the motor, it fires the relay, that closes the contactor that starts the motor, or am I missing something?

Posted
3 minutes ago, Yellowtail said:

From the line wire going to the motor. 

 

When the pump control turns on the motor, it fires the relay, that closes the contactor that starts the motor, or am I missing something?

But the pump control will be expecting flow and your timer will be preventing it. Pump control will no flow fault and switch off its output. 

Posted
6 minutes ago, Fruit Trader said:

But the pump control will be expecting flow and your timer will be preventing it. Pump control will no flow fault and switch off its output. 

What would signal it to restart, once the no-flow fault shut it down?

 

If the tank runs dry, the pump will run without flow until it overheats, yes?

 

 

Posted
Just now, Yellowtail said:

What would signal it to restart, once the no-flow fault shut it down?

 

If the tank runs dry, the pump will run without flow until it overheats, yes?

 

 

I dont know how it recovers but most likely keeps trying to call pump and get flow.

 

As you are only using this pump to fill a tank, I would take the electronic module out of circuit put 220v on the pressure switch to signal the timer which would bring in contactor to run pump. 

Posted
1 minute ago, Fruit Trader said:

I dont know how it recovers but most likely keeps trying to call pump and get flow.

 

As you are only using this pump to fill a tank, I would take the electronic module out of circuit put 220v on the pressure switch to signal the timer which would bring in contactor to run pump. 

Once I get the parts I'll give it a try, thanks!

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...