ATS working in manual only ( No auto)


Recommended Posts

Today im testing out the ATS before prepare to mount it up. I connected 2 wires to house grid power as 2 power sources and outpower to a light. All working when turn switch myself but there is no auto switch happening. When i remove the active power source it just close the light. Any ideas whats wrong? Auto/manual option is set to auto.

 

 

Pink

 

Edited by Pink7
Link to comment
Share on other sites

17 minutes ago, Crossy said:

U got the manual? (or any documentation)

 

No experience of that switch but I think there's supposed to be something connected to that green connector.

I have no manual. There is some info on lazada

 

Pink

Link to comment
Share on other sites

See that little bank of connectors on top (think they're green). They do effect how the switch works. Maybe they have nothing to do with your problem, but with my ATS the way they are wired effects my ATS operation. 

I have my ATS wired like Crossy's diagram then I wired the connectors to send an earth to auto start my genset.

Not the same ATS as yours.

Link to comment
Share on other sites

2 hours ago, Crossy said:

U got the manual? (or any documentation)

 

No experience of that switch but I think there's supposed to be something connected to that green connector.

I see some other ATS connect to those green connectors: example

 

Pink

Link to comment
Share on other sites

Yeah, I see that too, but it's unclear exactly what your green connectors do and connecting them incorrectly could fry something.

 

Try this.

 

With it connected as you have it.

In Manual set to OFF

Power on the Normal side.

Switch to Auto. - Does it move?

Power on the Reserve side

Power off Normal side - Does it move?

 

EDIT and message the seller of course ???? 

 

EDIT 2 Have you got a load on the output?

Link to comment
Share on other sites

Inside the ATS there is a relay, a motor and two main MCBs.

The relay is powered by the "N" circuit I think and will remain energised until power is lost at that input.

When the relay is de-energised the motor is powered to cause the MCBs to switch over to the "R" circuit.

The opposite happens when power is restored to  "N" input.

 

Make sure the supply to the "N" side and the "R" side is good.

  • Like 1
  • Thumbs Up 1
Link to comment
Share on other sites

5 minutes ago, Muhendis said:

Inside the ATS there is a relay, a motor and two main MCBs.

The relay is powered by the "N" circuit I think and will remain energised until power is lost at that input.

When the relay is de-energised the motor is powered to cause the MCBs to switch over to the "R" circuit.

The opposite happens when power is restored to  "N" input.

 

Make sure the supply to the "N" side and the "R" side is good.

Ok i will test that, thanks

 

 

Pink

Link to comment
Share on other sites

4 minutes ago, Muhendis said:

They are nothing to do with the basic function but are volt free and can be used for gen set starting.

 

Yeah, that's what I thought, but then I read on one of the pages for similar switches "this switch can not be used for generator starting" ???? 

Link to comment
Share on other sites

20 minutes ago, Crossy said:

Yeah, I see that too, but it's unclear exactly what your green connectors do and connecting them incorrectly could fry something.

 

Try this.

 

With it connected as you have it.

In Manual set to OFF

Power on the Normal side.

Switch to Auto. - Does it move?

Power on the Reserve side

Power off Normal side - Does it move?

 

 

Tested, no action 

 

Pink

Edited by Pink7
  • Sad 1
Link to comment
Share on other sites

14 minutes ago, Muhendis said:

Inside the ATS there is a relay, a motor and two main MCBs.

The relay is powered by the "N" circuit I think and will remain energised until power is lost at that input.

When the relay is de-energised the motor is powered to cause the MCBs to switch over to the "R" circuit.

The opposite happens when power is restored to  "N" input.

 

Make sure the supply to the "N" side and the "R" side is good.

https://www.google.com/search?q=inside+an+auto+transfer+switch+tear+dpwn&source=lmns&bih=937&biw=1920&hl=en&sa=X&ved=2ahUKEwiIxvf4h9b9AhV0q1YBHVVQCjEQ_AUoAHoECAEQAA#fpstate=ive&vld=cid:8b6337cb,vid:m1cX25IO2Bo,st:17

Link to comment
Share on other sites

9 minutes ago, Pink7 said:

Ok i will test that, thanks

 

 

Pink

Tested it now after change the wiring with no changes. My testing is with 2 pole connector so how it connect N to what house power wire is random.

Link to comment
Share on other sites

12 minutes ago, Crossy said:

 

Yeah, that's what I thought, but then I read on one of the pages for similar switches "this switch can not be used for generator starting" ???? 

Not on mine but I suppose different switches can do different things.

The installation book is the definitive source for this info.

Needless to say those green connectors can be left alone for a basic change over function.

  • Like 1
  • Thumbs Up 1
Link to comment
Share on other sites

21 minutes ago, Pink7 said:

Ok i will test that, thanks

 

 

Pink

Please make sure that the output side is wired with the two neutrals connected together and the two lives connected together like in the drawing.

 

image.png.015ebd0e55c1cd7c65f6cecbcc12360d.png

  • Like 1
Link to comment
Share on other sites

3 minutes ago, Muhendis said:

Please make sure that the output side is wired with the two neutrals connected together and the two lives connected together like in the drawing.

 

image.png.015ebd0e55c1cd7c65f6cecbcc12360d.png

Ok, i will re wire all and also be sure use 3 pole connectors so all connect correctly. Update will come later

 

Pink

Link to comment
Share on other sites

3 hours ago, Crossy said:

 

Try connecting it like this (all three L connected together): -

 

image.png.015ebd0e55c1cd7c65f6cecbcc12360d.png

 

i think same you because changeover motor inside is 220v and using only one phase and neutral

 

for single phase use best link all phase together because not sure which line inside circuit use for 220v control

 

 

  • Like 1
  • Thumbs Up 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...