Orangutan Posted April 3, 2013 Share Posted April 3, 2013 Hello, I am currently in the process of renovating a four story shop house, about 3400 sq.ft. I have plans that layout a three phase system, but I am now questioning if I really need it. I have read many references, but I have not found a simple convincing theory for what I need. This will be the primary home for my wife, son and myself. There is also an apartment rental included on the ground floor with mezzanine bedroom. Several TV sets, computers, 5-6 air-cons, two kitchens, 4 full bathrooms. Is there an existing topic regarding "single phase and triple phase electrical systems" that someone could point me to. Many thanks, -O Link to comment Share on other sites More sharing options...
Crossy Posted April 3, 2013 Share Posted April 3, 2013 Your big draw items will be water heaters and aircons. Let's assume 5kW heaters and 12,000 BTU aircons Quick and dirty maximum demand calculation ;- 4 x 5kW + 6 x 2kW = 32 kW = 145A @ 220V = no way on a Thai single phase supply, biggest available is 100A. I suggest a minimum of a 15/45 3-phase supply which should be adequate given diversity although a 30/100 3-phase may be better if your supply authority can provide (this supply is really intended for small industrial units). 1 Link to comment Share on other sites More sharing options...
InterestedObserver Posted April 3, 2013 Share Posted April 3, 2013 It all depends on what the PEA can supply to you at the transformer secondary. 30(100) amps single-phase is perhaps the top of the line in most installations, from there the rating goes down in rural areas. Anything more than 30(100) amps will need a three-phase installation. Link to comment Share on other sites More sharing options...
Orangutan Posted April 3, 2013 Author Share Posted April 3, 2013 Thanks Crossy I will take your recommendations to my contractor, and see if my electrical layout reflects something close to what you suggested. Link to comment Share on other sites More sharing options...
gamini Posted April 3, 2013 Share Posted April 3, 2013 you must have three phase. Link to comment Share on other sites More sharing options...
Crossy Posted April 4, 2013 Share Posted April 4, 2013 I would wire it as if it was three single phase installations, possibly as 1 phase per floor. Put the rental on a phase of its own, easier for metering and a fault in the rest of the home won't kill their power. As an aside, don't forget to arrange a water meter for the rental. 1 Link to comment Share on other sites More sharing options...
Orangutan Posted April 4, 2013 Author Share Posted April 4, 2013 I would wire it as if it was three single phase installations, possibly as 1 phase per floor. Put the rental on a phase of its own, easier for metering and a fault in the rest of the home won't kill their power. As an aside, don't forget to arrange a water meter for the rental. I think (I have to check with the contractor) that each of the four floors will be on their own separate circuit. As I understand it I will have a after market meter that can be zeroed out for the rental unit. The rental unit will be available on a daily/weekly basis, but most of the time we will be using it. What are the advantages for having three single phase installations as you suggested? Thanks, -O Link to comment Share on other sites More sharing options...
Crossy Posted April 4, 2013 Share Posted April 4, 2013 Running a single-phase sub-main from your main 3-phase panel to serve each floor and having a consumer unit (distribution board) on each floor is actually a good way of doing it and is easy to wire. Something like this:- If you have access to the proposed layout why not scan / photograph and post here for comment? Link to comment Share on other sites More sharing options...
Orangutan Posted April 4, 2013 Author Share Posted April 4, 2013 Running a single-phase sub-main from your main 3-phase panel to serve each floor and having a consumer unit (distribution board) on each floor is actually a good way of doing it and is easy to wire. Something like this:- shophouse1.jpg If you have access to the proposed layout why not scan / photograph and post here for comment? Crossy thank you for the hand holding .. here is a pdf file of the current layout. Your participation and opinion is greatly appreciated. -O electrical drawings.pdf Link to comment Share on other sites More sharing options...
Crossy Posted April 4, 2013 Share Posted April 4, 2013 A couple of quick comments, I'll have a proper look later but:- How is the rental flat split out and metered, everything seems to be on one board? The cable sizes for lighting (2.5mm2) and outlets (4mm2) seem excessive, I would normally specify 1.5mm2 on lighting and 2.5mm2 on outlets retaining the same breakers as in the current schedule. I don't see much (any) RCD protection. Link to comment Share on other sites More sharing options...
sibelius Posted April 4, 2013 Share Posted April 4, 2013 I had a nice surprise too. Our project is 500m from main road and they just made new electric line to pass our land with new electric poles. First i hear that they will make a 3 phase line from main road but then i realize it will be just normal low power line, single phase line. I going to need 3 phase line + big transformer. Because i going to have many houses and sauna building with pool too. I going to use a lot of electric. I ask from electric company estimate price to make 3 phase line to my land and answer was around 1,3 million b with transformer. Any one have experience of the prices to make own 3 phase line from main line???? Link to comment Share on other sites More sharing options...
Orangutan Posted April 5, 2013 Author Share Posted April 5, 2013 A couple of quick comments, I'll have a proper look later but:- How is the rental flat split out and metered, everything seems to be on one board? The cable sizes for lighting (2.5mm2) and outlets (4mm2) seem excessive, I would normally specify 1.5mm2 on lighting and 2.5mm2 on outlets retaining the same breakers as in the current schedule. I don't see much (any) RCD protection. As the ground floor rental will not be for long term tenants there is no separate meter. Although I have seen separate meters (after market) that can be fitted to keep track of individual spaces/rooms. In my current apartment building the owner has such a meter for one of the units.. she unlocks the meter cover and sets it back to 000000. I have added to my notes the cable size that you have pointed out, and I will discuss with my architect, so he can communicate with the electrical engineer about it. As you pointed out I do not see any reference to RCD's, and have a message into the architect, so he can communicate with the electrical engineer about it. Thanks, -O Link to comment Share on other sites More sharing options...
Crossy Posted April 5, 2013 Share Posted April 5, 2013 I would still be tempted to meter the rental separately just in case you get a long term tenant, same with water. It's easy to do at this stage Link to comment Share on other sites More sharing options...
Orangutan Posted April 9, 2013 Author Share Posted April 9, 2013 A couple of quick comments, I'll have a proper look later but:- How is the rental flat split out and metered, everything seems to be on one board? The cable sizes for lighting (2.5mm2) and outlets (4mm2) seem excessive, I would normally specify 1.5mm2 on lighting and 2.5mm2 on outlets retaining the same breakers as in the current schedule. I don't see much (any) RCD protection. Here is a pdf showing the ELCB's marked by the electrical contractor. Regarding your earlier suggestion, and example of running a single-phase sub-main from the main 3-phase panel to serve each floor, and having a consumer unit (distribution board) on each floor .. what are the advantages of this compared to my existing electrical layout? Thanks - O EE-ELCB.pdf Link to comment Share on other sites More sharing options...
Crossy Posted April 9, 2013 Share Posted April 9, 2013 Having a panel per floor would reduce the amount of wiring in the shaft and may even reduce the cable cost if the sub-mains were sensibly sized. It would also allow you to isolate a complete floor so you could work on it safely, or, in the case of the ground floor in the event of flooding it could be made safe with a single switch. Link to comment Share on other sites More sharing options...
Orangutan Posted April 10, 2013 Author Share Posted April 10, 2013 Having a panel per floor would reduce the amount of wiring in the shaft and may even reduce the cable cost if the sub-mains were sensibly sized. It would also allow you to isolate a complete floor so you could work on it safely, or, in the case of the ground floor in the event of flooding it could be made safe with a single switch. As I did not post my question in the "Do it yourself housing forum" you have provided me with an answer that even I can understand. The simplicity of your suggestion fits in with my request to my electrician for keeping each floor independent/separate, giving me the ability to shut down a specific floor. Thank you, -O Link to comment Share on other sites More sharing options...
Crossy Posted April 10, 2013 Share Posted April 10, 2013 Here is a pdf showing the ELCB's marked by the electrical contractor. I would expect to see ALL outlets protected by RCBO (what sparky is calling ELCB). EWH 1 and EWH 3 have RCD, EWH 2 does not. I would also put outside lighting on an RCD. EDIT Another possible advantage to the split by floor would be the ability to use RCDs rather than RCBOs (what sparky is calling ELCB) in a split board configuration, this would significantly reduce the cost of your distribution boards. Link to comment Share on other sites More sharing options...