sncoem Posted May 21, 2021 Share Posted May 21, 2021 hi, aircon working but needs 24 hours to reach 26 degres. it has been cleaned 1 week ago and gas checked. What can be the problem of not cooling enough air conditioning ? I try to read and maybe it could be thermostat or expansion valve ? aircon cleaning company said that it works perfectly, when in the past if could reach 24 degres in 2 hours ! It's a daikin inverter, is it possible that compressor works slower after few years, and then cool slower ? what else ? Thank you. Link to comment Share on other sites More sharing options...
Kwasaki Posted May 21, 2021 Share Posted May 21, 2021 It 2 minutes ago, sncoem said: What can be the problem of not cooling enough air conditioning It's an inverter and the room is not insulated enough for it to work properly you should of bought a cooler type unit. 1 1 Link to comment Share on other sites More sharing options...
Popular Post Crossy Posted May 21, 2021 Popular Post Share Posted May 21, 2021 It is a lot hotter than it has been recently (hence all the huge power bills everyone is moaning about). How big is the room? How big (BTU) is the aircon? 4 1 Link to comment Share on other sites More sharing options...
Popular Post Brierley Posted May 21, 2021 Popular Post Share Posted May 21, 2021 If you put your hand in front of the output, is the air cool/cold? 1 2 Link to comment Share on other sites More sharing options...
sncoem Posted May 21, 2021 Author Share Posted May 21, 2021 Please people, I have explained that this aircon cool the room, just slower than before, so of course it blows cool air. and I repeat that it is clean. I just want to find what could be the cause for not cooling as fast as before. And I repeat before someone tells to clean it, blablabla... it is perfectly clean already ! thanks again. 1 Link to comment Share on other sites More sharing options...
sncoem Posted May 21, 2021 Author Share Posted May 21, 2021 10 minutes ago, Kwasaki said: It It's an inverter and the room is not insulated enough for it to work properly you should of bought a cooler type unit. as clearly explained, it was working and cooling the room perfectly before and nothing changed. 1 Link to comment Share on other sites More sharing options...
sncoem Posted May 21, 2021 Author Share Posted May 21, 2021 10 minutes ago, Crossy said: It is a lot hotter than it has been recently (hence all the huge power bills everyone is moaning about). How big is the room? How big (BTU) is the aircon? sorry but irrelevant as already explained, it was cooling a lot faster before and nothing changed in this room. 1 Link to comment Share on other sites More sharing options...
sncoem Posted May 21, 2021 Author Share Posted May 21, 2021 Thank you for real technical help ! expansion valve ? thermostat ? talking about anything else just as the cleaning company that knows nothing seems useless.... thanks again. Link to comment Share on other sites More sharing options...
Kwasaki Posted May 21, 2021 Share Posted May 21, 2021 8 minutes ago, Crossy said: It is a lot hotter than it has been recently (hence all the huge power bills everyone is moaning about). How big is the room? How big (BTU) is the aircon? There's info on inverter air-cons about installing in certain rooms of houses. Thailands super intelligent air-cons engineering salespersons will tell you what you need. ???????????? 1 Link to comment Share on other sites More sharing options...
Kwasaki Posted May 21, 2021 Share Posted May 21, 2021 4 minutes ago, sncoem said: as clearly explained, it was working and cooling the room perfectly before and nothing changed. But the weather is hotter now at this time of year. How old is it.?? 2 Link to comment Share on other sites More sharing options...
Popular Post Crossy Posted May 21, 2021 Popular Post Share Posted May 21, 2021 Why not call the local service centre for your A/C manufacturer? They will have the necessary diagnostic equipment to sort it if there is a problem. 4 Link to comment Share on other sites More sharing options...
Popular Post Lacessit Posted May 21, 2021 Popular Post Share Posted May 21, 2021 The only thing I can think of is the OP was conned on a refrigerant refill, they said they topped it up and didn't. Or bled some off. If it was working well prior to the service, and now is performing poorly, it's not a difficult problem analysis. 3 1 2 1 Link to comment Share on other sites More sharing options...
Popular Post dddave Posted May 21, 2021 Popular Post Share Posted May 21, 2021 If it is blowing cool air but not cooling the room as it has in the past on similarly hot days, then I'd suspect it is somehow not re-circulating the cooled air in the room or that there is a significant air leak allowing hot outside air in. If your ac tech tells you nothing is wrong, get another ac guy. 1 2 1 Link to comment Share on other sites More sharing options...
Popular Post clivebaxter Posted May 21, 2021 Popular Post Share Posted May 21, 2021 4 minutes ago, Lacessit said: The only thing I can think of is the OP was conned on a refrigerant refill, they said they topped it up and didn't. Or bled some off. If it was working well prior to the service, and now is performing poorly, it's not a difficult problem analysis. we had a guy cleaning ours who always wanted to fill one up, ended up not cold. I insisted with mrs we get the Mitsubishi guys in. Their first reaction- who put this in (powerbuy) and 2nd who keeps putting gas in the system, then had to bleed it off. Get QUALIFIED people in not idiots with stepladders and a can of gas! 6 1 1 Link to comment Share on other sites More sharing options...
tifino Posted May 21, 2021 Share Posted May 21, 2021 an after-maintenance-visit Warranty-on-the -work-done beckons? - or cannot they be contacted anymore? 1 1 Link to comment Share on other sites More sharing options...
Popular Post Crossy Posted May 21, 2021 Popular Post Share Posted May 21, 2021 @sncoem Was it actually working reasonably well before being "serviced"? There are a whole bunch of scenarios from earlier posters which could be relevant (did they even use the correct refrigerant!). Either way, there's not actually a lot you can do if we identify an expansion valve fault. 2 1 Link to comment Share on other sites More sharing options...
lopburi3 Posted May 21, 2021 Share Posted May 21, 2021 Are the control settings the same? Techs may have changed them and set to lower fan speed of eco setting or some other change from remote. Also are the vanes blowing the correct direction - they may have been moved during cleaning. As mentioned the last week has been exceptionally hot here in Bangkok and suspect most of the country with additional almost 100% humidity. 1 1 Link to comment Share on other sites More sharing options...
Lacessit Posted May 21, 2021 Share Posted May 21, 2021 6 minutes ago, clivebaxter said: we had a guy cleaning ours who always wanted to fill one up, ended up not cold. I insisted with mrs we get the Mitsubishi guys in. Their first reaction- who put this in (powerbuy) and 2nd who keeps putting gas in the system, then had to bleed it off. Get QUALIFIED people in not idiots with stepladders and a can of gas! Interesting, I wasn't aware overfilling could be a problem as well. 1 Link to comment Share on other sites More sharing options...
tifino Posted May 21, 2021 Share Posted May 21, 2021 Is it possible the Label on the A/C, indicating the Refigerent to be Used is no longer current; following some retrofit in the past (previous owners) that the OP wasn't aware of? I assume amnay other readers have witnesses their own A/C being changed up from R12 to R134a etc etc btw what is the current refrigerant used in LOS these days? so say if the Unit had been refitted to now use 134a, but the Maint dudes put in the successor to 134a. I have one unit that was built for R12, but since changed to 134a; simply by changing the nipples. Does the same 'type' of physical change when a Unit is changed up to 134a's successor too? My units label was never changed, but simply overwritten by Texta 1 Link to comment Share on other sites More sharing options...
Trujillo Posted May 21, 2021 Share Posted May 21, 2021 Sounds like the compressor to me. Just call a service shop and have them come out. ACs are pretty basic machines; troubleshooting isn't a big deal. 1 Link to comment Share on other sites More sharing options...
Brierley Posted May 21, 2021 Share Posted May 21, 2021 26 minutes ago, sncoem said: Please people, I have explained that this aircon cool the room, just slower than before, so of course it blows cool air. and I repeat that it is clean. I just want to find what could be the cause for not cooling as fast as before. And I repeat before someone tells to clean it, blablabla... it is perfectly clean already ! thanks again. If the aircon is blowing out air that is just as cool as it was before but now it takes 22 hours longer to reach the desired room temperature, it seems as though the problem may not be with the aircon. As noted several times by various posters, many people currently are running their aircon units, for longer and at a lower setting, just to maintain the norm. We've started switching our main unit on at 10am and it runs until we go to bed when a second unit in the bedroom takes over and runs all night, we've never done those things ever before this year. 1 Link to comment Share on other sites More sharing options...
clivebaxter Posted May 21, 2021 Share Posted May 21, 2021 11 minutes ago, Lacessit said: Interesting, I wasn't aware overfilling could be a problem as well. As is installing too high to the ceiling making cleaning harder. Every few years ours are stripped down and taken outside for a thorough clean 1 Link to comment Share on other sites More sharing options...
2 is 1 Posted May 21, 2021 Share Posted May 21, 2021 Dont open that door all the time ! Buy new unit! 1 Link to comment Share on other sites More sharing options...
kiteman9 Posted May 21, 2021 Share Posted May 21, 2021 My aircon has been taking longer to cool our room. Especially after an all day power outage and the room heats up. It has been <deleted> hot lately... 1 Link to comment Share on other sites More sharing options...
Popular Post Liverpool Lou Posted May 21, 2021 Popular Post Share Posted May 21, 2021 (edited) 57 minutes ago, sncoem said: Please people, I have explained that this aircon cool the room, just slower than before, so of course it blows cool air. and I repeat that it is clean. I just want to find what could be the cause for not cooling as fast as before. "...what could be the cause for not cooling as fast as before". Current temperatures, probably. It was nowhere near this hot "before". Edited May 21, 2021 by Liverpool Lou 2 1 Link to comment Share on other sites More sharing options...
Liverpool Lou Posted May 21, 2021 Share Posted May 21, 2021 35 minutes ago, Lacessit said: The only thing I can think of is the OP was conned on a refrigerant refill, they said they topped it up and didn't. Or bled some off. If it was working well prior to the service, and now is performing poorly, it's not a difficult problem analysis. "The only thing I can think of is the OP was conned on a refrigerant refill, they said they topped it up and didn't". He says that it's still blowing cold air, so, so much for that disparaging theory. 1 1 Link to comment Share on other sites More sharing options...
ukrules Posted May 21, 2021 Share Posted May 21, 2021 (edited) 1 hour ago, sncoem said: Please people, I have explained that this aircon cool the room, just slower than before, so of course it blows cool air. and I repeat that it is clean. I just want to find what could be the cause for not cooling as fast as before. And I repeat before someone tells to clean it, blablabla... it is perfectly clean already ! thanks again. I had one like that, I called up an AC guy and had him fit a new unit of a slightly larger size which solved the problem. I can now get it down to 20C no problem. At this time of the year in that particular room it would only manage 24 to 25 C on a hot afternoon. I also noticed that my electricity bill went down by several thousand baht per month as a result of replacing 3 AC units which I use all day. My May bill went from about 11,500 Baht last year to 7,500 Baht this year. It looks odd having 2 AC units outside but I will take it with me when I move. Older AC units which might not be large enough in terms of BTU in my experience have problems keeping up in the hotter months no matter how much you clean them ,etc - replacing it is the answer. Edited May 21, 2021 by ukrules 1 Link to comment Share on other sites More sharing options...
MJCM Posted May 21, 2021 Share Posted May 21, 2021 9 minutes ago, ukrules said: I had one like that, I called up an AC guy and had him fit a new unit of a slightly larger size which solved the problem. I can now get it down to 20C no problem. At this time of the year in that particular room it would only manage 24 to 25 C on a hot afternoon. I also noticed that my electricity bill went down by several thousand baht per month as a result of replacing 3 AC units which I use all day. My May bill went from about 11,500 Baht last year to 7,500 Baht this year. It looks odd having 2 AC units outside but I will take it with me when I move. Older AC units which might not be large enough in terms of BTU in my experience have problems keeping up in the hotter months no matter how much you clean them ,etc - replacing it is the answer. Inverter aircon vs NON-Inverter aircons will do that. Changed a NON-inverter aircon in our condo for an Inverter Aircon and bill went less then half. But there is a caveat. Inverter Aircons are more expensive to buy, but you will be cheaper in the long run. And one more advice buy Daikin Inverters. 1 Link to comment Share on other sites More sharing options...
stubuzz Posted May 21, 2021 Share Posted May 21, 2021 1 hour ago, tifino said: so say if the Unit had been refitted to now use 134a, but the Maint dudes put in the successor to 134a. I have one unit that was built for R12, but since changed to 134a; simply by changing the nipples. Does the same 'type' of physical change when a Unit is changed up to 134a's successor too? My units label was never changed, but simply overwritten by Texta R12 and R134a are usually used in vehicles. R22 and the newer R410a are for residential units. Both use different lubricating oils. 2 Link to comment Share on other sites More sharing options...
frequentatore Posted May 21, 2021 Share Posted May 21, 2021 Really cheap solution. Reduce the size of the room (even with a very thin curtain) and you will have a cooler room. 1 1 Link to comment Share on other sites More sharing options...