The outlets ought to be wired in 2.5mm2 with a 20A breaker which will be fine with your heater.

Change the plug for a local one, the UK - Thai adaptors are not up to a 2kW appliance in continuous use, same goes for extension leads, avoid.

Fire it up at 1kW first just to ensure nothing is getting hot, no odd smells.

EDIT If you really must use an extension lead make your own http://www.thaivisa.com/forum/topic/878317-make-yourself-a-power-board-extension-lead/

Link to comment
Share on other sites

The outlets ought to be wired in 2.5mm2 with a 20A breaker which will be fine with your heater.

Change the plug for a local one, the UK - Thai adaptors are not up to a 2kW appliance in continuous use, same goes for extension leads, avoid.

Fire it up at 1kW first just to ensure nothing is getting hot, no odd smells.

EDIT If you really must use an extension lead make your own http://www.thaivisa.com/forum/topic/878317-make-yourself-a-power-board-extension-lead/

Agree, however a great % of socket outlets that I've seen here are wired using 1.5mm cable!!!!

As Crossy has said, move with caution.

Link to comment
Share on other sites

The outlets ought to be wired in 2.5mm2 with a 20A breaker which will be fine with your heater.

Change the plug for a local one, the UK - Thai adaptors are not up to a 2kW appliance in continuous use, same goes for extension leads, avoid.

Fire it up at 1kW first just to ensure nothing is getting hot, no odd smells.

EDIT If you really must use an extension lead make your own http://www.thaivisa.com/forum/topic/878317-make-yourself-a-power-board-extension-lead/

Agree, however a great % of socket outlets that I've seen here are wired using 1.5mm cable!!!!

As Crossy has said, move with caution.

Even 1.5mm would be OK at the 10A or so the heater will pull. Of course, add the kettle to the same circuit and things are going to get warm.

I'm more concerned that there's an iffy taped joint somewhere that will start fizzing on the unaccustomed load.

An undersize breaker is rarely more than an inconvenience (at least in a domestic environment).