Jump to content

Recommended Posts

Posted

On my list of things to do in the future has arrived. Been dealing with termites. Currently ripping off drywall and studs, in the spot where the underground power cable comes into the house. I currently have just a square D box, nothing fancy like earth fault detection (rccb?).

I have single phase 30A meter connection. I would like to change the breakers to rccb type (30ma) a whole house surge protection, ayne 2 transfer switches or one 3 way (one for solar and one for diesel genset andthen the mains) and perhaps a main cutoff switch. 

 

Is this overkill? If its not broke leave it alone is on my mind. Is the surge protection worth it? My cheapest route would just be to change the breakers to rccb type and forget the rest. There is so much lighting during the rainy season and I feel like I am way overdue for induction or a powerline strike nearby.

Posted

Good call on using RCBOs.

 

As a minimum I would install a separate 2-pole isolator on the incoming supply, before it goes to your box. This will allow you to completely isolate from the grid and work on your kit with no chance of live wires.

 

Definitely decent surge protection (60kA or more).

 

Ensure you have a proper ground and MEN connection.

 

You might want to get an over-size DIN rail box so you can add transfer switches etc. as and when required. Dependent upon exactly how you install your solar you may not actually need one.

 

This PEA document is worth a peruse Groundwire Mk2 book-Manual.pdf

 

The relevant diagram with my translations.

 

image.jpeg.39733a3a39947afa80015fb3e39fbb2c.jpeg

  • Thumbs Up 1
Posted
On 12/17/2024 at 6:18 AM, Crossy said:

Good call on using RCBOs.

 

As a minimum I would install a separate 2-pole isolator on the incoming supply, before it goes to your box. This will allow you to completely isolate from the grid and work on your kit with no chance of live wires.

 

Definitely decent surge protection (60kA or more).

 

Ensure you have a proper ground and MEN connection.

 

You might want to get an over-size DIN rail box so you can add transfer switches etc. as and when required. Dependent upon exactly how you install your solar you may not actually need one.

 

This PEA document is worth a peruse Groundwire Mk2 book-Manual.pdf

 

The relevant diagram with my translations.

 

image.jpeg.39733a3a39947afa80015fb3e39fbb2c.jpeg

What happens if there is a fault with the incoming neutral, the ground at some pole outside?, I feel like in that situation your ground  in your home becomes the new village ground/neutral. I'm certainly no expert but that is my first impression. Seems complicated to me. PEA reversed my neutral and Live at the meter a few years back, by accident I suppose, but that would really complicate the above diagram i think.

Posted
On 12/15/2024 at 1:24 AM, bearded_bluto said:

Currently ripping off drywall and studs

 

Sorry.

I thought you said....

Ripping off studs.

 

Anyway, I, too, must replace my breaker box.

I will chose one of the highest quality.

 

One from America.

 

Square D.

 

Schneider...all the way!

 

 

Posted
6 hours ago, GammaGlobulin said:

Anyway, I, too, must replace my breaker box.

I will chose one of the highest quality.

 

One from America.

 

Square D.

 

Schneider...all the way!

Those statements are mutually incompatible. 
Schneider Is a French origin company and uses DIN rail

Square D is a USA company that mostly uses their own non DIN rail components 

A box from the USA is not automatically one of the highest quality.

 

Also using a single box may not be the best choice depending on the number of circuits you have.

Posted
4 hours ago, sometimewoodworker said:

Those statements are mutually incompatible. 
Schneider Is a French origin company and uses DIN rail

Square D is a USA company that mostly uses their own non DIN rail components 

A box from the USA is not automatically one of the highest quality.

 

Also using a single box may not be the best choice depending on the number of circuits you have.

 

Last time I purchased a product with a Square D  symbol on it, Square D was a USA company.

In 1991, Square D became French.

In future, I will not use Square D.

Thank you.

 

Also, I will stop using APC back-up.

APC is owned by that French company.

No more APC for me.

Thank you, once again.

 

image.png.df2d370a412b6a98e1e71ceea2becf01.png

APC is French?

 

image.png.2166d3dd8a6877ec02879d89d7948bfc.png

 

 

 

Posted
13 hours ago, bearded_bluto said:

What happens if there is a fault with the incoming neutral, the ground at some pole outside?, I feel like in that situation your ground  in your home becomes the new village ground/neutral. I'm certainly no expert but that is my first impression. Seems complicated to me. PEA reversed my neutral and Live at the meter a few years back, by accident I suppose, but that would really complicate the above diagram i think.

 

Have a read of this page https://en.wikipedia.org/wiki/Earthing_system 

 

Thailand is TNC-S with MEN (Multiple Earthed Neutral) which is essentially the same as Aus who have one of the safest systems in the known universe, the UK isn't far behind (many Brits would argue here!) although the UK version of MEN is called PME (Protective Multiple Earthing).

 

Both MEN and PME are part of the mitigation of an open neutral, also the neutral is the top wire on the poles so it's likely to be the last wire to be damaged.

 

Reversed L&N at the meter does happen, we had one member who noticed his kitchen floor was getting warm where the earth rod was located. Turned out to be a swapped L&N. 

 

Thailand has no regulation that would preclude you using TT (but it wouldn't pass a PEA or MEA inspection for a permanent supply), so if you don't like the look of the N-E link you can eliminate it at the cost of reduced overall safety. Going TT would make RCD/RCBO mandatory for protection from shock in the event of a L to appliance metalwork fault.

  • Thanks 1
Posted
11 hours ago, sometimewoodworker said:

Those statements are mutually incompatible. 
Schneider Is a French origin company and uses DIN rail

Square D is a USA company that mostly uses their own non DIN rail components 

A box from the USA is not automatically one of the highest quality.

 

Also using a single box may not be the best choice depending on the number of circuits you have.

 

Maybe still USA?

 

image.png.acc990ea5e2741ee752714a2ff1aa703.png

Posted
1 hour ago, GammaGlobulin said:

 

Maybe still USA?

 

image.png.acc990ea5e2741ee752714a2ff1aa703.png

They maybe a USA product, that however doesn’t answer the question of the fittings not being DIN rail components. Also what is so good about being made in the USA? that of course doesn’t address the point that the products are probably made in China, Vietnam, Thailand etc anyway. Being a USA product is no guarantee of quality.

Posted
8 hours ago, sometimewoodworker said:

They maybe a USA product, that however doesn’t answer the question of the fittings not being DIN rail components. Also what is so good about being made in the USA? that of course doesn’t address the point that the products are probably made in China, Vietnam, Thailand etc anyway. Being a USA product is no guarantee of quality.

Any recommendations for a brand? I bought some safe-T-cut switch/breakers a few years back, I think its made in Thailand and they have some consumer box/panels in the stores around me. So if I understand if its din then I can buy whatever and throw it in whatever box as long as its a din box/rail and din breaker etc.? I liked the look of the square D/Schneider with each breaker having their own rccb with fixed 30 or 10ma for choice. I would go with 30ma. The ones I looked at in the stores seem to use just the main breaker, so if that trips your house is dark I guess.

Posted

Individual RCBOs are available here for both DIN and plug-in (Schneider/Square-D, BTIcino) consumer units. 

 

DIN have the advantage of being pretty universal "do what you like" boxes, plug-in is quick and easy but restricts your configuration choices.

 

All the major brands are here, ABB, etc. etc.

 

If you can find a specialist outlet rather than the big DIY stores they will have (or be able to order) the rarer gear.

 

If you must import kit, get it from the UK, Europe, Aus/NZ. The US electrical system is sufficiently different that US components may not operate correctly or even be destroyed!

  • Like 1
  • Thanks 1
Posted
9 hours ago, Crossy said:

Individual RCBOs are available here for both DIN and plug-in (Schneider/Square-D, BTIcino) consumer units. 

 

DIN have the advantage of being pretty universal "do what you like" boxes, plug-in is quick and easy but restricts your configuration choices.

 

All the major brands are here, ABB, etc. etc.

 

If you can find a specialist outlet rather than the big DIY stores they will have (or be able to order) the rarer gear.

 

If you must import kit, get it from the UK, Europe, Aus/NZ. The US electrical system is sufficiently different that US components may not operate correctly or even be destroyed!

So with a din type there must be I am guessing 3 bus bars for single phase? And the plug in type, which is what I have now (square D) has the bar for clipping the breaker in and 2 bus bars (earth and neutral)? I noticed I have a couple breakers way oversized for the 2.5mm cable. I am amazed at how cheap and available everything is. For the isolation switch I was looking at "ABB Switch-Isolator WSD Series switch" on shopee, 63A. According to the stories I hear around me the PEA people want to wiring, I may just order the stuff and let them install it, What I am thinking --> Isolation switch box --> transfer switch unit (future proofing) --> consumer unit.  Then inside the din type consumer unit >> surge protection (2 slots), under over voltage (2 slots), main breaker (2 slots) without earth leakage detection, then the individual breakers with earth leakage (30mA). If I didn't mention it this is single phase. Would all that put me over the target in your opinion?

Posted
16 hours ago, bearded_bluto said:

So with a din type there must be I am guessing 3 bus bars for single phase?

No, the usual is 2, one for the protective earth and one for neutral. 
IMG_1969.thumb.jpeg.08257021523e832a31bb8c12aa4c6738.jpeg

 

you can, most will, add bus bars to groups of units as above.

just a FWIW
AFIR the 4 circuits on the left are lighting and are unprotected by the under over voltage protection unit on the left.
The 3 on the right are for power machinery that may be damaged if the power is too low/high and the power goes through the contactor in the centre but is controlled by the second from the left unit

 

also of course there is the DIN rail that is isolated from everything 

IMG_1973.thumb.jpeg.81c4a42585b04699ac7eb0e1b504e37a.jpeg
 

Because DIN rail is so popular there are hundreds of different modules available from thousands of suppliers so usually DIN rail units are less expensive than plug in units 

 

These are 

at the top, the incomer box with lighting protection and the isolators for the workshop and house

the next 2 are for the workshop, (I have too many power circuits in the workshop for a single box to be logical) 

the bottom one is for the garden 

 


IMG_1972.thumb.jpeg.eb2a6135f6add41dd3f8bcf2c8716e3d.jpeg

 

the house has its own boxes.

 

All of this is far more than is strictly necessary but units are cheap and when building it’s simple to add circuits for versatility, I can easily have too many high power consumption tools to overload a single, or 2 or 3, circuits 
 

 

  • Like 1
Posted
On 12/20/2024 at 8:43 PM, sometimewoodworker said:

No, the usual is 2, one for the protective earth and one for neutral. 

 

 

I see something called a floating bus bar when using google, If not that then how does the Live from the main breaker get distributed to the individual breakers? I am picturing 10 wires jammed into a a terminal. lol If it is indeed a "floating bus bar", then I would think it would be included with the consumer unit for the number of slots?

Posted
9 hours ago, bearded_bluto said:

I see something called a floating bus bar

If you reread my post you will see 

 

On 12/21/2024 at 8:43 AM, sometimewoodworker said:

you can, most will, add bus bars to groups of units as above.

The 2 bus bars have a plastic sleeves on them they are in the first picture feeding the groups of MCB’s

 

9 hours ago, bearded_bluto said:

floating bus bar", then I would think it would be included with the consumer unit for the number of slots?

It is! 
 

 

9 hours ago, bearded_bluto said:

I am picturing 10 wires jammed into a a terminal. lol

That is the builders way, 😉 an electriction will know that you can loop the connections  

 

a bus bar is nothing more than a conveniently shaped wire, faster and safer to install than wire.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...