1st quesrion. I'm doing some major renovation to my Thai home, so it's a good time for me to update the electrical system (house was built around 20 years ago). Will be renewing most of the wiring and CU.

Am in the UK now for a short trip, so am wondering..... any reason why I can't use kit from the UK ? The 18th Edition spec is a metal CU c/w 100A main switch and 40kA Type 2 SPD (20 way is 60gbp). With all RCBO protected circuits, 30mA RCBO - Type A B Curve (these are 15gbp each)

 

I've looked at the Schneider range in Thailand which I'm sure is OK but the prices seem higher than UK? The RCBOs are around 1200 baht on Lazada.

 

I'm aware that the electrical system in Thailand is TN-C-S with MEN. So I will need to add the N to E link in the CU. Is 10mm adequate for that ?

Its a DIN rail system so in theory, can always fit another brand of RCBO in the future if need be.

 

 

2nd question. Can I fit a supply isolator switch between the incoming L and N cable and the CU, just like they do in many UK homes ? They are sold here as a 100A DP switch,  along with 63/80/100 fuses. Gives some protection and can isolate the CU easily.

 

3rd question. I have an electronic engineering background, so pretty confident about overseeing the installation. But how competent is a Thai electrician with regards to testing continuity, resistance, polarity etc. Would they ever use a Megger tester or is that a silly question ?

 

Many thanks for any advice given

 

Posted

 

You will need to replace the main switch with a suitably rated 2-pole MCB for over-current protection, Thailand has no DNO fuses.

 

You could then put that switch in a small DIN box and use it as an isolator.

 

You need to wire MEN as per the Thai requirements routing the incoming neutral via the earth bar, so your MEN link actually needs to be the same size as your incoming cables.

 

I've never seen a Thai domestic sparks with a megger, they do tend to rely on the "bang-test" (if it doesn't go bang, all is good). 

 

Look at the routing of the incoming neutral: -

image.jpeg.504afc8860e8ba7e808f53399542b68c.jpeg

  • Thumbs Up 1
Posted

Thank you crossy thats really helpful, no problem to use an MCB in the isolator. And use 25mm meter tail cable for the MEN link.

I guessed as much about a lack of proper testing in Thailand.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...