Jeff Reinstad Posted September 8, 2024 Posted September 8, 2024 I lived here for a long time without air conditioning, but during the last heatwave, I decided to buy one at GlobalHouse. Some guys came over the next day to install it. Since day one, it’s been dripping water, and every morning there's a big puddle underneath. As it’s installed directly under our patio door, it’s become a problem. Is this something normal, like condensation, and nothing can be done about it? Or is it something I should complain about that can be fixed?
Popular Post Tim K Posted September 8, 2024 Popular Post Posted September 8, 2024 If the unit is not on the ground there should be special pipe that connects to the condensation outlet and allows droplets to silently flow to the ground. In Thailand almost all ACs have it. In Russia almost none(illegally, owners don't care) and in multi-story buildings it creates hell in June-August, as water drips from 5 - 6 - 8 - 10 -12th floor down to the ground or into your balcony or window sill depending on the wind making loud thumps. I don't see that pipe on your photo. 1 1 2
Popular Post Tim K Posted September 8, 2024 Popular Post Posted September 8, 2024 Or they have messed up this part Not providing enough insulation for the pipes so when hot outside air touches the cold pipe water droplets appear and slowly flow down to the bottom of the AC. 2 3
Popular Post Captain Monday Posted September 9, 2024 Popular Post Posted September 9, 2024 Looks lile a good install, except no condensation drain line? My units have flexible or fixed hoses leading to rain channel on balcony or to drain pipe inlet. 2 1 1
Liverpool Lou Posted September 9, 2024 Posted September 9, 2024 11 hours ago, Jeff Reinstad said: is it something I should complain about that can be fixed? Why not just call the seller and ask them to take a look at it? 1 1 1
Popular Post Lacessit Posted September 9, 2024 Popular Post Posted September 9, 2024 Condensation is normal. The unit is extracting moisture from the air it is cooling. As others have said, it should have a drain pipe. 2 2 4
G Rex Posted September 9, 2024 Posted September 9, 2024 Do you have water dripping from the main drain line? In normal split system instals, the water forms in the head unit and is drained outside by piping. There should be no dripping from the inverter unit. You may be correct in suggesting insufficient lagging on the gas pipes coming from the inverter. Edit. looking again at the main picture - it looks like they did not instal a drain line, which should be 'in the bundle' with the gas pipes. I would be calling the installers back... 1
Popular Post ChipButty Posted September 9, 2024 Popular Post Posted September 9, 2024 I once a villa and all the A/C where at the back of the villa, I extended the drain pipes onto the flower beds, kept them watered, 6 1
Will B Good Posted September 9, 2024 Posted September 9, 2024 1 minute ago, ChipButty said: I once a villa and all the A/C where at the back of the villa, I extended the drain pipes onto the flower beds, kept them watered, Yes.....we've done the same, we get at least a gallon a day of water from each unit.....how come his photos show no drain???... 2
Dirk Z Posted September 9, 2024 Posted September 9, 2024 I had the same problem. After unblocking the drain pipe problem solved.
4MyEgo Posted September 9, 2024 Posted September 9, 2024 13 hours ago, Jeff Reinstad said: Is this something normal, like condensation, and nothing can be done about it? Or is it something I should complain about that can be fixed? As others have said, it appears that there isn't a drain pipe, however I doubt that would be the problem as it looks more like condensation to me. There should be two brass nuts in sight, I have been known to get on a stool while the A/C was running on one unit, sitting exactly like yours, high up on the wall, and getting a shifting spanner to turn one gently until the condensation stopped. Try that, if that fails, call the installer, no doubt he will want at least 500 baht to come out for what could be a simple job as I pointed out. Let us know if that works will yah. 1
sometimewoodworker Posted September 9, 2024 Posted September 9, 2024 1 hour ago, Captain Monday said: Looks lile a good install, except no condensation drain line? My units have flexible or fixed hoses leading to rain channel on balcony or to drain pipe inlet. All mine have condensation lines incorporated into the line set on the left of the picture, I highly doubt that that has been forgotten, though it may be plugged. 1 1
Dazinoz Posted September 9, 2024 Posted September 9, 2024 1 hour ago, G Rex said: Do you have water dripping from the main drain line? In normal split system instals, the water forms in the head unit and is drained outside by piping. There should be no dripping from the inverter unit. You may be correct in suggesting insufficient lagging on the gas pipes coming from the inverter. Edit. looking again at the main picture - it looks like they did not instal a drain line, which should be 'in the bundle' with the gas pipes. I would be calling the installers back... Yes, looks like many people here think should be a drain line from the outdoor unit, wrong, as you say should come from indoor unit. In reverse cycle units, which I have never seen in Thailand there is also a drain line on the outdoor unit as it does produce condensation when in the heating mode. I have also found if the unit is short on refrigerant icing can occur on the service valves and piping on the outdoor unit and hence more condensation. Looking at the picture the refrigerant piping is on the right side and the internal drain line comes out the bottom of the ducting on the left. 1
Dazinoz Posted September 9, 2024 Posted September 9, 2024 1 hour ago, Will B Good said: Yes.....we've done the same, we get at least a gallon a day of water from each unit.....how come his photos show no drain???... I believe it does, coming from bottom of ducting on left hand side of unit. 1
steven100 Posted September 9, 2024 Posted September 9, 2024 of coarse it's normal ... but where from? ... don't you have a drain pipe coming from the AC to outside? or are you saying it's dripping water at the front onto the floor ? edit : sorry ... I just seen your pictures. It is normal for the AC to acquire water at that point, sometimes there's a drain attachment there with a small pipe .... and some don't have it.
Dazinoz Posted September 9, 2024 Posted September 9, 2024 2 minutes ago, steven100 said: of coarse it's normal ... but where from? ... don't you have a drain pipe coming from the AC to outside? or are you saying it's dripping water at the front onto the floor ? Photo he posted showed where water dripping from.
steven100 Posted September 9, 2024 Posted September 9, 2024 1 minute ago, Dazinoz said: Photo he posted showed where water dripping from. yes Daz, my bad ... I just seen that after i posted. I edited my comment. 1
Wrwest Posted September 9, 2024 Posted September 9, 2024 14 hours ago, Jeff Reinstad said: I lived here for a long time without air conditioning, but during the last heatwave, I decided to buy one at GlobalHouse. Some guys came over the next day to install it. Since day one, it’s been dripping water, and every morning there's a big puddle underneath. As it’s installed directly under our patio door, it’s become a problem. Is this something normal, like condensation, and nothing can be done about it? Or is it something I should complain about that can be fixed? You have good answers already. I would just add that, while cost is negligible, my four new units installed charged for the plastic drain piping. 1 1
brianthainess Posted September 9, 2024 Posted September 9, 2024 Where is the drain pipe from the indoor unit ??? The yellow arrow is the drain pipe, but water could be tracking down through the gas line, insulation/trucking into the outside unit. What is that pipe to the left of your unit ? 1
Fruit Trader Posted September 9, 2024 Posted September 9, 2024 Condensate dripping from the outdoor unit. Sometimes it comes from pipes inside the condenser but more often from exposed service valves or uninsulated pipe near to them. Below shows recent installation here where we have insulated the service valves to stop dripping on the walkway. 1 1
sometimewoodworker Posted September 9, 2024 Posted September 9, 2024 1 hour ago, steven100 said: edit : sorry ... I just seen your pictures. It is normal for the AC to acquire water at that point, sometimes there's a drain attachment there with a small pipe .... and some don't have it. None of the 3 different makes of unit I have have any water from that area, it is more probable that the unit is probably not clean.
andygrr Posted September 9, 2024 Posted September 9, 2024 14 hours ago, Jeff Reinstad said: I lived here for a long time without air conditioning, but during the last heatwave, I decided to buy one at GlobalHouse. Some guys came over the next day to install it. Since day one, it’s been dripping water, and every morning there's a big puddle underneath. As it’s installed directly under our patio door, it’s become a problem. Is this something normal, like condensation, and nothing can be done about it? Or is it something I should complain about that can be fixed? Just need to blow through the drain line. I do mine energy few months.
Fruit Trader Posted September 9, 2024 Posted September 9, 2024 38 minutes ago, brianthainess said: Where is the drain pipe from the indoor unit ??? The yellow arrow is the drain pipe, but water could be tracking down through the gas line, insulation/trucking into the outside unit. What is that pipe to the left of your unit ? See photo. 1
steven100 Posted September 9, 2024 Posted September 9, 2024 3 minutes ago, Fruit Trader said: See photo. perhaps you could get them to install a small tray under that drip point with tubing and run it into that indoor drain line going down. 1
Fruit Trader Posted September 9, 2024 Posted September 9, 2024 1 minute ago, steven100 said: perhaps you could get them to install a small tray under that drip point with tubing and run it into that indoor drain line going down. Why me?
brianthainess Posted September 9, 2024 Posted September 9, 2024 10 minutes ago, Fruit Trader said: See photo. Shame you didn't put that before, could have saved my effort. I would go back to Global and Complain, it is not normal. 1
steven100 Posted September 9, 2024 Posted September 9, 2024 15 minutes ago, Fruit Trader said: Why me? sorry, I mean the OP... haha 1
Will B Good Posted September 9, 2024 Posted September 9, 2024 47 minutes ago, andygrr said: Just need to blow through the drain line. I do mine energy few months. How do you do that?