Fuse or not to fuse, that is the question.

Featured Replies

All solar DC combiner boxes in Thailand have a fuse, breaker and surge protection, but in many parts of the world they skip the fuse and just have a 20A breaker and surge protector.

 

Is the fuse really needed? What protection is the fuse offering that a breaker can't do?

 

 

images (90).jpeg

The fuse only provides protection against short circuits whereas the MCB provides both short circuit and overload protection, where is the fuse located in the circuit and what is the fuse and MCB ratings?

  • Popular Post

I think the MCB is a mechanical device and so could fail...the fuse is backup.

A fuse is redundant, the panels are incapable of delivering more than the rated current.  Even a short circuit is no problem.

 

The breaker’s main purpose is to be able to isolate the panels from the inverter, it’s never going to trip because of an overcurrent situation.

  • Popular Post

I'm with @JBChiangRai unless your "combiner" actually combines two or more strings into a single output.

 

in the case of multiple parallel strings each individual string should have a suitable fuse, then all those fuses feed a single breaker.

 

The reasoning is thus. If you have, say, three 10A strings in parallel then in the event of a failed (short) panel in one string (reducing its output voltage) the other strings will push current "backwards"  through that string possibly resulting in a hotspot and conflagration.

 

I suspect the fuses in the "not actually combiner" units are simply a result of just taking out the extra strings from a real combiner design without really understanding what's going on.

"I don't want to know why you can't. I want to know how you can!"

12 hours ago, ExpatOilWorker said:

All solar DC combiner boxes in Thailand have a fuse, breaker and surge protection, but in many parts of the world they skip the fuse and just have a 20A breaker and surge protector.

 

Is the fuse really needed? What protection is the fuse offering that a breaker can't do?

 

 

images (90).jpeg


A fuse and a breaker are the same thing just a different style. They protect against over loads and shorts. Just use whichever you prefer.
Make sure you have a spare breaker though, they do go bad at the worst time

1 minute ago, daveAustin said:

Fuse will blow faster than breaker?


No Sir but a breaker is resettable. They perform the exact same function

1 hour ago, Crossy said:

I'm with @JBChiangRai unless your "combiner" actually combines two or more strings into a single output.

 

in the case of multiple parallel strings each individual string should have a suitable fuse, then all those fuses feed a single breaker.

 

The reasoning is thus. If you have, say, three 10A strings in parallel then in the event of a failed (short) panel in one string (reducing its output voltage) the other strings will push current "backwards"  through that string possibly resulting in a hotspot and conflagration.

 

I suspect the fuses in the "not actually combiner" units are simply a result of just taking out the extra strings from a real combiner design without really understanding what's going on.


Is there a diode in each panel preventing back flow?

  • Popular Post
20 minutes ago, JBChiangRai said:

Is there a diode in each panel preventing back flow?

 

Sometimes, but rarely on the larger panels, they tend to be included in small panels intended as battery maintainers or similar applications.

 

The problem is that every time a diode is introduced into the circuit there's a volt-drop of around 0.8V (power schottky device). With 10 panels in series that's 8V that's not getting through (80W @ 10A).

 

Some do advocate adding a single blocking diode to each string and they are also sometimes included in the combiner box.

 

As always, there are many ways to skin a cat.

"I don't want to know why you can't. I want to know how you can!"

  • Author
1 hour ago, Crossy said:

 

Sometimes, but rarely on the larger panels, they tend to be included in small panels intended as battery maintainers or similar applications.

 

The problem is that every time a diode is introduced into the circuit there's a volt-drop of around 0.8V (power schottky device). With 10 panels in series that's 8V that's not getting through (80W @ 10A).

 

Some do advocate adding a single blocking diode to each string and they are also sometimes included in the combiner box.

 

As always, there are many ways to skin a cat.

Very good 👍 idea.

 

Screenshot_20250528_091316_Shopee.jpg

  • Popular Post

It's worth remembering that the panels, by their very nature, are current and voltage limited.

The fuses, surge absorbers and breakers normally fitted are more to protect against lightning EMP (electromagnetic pulse) events.

The fuses fitted are normally "quick blow" which is considerably faster than a circuit breaker.

The scenario in the event of a lightning surge is:

The EMP will cause a high current flow in the solar panel wiring.

The surge absorber conducts this high current to ground.

This high current causes the fuse to blow very quickly.

A second strike nearby will go nowhere because the fuse has already blown.

House and inverter et al should never see any dangerous and damaging surges.

Having said all that I've never heard of such a disastrous event happening but sods law being what it is .........

  • Popular Post
5 hours ago, ExpatOilWorker said:

Very good 👍 idea.

 

Screenshot_20250528_091316_Shopee.jpg

Idea is good, but take a suitable diode, not one of these toys. At 0.8V and 10A, the diode needs to dissipate 8W.  Put this into your MC4 connector and you get a nice ignition device to burn down your whole installation. 

 

  • Popular Post
8 hours ago, SLOWHAND225 said:


No Sir but a breaker is resettable. They perform the exact same function

It sure is but beg to differ. Dunno about this system specifically, but fuses are incorporated into electronic circuitry routinely in order to protect components against shorts. A fast blow fuse will drop out a lot quicker than an mcb, which is chiefly to protect from overcurrent. 

On 5/28/2025 at 9:35 AM, Muhendis said:

It's worth remembering that the panels, by their very nature, are current and voltage limited.

The fuses, surge absorbers and breakers normally fitted are more to protect against lightning EMP (electromagnetic pulse) events.

The fuses fitted are normally "quick blow" which is considerably faster than a circuit breaker.

The scenario in the event of a lightning surge is:

The EMP will cause a high current flow in the solar panel wiring.

The surge absorber conducts this high current to ground.

This high current causes the fuse to blow very quickly.

A second strike nearby will go nowhere because the fuse has already blown.

House and inverter et al should never see any dangerous and damaging surges.

Having said all that I've never heard of such a disastrous event happening but sods law being what it is .........

 

Just to be on the safe side I have sketched up a schematic of a combiner box.

 

Combiner box.jpg

On 5/28/2025 at 9:35 AM, Muhendis said:

It's worth remembering that the panels, by their very nature, are current and voltage limited.

The fuses, surge absorbers and breakers normally fitted are more to protect against lightning EMP (electromagnetic pulse) events.

The fuses fitted are normally "quick blow" which is considerably faster than a circuit breaker.

The scenario in the event of a lightning surge is:

The EMP will cause a high current flow in the solar panel wiring.

The surge absorber conducts this high current to ground.

This high current causes the fuse to blow very quickly.

A second strike nearby will go nowhere because the fuse has already blown.

House and inverter et al should never see any dangerous and damaging surges.

Having said all that I've never heard of such a disastrous event happening but sods law being what it is .........

Is having solar panels not a bigger risk for a direct lightning strike ?

I'm just asking. Fuses or breakers won't do much in that case.

8 minutes ago, FlorC said:

Is having solar panels not a bigger risk for a direct lightning strike ?

I'm just asking. Fuses or breakers won't do much in that case.

 

No more so than having any other grounded metal structure such as you car-port or even your house roof.

 

As you say, nothing is going to save you in the event of a direct strike. The issue is induced currents from nearby strikes which is exactly what the surge suppressors are there for.

"I don't want to know why you can't. I want to know how you can!"

4 minutes ago, Crossy said:

The issue is induced currents from nearby strikes

How nearby must a strike be to become a risk through inducted currents ?

I always unplug for lightning closer than 10 seconds = 3 km.

Before we had solar we took a direct hit on the house, at the time we had no MOVs at all, killed a few things and blew off a couple of ridge tiles.

 

We had a tree 20m away hit a couple of weeks back. Scared me s**tless!!

 

No actual damage apart from one (unprotected) rs-485 receiver although the inverters did reset. We have a lot of MOV suppression mind.

 

My main worry is actually nasties coming in on the grid, we have a 100kA MOV on the incoming supply and if there's a really close storm I flip the main breaker.

 

 

 

 

"I don't want to know why you can't. I want to know how you can!"

I'm not going to risk my big tv and computer , so I unplug.

I only have the small 1,5 cm round MOV's , they don't stand a chance.

3 minutes ago, FlorC said:

I'm not going to risk my big tv and computer , so I unplug.

I only have the small 1,5 cm round MOV's , they don't stand a chance.

 

Why not install some decent protection on the incoming supply? The kit isn't exactly expensive 🙂 

You can still unplug of course if things get really exciting.

 

We also have those little baby ones all over including in each LED light fitting.

"I don't want to know why you can't. I want to know how you can!"

  • Author
50 minutes ago, Crossy said:

we have a 100kA MOV on the incoming suppl

Can you share a link or picture of your 100 kA MOV?

 

I know you play in a different electric league than the rest of us, but I only have a 20 kA on my single phase supply line. Good enough, or time to upgrade?

My supply is underground until 200 m from the house, where it continues in poles.

 

 

Screenshot_20250530_153255_Gallery.jpg

16 minutes ago, ExpatOilWorker said:

Can you share a link or picture of your 100 kA MOV?

 

I know you play in a different electric league than the rest of us, but I only have a 20 kA on my single phase supply line. Good enough, or time to upgrade?

My supply is underground until 200 m from the house, where it continues in poles.

 

 

Screenshot_20250530_153255_Gallery.jpg

 

This is actually our spare. It and its friend that's in the CU were actually bought in Shanghai when I was there a while back, the supplier was recommended by the company I was visiting.

 

There are loads of similar units on Lazada for various prices, I would avoid the cheapest of the cheap!

 

Note that these are about 1.5 units wide so a double will take up 3 DIN slots.

 

image.jpeg.001b62e0f06b4b9885bd5ca512ecfdf7.jpeg

"I don't want to know why you can't. I want to know how you can!"

  • Author
  • Popular Post
27 minutes ago, Crossy said:

 

This is actually our spare. It and its friend that's in the CU were actually bought in Shanghai when I was there a while back, the supplier was recommended by the company I was visiting.

 

There are loads of similar units on Lazada for various prices, I would avoid the cheapest of the cheap!

 

Note that these are about 1.5 units wide so a double will take up 3 DIN slots.

 

image.jpeg.001b62e0f06b4b9885bd5ca512ecfdf7.jpeg

Here is a zoom-out picture of Crossy's workshop.....

 

FB_IMG_1747734905210.jpg

6 minutes ago, ExpatOilWorker said:

Here is a zoom-out picture of Crossy's workshop.....

 

FB_IMG_1747734905210.jpg

 

That's not too far from the truth I'm afraid :whistling:

 

It does get tidied on occasion but after a while the gorilla gets in and throws everything about again ...

 

"I don't want to know why you can't. I want to know how you can!"

On 5/27/2025 at 6:42 PM, ExpatOilWorker said:

world they skip the fuse and just have a 20A breaker and surge protector.

Fuses protect the panels when the "surge arrestor" gets short to the ground.
breaker protect  (and works as a sw as well) panels from controller and inverter. 
muhendis diagram shows that how it works. Your sample diagram is very basic. 

Create an account or sign in to comment

Recently Browsing 0

  • No registered users viewing this page.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.