Hello All,

 

please, my question is how far I can install subpanel from main consumer unit.

I want to install subpanel in second floor.

my consumer unit main breaker is 50A, 15/45 and have 2 empty slots.

what 1. breaker size  and wire size to use and how to run it.

the second floor only have 1 A/C and 2 outlets and six lights

thanks

Posted
4 hours ago, Nuitum said:

please, my question is how far I can install subpanel from main consumer unit.

As far as you like, though the further away the larger the supply cable should be

 

Our house CU is about 15~20 metres from the incoming CU.

 

4 hours ago, Nuitum said:

what 1. breaker size  and wire size to use and how to run it.

Probably 6mm cable to alow for future expansion 

6 mm2 cable - 32 amp maximum circuit breaker

though 4 mm2 cable - 25 amp maximum circuit breaker, will be enough for your current needs.

 

You can clip the cable (as many locals do)to the wall or run it in conduit, that will look neater.

Posted

Yeah, assuming the cable length is less than 40m (let us know if it's further) then run 6mm2 3-core or 3 x single core in conduit (you could use a smaller (2.5mm2) ground then).

 

Supply from a 32A breaker in your existing panel.

 

Small breaker panel at the other end and you're good to go. 

 

If you don't already have earth leakage protection (RCD / RCBO / Safe-T-Cut) now would be a good time to install same ????

 

 

 

  • Thanks 1

"I don't want to know why you can't. I want to know how you can!"

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.


  • Topics

  • Popular Contributors

  • Latest posts...

    1. 0

      Cambridge University Faces Backlash discriminating against white job seekers

    2. 0

      The Vaccine Whisperer: How One Doctor Is Rebuilding Trust in Immunisation

    3. 0

      Trump's Crypto Windfall: President Reports $57 Million in Earnings from Digital Token

    4. 0

      Bribes and Betrayal: USAID Official at Center of $550M Corruption Scandal

    5. 0

      Cracks Within: Iran’s Supreme Leader Faces Mounting Pressure Amid Crisis

    6. 0

      Wes Streeting’s NHS Gamble: Labour’s Make-or-Break Moment

  • Popular in The Pub

×
×
  • Create New...