4,500 Watts will pull just over 20A at 220V, marginal on 2.5mm2 on a 20A breaker (which is often found in existing installations) but it will be OK if you don't take 30 minute showers. If the 20A breaker does trip don't be tempted to put in a bigger one.

If you are pulling new cable use 4mm2 and put it on a 32A breaker.