Jump to content

Recommended Posts

Posted

Hi all,

 

I know next to nothing about electrics so go easy on me.

 

My kitchen sink has a water heater underneath with it's own breaker switch. The breaker switch regularly switches off when I'm washing up. Why is this & what should I do about it?

 

Thanks

Posted

Yes, it could be a defective breaker, but maybe, just maybe, the breaker is doing its job and protecting the heater and possibly the user from going up in smoke!  What I would do is put a meter with a current clamp on the wire to the heater and see exactly how much current is being drawn when the breaker trips.  I have the equipment to do it so I can do it easily.  But since the OP already admitted that he's a sparky NOT, he should hire someone to troubleshoot and resolve the problem!!

Posted

Is this something which has just started and everything has been OK in the past?

 

How many Watts is the heater?

 

How many Amps is the breaker?

 

Does the breaker have a "test" button? (is it an RCBO)

 

If you're not sure, post photos.

Posted
On 16/02/2017 at 5:02 AM, Crossy said:

Is this something which has just started and everything has been OK in the past?

 

How many Watts is the heater?

 

How many Amps is the breaker?

 

Does the breaker have a "test" button? (is it an RCBO)

 

If you're not sure, post photos.

Hi Crossy

Sorry for taking so long to reply, been looking for the heater user manual. It's a Siemans DH 0611, 6 kW & 32 A fuse protection. Not sure about the breaker so I've attached a photos.

It has been happening for a long time but only intermittently, not every time I use it.

Cheers

Breaker switches.JPG

Breaker box.JPG

Posted (edited)

Breaker 13 (hot water kitchen) is a 20A breaker. Too small for 6KW

 

Adding.. 32A would be ok if the wire size is  thick enough. What wire size do you have from breaker box to heater.?

Edited by ThaidDown
Posted
25 minutes ago, ThaidDown said:

Breaker 13 (hot water kitchen) is a 20A breaker. Too small for 6KW

 

Adding.. 32A would be ok if the wire size is  thick enough. What wire size do you have from breaker box to heater.?

No idea about the wire size I'm afraid. What size would it need to be for a 32 A breaker?

Posted

^^^ If the heater is the only thing on the circuit, and you do not intend to put a bigger heater in, then 4mm should be ok.

 Note.... If Crossy  comments later and says 6mm, then go with his recommendation.

 

Posted

Yup ^^^ the installation instructions say 32A breaker and 4mm2 cable http://media3.bsh-group.com/Documents/9001155288_A.pdf

 

In truth if it's on 2.5mm2 it will be fine so long as it's not used for hours at a time.

 

What power is the oven (is it just an oven)? Most domestic ovens (no hob) would be fine on a 20A breaker. Swapping the last two breakers could be a quick (and very cheap) fix.

Posted
15 hours ago, Crossy said:

Yup ^^^ the installation instructions say 32A breaker and 4mm2 cable http://media3.bsh-group.com/Documents/9001155288_A.pdf

 

In truth if it's on 2.5mm2 it will be fine so long as it's not used for hours at a time.

 

What power is the oven (is it just an oven)? Most domestic ovens (no hob) would be fine on a 20A breaker. Swapping the last two breakers could be a quick (and very cheap) fix.

The water heater is only used for 15 minutes max so as long as the cable is at least 2.5mm then I can use a 32A breaker right?

Not sure about the power of the oven but I've run it at max temp for short periods & at low temp for 8 hours+ & the breaker has never gone off.

Posted

Stop resetting it, your playing with fire. Electrician won't cost more than 1 thousand baht to sort it

Sent from my Redmi Note 3 using Tapatalk

Posted
5 hours ago, happydays said:

The water heater is only used for 15 minutes max so as long as the cable is at least 2.5mm then I can use a 32A breaker right?

Not sure about the power of the oven but I've run it at max temp for short periods & at low temp for 8 hours+ & the breaker has never gone off.

Post a picture of the label on the back of the oven or read it and post the results.  It should have either kWh data or amps.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...