Posted

AC is not my strong point.

On all connection diagrams I found on Interweb they show black incoming connected to black outgoing and white connected to white. 

My house wiring at that location has white to black and black to white.

Surely with AC they flip at 50 hz. so "polarity" shouldn't be an issue.

So is it crucial. To correct I have to take the mount off the wall etc. and reverse the holes that the wires protrude from.

Posted
51 minutes ago, VocalNeal said:

On all connection diagrams I found on Interweb they show black incoming connected to black outgoing and white connected to white. 

My house wiring at that location has white to black and black to white.

Surely with AC they flip at 50 hz. so "polarity" shouldn't be an issue.

So is it crucial. To correct I have to take the mount off the wall etc. and reverse the holes that the wires protrude from.

Just swapping so the colours match may not be a good idea.

 

checking that line is black and neutral is white is a good first step.

 

if you just reverse the connection you could well end up switching neutral not line, so allowing for entertaining dancing when you accidentally make contact with a live part that is switched off so should be dead.

 

There isn’t polarity on AC but there is line (usually at about 220v to earth) and neutral (usually at about 0v to earth).

 

Holding a neutral with a sweaty hand with sweaty feet on a damp floor certainly isn’t recommended but usually doesn’t do anything.

 

Holding a live line with a sweaty hand with sweaty feet on a damp floor can be everything from entertainment for onlookers to deep sadness that they have to deal with hospitals, embassies, temples and spending money on a “he’s dead” party.

 

is it crucial to correct? No. Is it important to correct? Quite possibly.

is it as simple as swapping wires? That depends on your desire for the real possibility of a shocking experience. ????  But no it isn’t without checking everything else first.

Posted (edited)

But does the RCCD device know which is Line or Neutral?

 

There is no terminal designation on the device.

 

It trips when the test button is pressed.

Edited by VocalNeal
Posted (edited)
11 minutes ago, VocalNeal said:

But does the RCCD device know which is Line or Neutral?

For an RCCD with no markings for line/neutral probably not. But some do need to be wired correctly to function, they should be/are marked.

 

The way an RCCD disconnects is important. If both L/N are disconnected it probably makes no difference. If just 1 gets switched then it is rather important that it’s Line, at least I think so. ???? 
 

I’m sure @Crossy will correct me soon if I’m wrong. ???? 

Edited by sometimewoodworker
Posted
12 minutes ago, VocalNeal said:

But does the RCCD device know which is Line or Neutral?

 

There is no terminal designation on the device.

 

It trips when the test button is pressed.

A two-pole RCD will function properly either way - if no designation, then it doesn't matter.

 

But, L and N should not be assumed based on color.  N should not be connected to single-pole breaker and it should not be switched.  When designated, L, N, and E should always be connected accordingly.

Posted
28 minutes ago, bankruatsteve said:

N should not be connected to single-pole breaker and it should not be switched.

That makes sense. I'll check that the internal relay is double pole.

 

 

 

Posted
1 hour ago, VocalNeal said:

But does the RCCD device know which is Line or Neutral?

There is no terminal designation on the device.

It trips when the test button is pressed.

 

Can you post a photo of the device in question? If not a manufacturer and part number?

 

Posted

Can do but I am not at home at present. Japanese RCCD. Starts with a K.

 

Was in the house when I viewed but one was broken so I went to local electrical store with sample and they gave me an exact copy. 

 

From memory 30mA

Posted
10 minutes ago, VocalNeal said:

Can do but I am not at home at present. Japanese RCCD. Starts with a K.

Can't remember seeing the term "RCCD".  Is that what many would call a "RCCB" or "RCBO"?

Posted
10 minutes ago, bankruatsteve said:

Can't remember seeing the term "RCCD".  Is that what many would call a "RCCB" or "RCBO"?

I call them GFI but some use the residual current terminology. 

Posted (edited)
22 minutes ago, bankruatsteve said:

Can't remember seeing the term "RCCD".  Is that what many would call a "RCCB" or "RCBO"?

RCD, RCCD and RCCB (device vs breaker)  are the same but an RCBO is not.

 

Quote

About RCCB 

RCCB (residual current circuit breaker) detects current difference between neutral and live conductors. The difference is also known as ‘residual current’. Proper functioning circuits will have balanced neutral and live current and the residual current occurs when there is some potential shock hazard or fault. The device is an RCD i.e. residual current device class of item and circuit breaker, which is a part of its name, indicates that the electrical product sits within costumer unit with the other CBs (circuit breakers).

It should not be confused with MCB current rating at which it will trip out.

Defining RCBO

RCBO means residual current circuit breaker with over current protection, which is a combination of RCCB and MCB.

When current leakage occurs, the RCCB (residual current detecting element) will trip the entire circuit. Similarly, in case the circuit is overloaded then components of internal magnetic/thermal circuit breakers are capable to trip the electronic device.

But I don’t know which type a GFI is 

Edited by sometimewoodworker
Posted
3 minutes ago, VocalNeal said:

I call them GFI but some use the residual current terminology. 

A GFI or GFCI normally has no overcurrent protection - same as RCD and RCCB.  RCBO combine RCD with MCB.  Some RCBO are single pole but when used as single phase main breaker are always 2-pole.

Posted
31 minutes ago, sometimewoodworker said:

RCD, RCCD and RCCB (device vs breaker)  are the same but an RCBO is not.

 

Right.  Well, the "B" in RCCB is for breaker.  Whatever, I just didn't know what "RCCD" is referring to.

Posted
2 hours ago, bankruatsteve said:

Right.  Well, the "B" in RCCB is for breaker.  Whatever, I just didn't know what "RCCD" is referring to.

I think the "D" is for device

  • Thanks 1
Posted
20 minutes ago, VocalNeal said:

I think the "D" is for device

I suppose it would be if that was a common term used for RCD - but it's not that I am aware.  IE: Google RCCD and you won't get anything resembling a RCD.  At least I don't.  Cheers.  ????

  • 3 weeks later...
Posted
On 9/30/2020 at 12:33 PM, Crossy said:

 

Can you post a photo of the device in question? If not a manufacturer and part number?

 

Home again.

 

20201017_101926[1].jpg

Posted
5 minutes ago, VocalNeal said:

Home again.

 

It's 2 pole so L & N are interchangeable. 

 

Do ensure that the line (input) and load (output) are the correct way round. Some units are reversable, many are not and will emit the magic-smoke when the "test" button is pressed (ask me how I know).

Posted
20 minutes ago, VocalNeal said:

Electricity is just smoke inside a wire?

 

All electrical and electronic appliances are powered by smoke. If the smoke gets out they stop working.

  • Like 1
  • Haha 1

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.


  • Topics

  • Latest posts...

    1. 17

      Truck Collides with BMTA Bus in Dramatic U-Turn Crash

    2. 23

      Is this the "Little Surprise" of 47 and the Speaker?

    3. 0

      ZeroGPT: The Ultimate AI Content Detection Tool

    4. 58

      Thai man loses 372,000 baht to nursing student in scam wedding

    5. 88

      British lawyer latest to fall in Laos alcohol poisoning tragedy

    6. 87

      Elon Musk reportedly creating tension within Donald Trump’s inner circle

    7. 152

      Europe Braces for Escalation: Germany Mobilizes NATO Troops Amid Putin's Nuclear Threats

  • Popular in The Pub


×
×
  • Create New...