Ran a couple of 2.5 wires and 2 earth wires in a small duct. Very tight fit and had to belt the cover to get it to go on over the wires. Is that OK, or do I need to replace it with the next size larger ducting?

Thanks.

Posted

You're probably over the intended fill ratio of the duct. The tighter cables are packed together the warmer they will get and will need de-rating accordingly.

Taking a pragmatic approach, what is the actual load on those 2.5mm2 cables? Anything under 10A continuous I would not be worrying.

Posted

Thanks Crossy. As it's easy to change the ducting, I'll pick up a larger size next time I'm at Global House. They certainly make life easier- no spending ages clipping cables.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.


  • Topics

  • Latest posts...

    1. 104

      So the U.S. elected an autocrat -- what to expect next from a Hungarian perspective

    2. 66

      Driving round on my Harley shouting 'Slava Ukraini' to passers by..

    3. 17

      Bangkok students assaulted, stripped, blackmailed by classmates

    4. 10

      Boris Johnson Accuses Starmer of Aligning with Hamas Over ICC Netanyahu Arrest Warrant

    5. 10

      Boris Johnson Accuses Starmer of Aligning with Hamas Over ICC Netanyahu Arrest Warrant

    6. 5

      World War III Has Already Begun": Ukraine's Former Military Chief Warns of Global Conflict

    7. 246

      K bank E-mail with Tax Forms attached ?

  • Popular in The Pub


×
×
  • Create New...