My Issan 10kw on grid solar project fully installed by contractors 337,500bht


Recommended Posts

Posted
2 hours ago, BritManToo said:

Agreed, it's almost as if the solar meter readings are double everything.

 

He does have two inverters, software configuration issue?

 

I'm also not clear if he has the "Smart Power Sensor" (item H on page 6 of the manual) it's not on the single-line that I can see (our equivalent is a simple clamp-on current transformer on the incoming supply). If not where is the "self consumption" number coming from?

 

SUN2000-(2KTL-5KTL)-L0 User Manual.pdf

 

@Thaifish Any actual documentation from PEA yet?

 

 

Posted
Just now, Crossy said:

He does have two inverters, software configuration issue?

 

I'm also not clear if he has the "Smart Power Sensor" (item H on page 6 of the manual) it's not on the single-line that I can see. If not where is the "self consumption" number coming from?

 

@Thaifish any photos of what you have and the general installation, it's certainly looking good from an export point of view.

 

Yes, I could absolutely believe he was generating 25kwhr and using 20kwh a day.

Posted

Here are our graphs for yesterday, note that the right hand side is grid consumption not self consumption.

Real time version (with some additional graphs) here https://thingspeak.com/channels/991448

 

Untitled.jpg

You can see the irrigation pumps in the morning, Madam washing and ironing around mid day and the bedroom A/C and shower in the evening. This is the sort of thing I'd be expecting to see.

 

 

  • Like 2
Posted
On 2/25/2021 at 8:21 AM, Thaifish said:

I run an 8000w hot water machine for my shower and fill jacuzzi,

Maybe you should spend a few bob on a Solar water heater too,

regards Worgeordie

  • Like 1
  • Haha 1
Posted
1 minute ago, Srikcir said:

Do you have storage, ie., Telsa Power Wall?

 

The systems under discussion here are all on-grid systems which export excess production to the grid, no batteries.

Posted
1 hour ago, worgeordie said:

Maybe you should spend a few bob on a Solar water heater too,

regards Worgeordie


It may be cheaper to use 6 solar panels of V(max) 40 volts in series powering a stored hot water tank

Posted
2 hours ago, Crossy said:

it's not on the single-line that I can see (our equivalent is a simple clamp-on current transformer on the incoming supply).

 

But what throws a spanner in the works is :-


QUOTE - We had to run a second phase from the grid meter as we burnt the supply cable out. So we have 2 phases coming into the bahn.


Wiring around the Schneider load center is interesting.


I will hold back any comments about solar production until the OP has all ducks in a row.
 

  • Like 2
Posted

Thanks very much for the information, from all the contributors, I am interested in going Solar, my normal usage is 750 units approx 3,500Baht at least half of that is for the Pool pumps which are on twice a day.

I rarely if ever use the AC,

The batteries seem to be a very high expense within any system, could I use the solar power to run the house and pumps during the day and revert to PEA for night and dull days?

I shall be following your experience with interest.  thanks

Posted
On 2/24/2021 at 9:16 PM, Thaifish said:

 

20210217_115804.jpg

 

Oooh, hybrid inverters it seems ???? 

 

Any plans to add batteries at a later date (I'm assuming they have "emergency" power outputs).

 

 

Posted
On 2/22/2021 at 9:31 PM, Thaifish said:

Folks give me a few days to put this together. My system has been up and running for only 4 days and I would call it a commissioning stage. There was a black out 4 hours from grid day 3 which did not help. There is plenty to tell so far already from my experience. Slowly Slowly catch the monkey!! Yes my outlay was 337,500bht + 3 cases of Chang and 1case of Leo... Physical installation took 2 days to install + 2 days initial start up. The initial start up on day 3  configuring output performance/display was hampered by lousy internet reception and was sorted early on day 4. Not an installer issue. It could have been finished on day 3 bar the internet issue. The 6 guys who physically installed the system come from Bangkok so free accommodation was supplied on site in Yai's bahn on the floor!!. Also my "Issan Luv Machine" acka   "Missus" provided 3 cooked meals a day for workers which is being charged back to the company. (~1500bht) I was more than happy with the arrangement of accommodation set up before it happened knowingly I could build up a relationship with these guys with the installation. So I will progress with this thread and put some photos and links up to web pages etc.. After day 4 I am producing way more than what is being consumed... The meter does not lie! 

i would have to live to be 115 to get a payback, so I won't be doing that. 

Posted

I'm considering going down this route myself - not so much to try to save or make money, more so that I have one less monthly outgoing when I finally get to retire... 

  • Like 2
Posted
8 hours ago, Crossy said:

Our OP is apparently getting a LOT more from his panels than we are, he has roughly 10kWP of panels and is getting 53kWh (5.3kWh per 1kWP installed), we have 6.5kWP installed and are currently getting about 22.5kWh (3.5kWh per 1kWP installed). He's getting better than 50% more than we are.

 

If I pick a really good day recently (not avg) then I get 19.6 kWh / 3.96 kW = 4.95kWh per kWp. He got 7% higher and in my case the panels are not clean. The slope of "my" roof is 15 degrees pointing reasonably south and has a tiny bit shadowing in the very early morning. I can see him getting the quoted yields.

  • Like 2
Posted

Day 7and my updates... First up I really did not want to post my power bill but I have had heaps of questions about previous consumption. The bill is not accurate consumption as I returned to Thailand January with lock out fellang since March last year.. Long story.. I do know from memory from my previous 8 years living here that I would expect this time of year for the Bin to be in the high 4,000bht range... Maybe 4,600bht and it will build up over the wet season to maybe 5,400bht.. Each year it builds up.. The consumption shown in the last 6 months is low for reasons yours truly has not been on the ground... I wish to show a full picture here of my installation. The ATM has been broken until I got back... On the bonus side the Durian is fruiting for the first time..4 years... with all the water from irrigation.. 

20210226_204945.jpg

Posted

For those crunching numbers attached is my diary readout from the old meter 7 days now in production.. As many posters are saying.... To good to be true with output.... A big shortfall with this system is the poor readout display. Enviouse of other posters display....Maybe with smart meter when it turns up I might get a more accurate info with display??  

20210226_202254.jpg

Posted

From my readouts I found by clicking on the inverter Icon and Meter Icon I could gain a bit more info as in the Pics attached... Even though the main screen shows power coming from the grid the box shows a minus which means it is being fed into grid. The meter is spinning backwards all day.. Sheeet software readout.. It is all I have to go by...

Inverter readout click on 260221.png

Meter click on readout 260221.png

Posted

There is a smart meter wired in as earlier questioned. In the schematics of wiring I think there are 2 but I watched the installers remove 1 during initial start up. There is a scrolling readout with active energy IMP/EXP and Active Power which I do not comprehend??? Not sure which side of power input it is coming from....ie PV or Grid?? The other readouts are basic Amp, Watt, Freq to me which I understand

Smart meter Solar.jpg

Posted

IMP/EXP should be Import (consumption from grid) and Export (production sent to grid). Active Power should be I guess the current wattage.

  • Like 1
Posted
20 hours ago, TyJames said:

Thanks very much for the information, from all the contributors, I am interested in going Solar, my normal usage is 750 units approx 3,500Baht at least half of that is for the Pool pumps which are on twice a day.

I rarely if ever use the AC,

The batteries seem to be a very high expense within any system, could I use the solar power to run the house and pumps during the day and revert to PEA for night and dull days?

I shall be following your experience with interest.  thanks

 @TyJames No need for batteries, run grid-tie like many of us are, your solar just offsets the bill. If you size the system to maintain your pool pumps then the meter will rarely, if ever, go backwards so no attract teh attention of PEA.

 

Why not start a thread of your own or have a read of the other solar threads then ask questions?

 

  • Like 1
Posted (edited)

Your past meter readings show 20 units/day, your new power readings display shows production of 30 units and use of 27 units a day.

These are far more believable than your previous claims of 50-70 units production and 40 units use a day.

 

912875498_Inverterreadoutclickon260221.png.99bb000bc480fc53c03913fdc361edf5.png

Edited by BritManToo
  • Like 1
Posted
11 hours ago, Thaifish said:

There is a smart meter wired in as earlier questioned. In the schematics of wiring I think there are 2 but I watched the installers remove 1 during initial start up. There is a scrolling readout with active energy IMP/EXP and Active Power which I do not comprehend??? Not sure which side of power input it is coming from....ie PV or Grid?? The other readouts are basic Amp, Watt, Freq to me which I understand

 

The DDSU666-H is the "Smart Power Sensor" which interfaces the current transformer hanging off your incoming supply in the Schneider box and your inverters. It's this that's generating your usage/export/import data.

 

One assumes that the manuals for all your devices are in a pile of documentation somewhere.

 

DDSU666-H Manual.pdf

 

  • Like 1
Posted
1 hour ago, Crossy said:
1 hour ago, Crossy said:

The DDSU666-H is the "Smart Power Sensor" which interfaces the current transformer hanging off your incoming supply in the Schneider box and your inverters. It's this that's generating your usage/export/import data.

 

One assumes that the manuals for all your devices are in a pile of documentation somewhere.

data:image/gif;base64,R0lGODlhAQABAPABAP///wAAACH5BAEKAAAALAAAAAABAAEAAAICRAEAOw==

 

 

Ok got it. The one fitted is a Chinese model not a Huawei brand. Chinglish manual included. If the sensor is generating the data then maybe this is what is causing the unusual production/consumption readouts? It looks like you can change the values if I am reading it correctly?? Is that possible?? If so then I will get onto the installers to fix..

 

Posted
26 minutes ago, Thaifish said:

Ok got it. The one fitted is a Chinese model not a Huawei brand. Chinglish manual included. If the sensor is generating the data then maybe this is what is causing the unusual production/consumption readouts? It looks like you can change the values if I am reading it correctly?? Is that possible?? If so then I will get onto the installers to fix..

 

You shouldn't be able to change anything on the DDSU unit other than the RS-485 address. I wouldn't mess with it.

 

I included the English manual with my earlier post but it probably isn't really going to help.

 

 

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.




×
×
  • Create New...