I completely rewired my workshop which is in an extension to the house.

 

I have two (radial) circuits:

  • Socket circuit with 4 sqmm wires which tails off to 2.5 sqmm in places
  • Light circuit 1.5 sqmm wire; total consumption less than 150 W

 

I don't have a separate CU in my shop and only have one cable (3 X 4 sqmm) coming in from the house's CU. This cable is protected with a 20 A breaker.

 

Questions: Would it be necessary (or recommend) to protect the light circuit that only has 1.5 sqmm wires with a lower breaker i.e. 10 A or 6 A, rather than connecting it directly to the socket circuit?  Would a simple a 2P/ 10 A breaker in my shop be sensible in order to separate the light circuit?

Link to comment
Share on other sites

What is your idea?

I guess if something needs extra protection then it will be the sockets and not the light? Or not?

Like it something goes wrong with a tool in your workshop then you want that the tool is disconnected but probably you still want that the light is on.

  • Like 1
Link to comment
Share on other sites

With a 20A breaker at the house end you should be fine. 

 

1.5mm2 is good for a load of 16A so 20A isn't really going to bother it and it would be a short term overload anyway until the 20A breaker operated.

 

If you have a very long run to the shed you might run in to issues with the adiabatic equation but I'd leave it as it is.

 

What you wouldn't want to do is up that 20A breaker (to support your new industrial welder) without putting a baby CU in the shop.

  • Thanks 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...