From where is this stray 14VAC coming and what can I do about it?


Recommended Posts

Posted

I was under the impression with modern earth leakage switches in the control box earth was no longer required, input appreciated

 

Also most water heaters have an elb fitted so there could be two to trip and cut off elect

Posted
4 hours ago, sometimewoodworker said:

Effective earthing may allow them to trip before a human is involved and is an absolutely good thing 

Which is exactly why I didn't bother mentioning imbalance in line voltage, it just confuses the issue.

If people believe an effective earth is required for a ELCB (RCD) to operate efficiently, is that a bad thing.?

Especially considering how lax most Thai electricians are, and how antiquated much of Thai household wiring is.!

BTW, in my days (late 60s through 70s) ELCBs (as they were known then) were commonplace on larger electrical installations, condos, factories etc.
But were less common on domestic household switchboards.!

It was the emerging popularity of swimming pools, their associated electrical equipment and several electrocutions that brought on the requirement for domestic RCDs in the 1980s.!

Many western countries have legislation that will not certify an installation without an operating RCD, as Thailand should do.!

Electricity does deserve respect, it can't be seen, smelt or heard, but by 'F' you can feel it.!

Posted
5 minutes ago, millymoopoo said:

Many western countries have legislation that will not certify an installation without an operating RCD, as Thailand should do.!

 

Actually Thailand does, it's just so often ignored and it's not retrospective. 

 

Once you have permanent meter the supply authorites don't give a fart unless they see the meter going backwards (so make sure they don't).

 

  • Like 1
Posted
4 hours ago, Crossy said:

 

That's a good connection, is that shower to CU or CU to rod?

Both. I had placed the screw driver about five meters from the grounding rod so I ran a wire from the rod to the screw driver.  So, probe to existing ground wire still dangling by heater, to Gbar in CU, through heavier ground wire to rod, to screw driver, back through temp ground wire to probe.

 

 

Quote

 

Doesn't it have a 200 ohm range?

 

 

Yes, 0.1

Posted

 

 

 

9 hours ago, millymoopoo said:

Whilst there are many respondents to this subject it is worth while understanding some basics.

1: Electricity and wet areas don't mix well.!

2: Effective earthing in these areas is essential.

3: Multiply earthed neutral system, with or without ELCB (safety switch) is appropriate.

Effective earthing in Thailand is often overlooked.

The length of an earth spike is irrelevant, it's effectiveness is.!

A 60ft earth spike into dry ground is almost as ineffective as a 6ft spike into dry ground.

A spot where the ground is permanently moist is essential for an earth spike to work.

So a spikes into the ground near the septic leach drain long enough to be well into the moist area should work.

Several spikes spaced out within the moist area are more effective than one.

If this is not available then a spike long enough to reach into the ground water table should be used.

Earth spikes that join together (male and female screw ends) can be assembled and driven into the moist ground at what ever depth is required.

Testing (megameter) of the effectiveness of earthing is advised.

Multiple earthed neutral systems are appropriate.

This is the long brass bus bar in the main switchboard, it will have all the neutral wires (black or blue) from the house circuits connected into it as well as the main earth wire (green).

This can be divided into two sections connected together by the earth leakage circuit breaker safety switch (ELCB) as a fail safe.

It should be noted that ELCBs (safety switches) do not work when there is no effective earth.

In pre plastic pipe days, electrical safety in wet areas was taken care of by effective earthing of steel and copper pipes and fittings.

In this plastic pipe era safety is now taken care of with ELCBs.

And thus where there is no effective earth ELCBS are useless.!

In this specific situation it may be worth while opening the hot water heater to see the actual heater (boiler), many are small copper tanks with electric elements within, some are now made of heat proof plastic.

If the boiler is copper, test the tank body with the pen volt meter, it should test at 0v, if a voltage is detected and the tank is not earthed, earth it.

Plastic boiler tanks are more difficult to test, the heater element within the tank will have a copper outer shell, some of this outer may be protruding from the tank, test this, it too should be at 0v.

If a voltage is detected and the tank is earthed, the earth is faulty (ineffective).

Refer to above on how to ensure the earth is effective.

Some water heaters come with built in ELCBs but as previously mentioned become useless when there is no effective earth.

ELCBs trip on less than 1v, if the voltage detected is 12v - 14v this suggests, 1: there is no ELCB on the circuit or 2: the earth is ineffective.

A lot of good information here, it will take awhile to digest it all.  Thank you.

Posted
9 hours ago, Grusa said:

It is entirely possible there is an induced voltage between the supply ground and your grounding rod.

It would appear so. Is this normal and what causes it? In your opinion should I do something about it and if so, what?

Posted
8 hours ago, sometimewoodworker said:

The majority of you post is excellent but in your concentration on an ELCB as the safety switch and the way it works you have made a significant error which is drawing a dangerously wrong conclusion (in that if believed people may decide not to install one) 

The function of the vast majority of RCCBs (a common term for your ELCB) that are required to be installed in Thailand and many other countries, is to measure the current on both the line and neutral and if there is an imbalance to cut the circuit NO PERMANENT EARTH CONNECTION IS REQUIRED FOR THEM TO FUNCTION, they work if enough (a very tiny amount) of difference is detected.
 

Effective earthing may allow them to trip before a human is involved and is an absolutely good thing 

This is slightly off-topic but frankly I do not trust ELCB s in Thailand simply because I have been hit hard by 220VAC twice and I think that proper functioning ELCB s , which were installed, should have prevented them both. Each time I got hit I was grounded to an object other than the N which in theory should have activated the ELCB. I compare these to a time prior when I felt a slight “bump” (still 220) and the ELCB did trip. This distrust includes the ELCB s in the shower heaters and that is why I would like to mitigate their need as much as possible.

 

 

Posted
11 hours ago, ellobo said:

This is slightly off-topic but frankly I do not trust ELCB s in Thailand simply because I have been hit hard by 220VAC twice and I think that proper functioning ELCB s , which were installed, should have prevented them both. Each time I got hit I was grounded to an object other than the N which in theory should have activated the ELCB. I compare these to a time prior when I felt a slight “bump” (still 220) and the ELCB did trip. This distrust includes the ELCB s in the shower heaters and that is why I would like to mitigate their need as much as possible.

 

 

The RCCB will not stop you getting a shock, it will reduce the time of a shock to a usually non lethal one. Some RCCDs allow the length of the cutoff to be extended and even bypassed. Electric shock is a strange thing it has a variable effect depending on the person the path through that person among other factors. Correct Earthing is always good but incorrect earthing can be deadly.

Posted
4 minutes ago, sometimewoodworker said:

The RCCB will not stop you getting a shock, it will reduce the time of a shock to a usually non lethal one. Some RCCDs allow the length of the cutoff to be extended and even bypassed. Electric shock is a strange thing it has a variable effect depending on the person the path through that person among other factors. Correct Earthing is always good but incorrect earthing can be deadly.

But they still should trip, right?  These did not.

Posted
7 minutes ago, ellobo said:

But they still should trip, right?  These did not.

 

Did they trip on the "Test" button?

 

Most will only trip between 15 and 30mA, that hurts, a lot! But you probably won't die. 

 

The requirement for a "30mA" RCD is that is must NOT trip at 15mA and it MUST trip at 30mA. So if you get one that goes at 25mA and you only draw 20mA whilst dying it won't open.

 

Hence the requirement that Class-1 appliances must still be earthed, the RCD is secondary protection.

  • Like 2
Posted
1 minute ago, ellobo said:

But they still should trip, right?  These did not.

As I mentioned shock is a funny thing, they can be bypassed and need regular testing to make sure they are working.

Do you know for sure that they 1) weren’t bypassed? 2) had been tested within a month? 3) weren’t set so high that you broke the contact before they did 4) that the current was actually going through them?

  • Like 1
Posted
2 minutes ago, sometimewoodworker said:

As I mentioned shock is a funny thing, they can be bypassed and need regular testing to make sure they are working.

Do you know for sure that they 1) weren’t bypassed? 2) had been tested within a month? 3) weren’t set so high that you broke the contact before they did 4) that the current was actually going through them?

#1 and 4.  Installed in CU as right out of the box.  The photo attached to my first post is typical.  #3.  No settings provided in this brand of ELCB s.

 

#2.  Probably not, and I doubt most people test every month although I am sure that you and Crossy do, no disrespect intended, but you are not typical when it comes to electrical matters .  Just another hoop that makes me distrust them.  And yes they still trip on the test button.

 

 

Posted

Look, I am not anti-Thai (married to, visited for …, lived for …, yada, yada) nor am I anti-ELCB, but, we all know that sooomtimes in Thailand we get <deleted>. And, I know just enough electrical to be dangerous, so when I walk into the hardware store I have no idea what is good and what is not.

 

So if you all will tell me in your opinion which brand of ELCB is most trustworthy, and what settings I should use, I will replace my existing ELCB s.      TIA

Posted
On 7/21/2021 at 5:48 PM, Crossy said:

 

Yeah, it should be a proper rod, report to your local PEA office.

 

Long time ago now Crossy, and the house also had some typical Thai wiring, inasmuch as the feed for the aircon in the main bedroom came straight from the cables from the power pole in the road!! They had been "hacked into", insulation stripped back and the aircon feed wrapped around them and covered in tape...........never went anywhere near the Dist board, so the aircon was permanently live!!

 

 

  • Like 1
Posted
1 hour ago, ellobo said:

So if you all will tell me in your opinion which brand of ELCB is most trustworthy, and what settings I should use, I will replace my existing ELCB s. 

 

Firstly please stop using the old abbreviation, it means something very different in the modern world and should be reserved for the old voltage operated units (which you probably won't find here), please call it an RCD (or RCBO if it has overload protection).

 

Big names are Schneider (Square-D), Siemens, ABB and the commonly referred to "Safe-T-Cut" which is great if you want to add protection to an existing and already full distribution board.

 

Lower cost brands Haco, BTIcino, Chang are also acceptable.

 

If your existing units test ok why replace them? What brand are they?

  • Like 2
Posted
1 hour ago, ellobo said:

Look, I am not anti-Thai (married to, visited for …, lived for …, yada, yada) nor am I anti-ELCB, but, we all know that sooomtimes in Thailand we get <deleted>. And, I know just enough electrical to be dangerous, so when I walk into the hardware store I have no idea what is good and what is not.

 

So if you all will tell me in your opinion which brand of ELCB is most trustworthy, and what settings I should use, I will replace my existing ELCB s.      TIA

I am neither pro nor anti Thai, there are some things that are significantly different, some really good, others strange (to my eyes) others not great, but it’s not my country or society so try to accept mostly.

 

There are things available that are very poor quality and may barely function, generally higher priced items are better. 
 

If your RCCBs apparently aren’t working then it’s possible that they do work but are incorrectly installed or that they are actually faulty so if you can find someone who can check to see if they are correctly installed and working that should be the first step before buying something that may not be needed 

Posted
15 hours ago, ellobo said:

It would appear so. Is this normal and what causes it? In your opinion should I do something about it and if so, what?

Yes it is normal. DC can be caused by ground chemistry, but that is not the case here, you are getting AC. It can be induction from overhead or buried power line or some other source, even leakage current from a remote source.

 

It's not my field of expertise, so don't take my word for it!  If it bothers you, simply bond your local ground to the incoming ground if there is one, and to the neutral bus. Take expert advice before doing it. (@Crossy ?)

Posted
On 7/22/2021 at 5:37 AM, Grusa said:

It is entirely possible there is an induced voltage between the supply ground and your grounding rod.

why do some countries supply a ground and other don't? ie France doesn't

And if you're supplied with a ground why are folks using a 'grounding rod' instead?

Yours confused lol

Posted
2 minutes ago, driver52 said:

why do some countries supply a ground and other don't? ie France doesn't

And if you're supplied with a ground why are folks using a 'grounding rod' instead?

 

Because of how the local supply system is organised. Here, like Oz is TNC-S with MEN so you get a solidly grounded neutral to which you connect a further rod and that becomes your "ground". In the UK you won't notice what you have 'coz it's all hidden in the service head.

 

Using a rod instead of the provided "ground" could be because you have an EV charge point or farm animals (very sensitive, cows will stop milking from even a miniscule shock).

  • Thanks 1
Posted
6 minutes ago, Crossy said:

TNC-S with MEN

thanks for the post, it's getting above my pay grade to be honest lol

So in Thailand it's like this?

 

300px-TN-C-S-earthing-EN.svg.png

Posted

 

 

On 7/22/2021 at 10:16 AM, millymoopoo said:

Whilst there are many respondents to this subject it is worth while understanding some basics.

1: Electricity and wet areas don't mix well.!

2: Effective earthing in these areas is essential.

3: Multiply earthed neutral system, with or without ELCB (safety switch) is appropriate.

Effective earthing in Thailand is often overlooked.

The length of an earth spike is irrelevant, it's effectiveness is.!

A 60ft earth spike into dry ground is almost as ineffective as a 6ft spike into dry ground.

A spot where the ground is permanently moist is essential for an earth spike to work.

So a spikes into the ground near the septic leach drain long enough to be well into the moist area should work.

A separate grounding rod for the shower heaters has been added right next to one of the septic tanks. The earth around this tank will remain moist as long as someone in living in the house. The existing grounding wires from the shower heaters have been moved to the new grounding rod.

 

On 7/22/2021 at 10:16 AM, millymoopoo said:

Testing (megameter) of the effectiveness of earthing is advised.

Not available.

 

On 7/22/2021 at 10:16 AM, millymoopoo said:

In pre plastic pipe days, electrical safety in wet areas was taken care of by effective earthing of steel and copper pipes and fittings.

In this plastic pipe era safety is now taken care of with ELCBs.

The water line from the supply tank to the shower is all plastic except for some valves which are isolated from the ground. I cut a portion of the plastic pipe and added a section of steel pipe and earthed it. (It is above ground for now but I will add some underground later.)

 

On 7/22/2021 at 10:16 AM, millymoopoo said:

In this specific situation it may be worth while opening the hot water heater to see the actual heater (boiler), many are small copper tanks with electric elements within, some are now made of heat proof plastic.

If the boiler is copper, test the tank body with the pen volt meter, it should test at 0v, if a voltage is detected and the tank is not earthed, earth it.

Plastic boiler tanks are more difficult to test, the heater element within the tank will have a copper outer shell, some of this outer may be protruding from the tank, test this, it too should be at 0v.

It's a copper tank with a plastic shield but can test the copper intake and output lines, 0v.

 

line and cu schematic.jpg

Posted
5 hours ago, ellobo said:

It's a copper tank with a plastic shield but can test the copper intake and output lines, 0v

Excellent result, 0v..!

General rule of thumb, if an electrical appliance has a metal body it will require an earth which willl be connected to a third pin or contact on the plug, any appliance showing any voltage above 0 on the metal body (third pin) is not earthing properly and should be disconnected, the earthing checked, fixed and not reconnected until 0v can be achieved.

Note: All earth spikes (ground rods) should be connected together, including the shower earth, as this ensures continuity, should one fail the others will take over..!

 

schematic.jpg

Posted
6 minutes ago, millymoopoo said:

Note: All earth spikes (ground rods) should be connected together, including the shower earth, as this ensures continuity, should one fail the others will take over..!

 

I agree, BUT make the connections OUTSIDE the house. A lightning strike near one rod will create a big potential between the rods leading to a very large current in the link, you don't want that inside your home.

 

There is a reason multiple rods are not permitted in Oz (except in specific circumstances).

 

  • Like 1
Posted

 

 

Quote

Note: All earth spikes (ground rods) should be connected together, including the shower earth, as this ensures continuity, should one fail the others will take over..!

 

schematic.jpg

Thank you for your response.  Unfortunately, if I connect the earth spikes as you suggest, this will put me right back where I started.

 

A quick recap of what I have found with an illustration this time.

 

I have an unknown source of fourteen to fifteen V potential at my Ns.

 

The CU in the parking area is a newer one with the N connected directly to the Gbar and then proceeding to the Main CB. Therefore, with the G connected to the Gbar, I have a 12V+ (probably the same 14-15V but as you know, the pen meter is not concise) on the G which gives me the 12V+ in the shower water heater, G, tank, and all.

 

Hence, the second, unconnected G-rod giving me 0V at the water heater.

 

If you think that multiple G-rods are necessary, I will install additional rods as illustrated but still keep the groundings separated.

 

1323841476_lineandcuschematic2.thumb.jpg.98fd8dee5e652d0efd014d45c7360f5e.jpg

 

 

Posted

@ellobo

 

Have you done the "screwdriver in the lawn" check (measuring voltage, not resistance between the driver, L, N and E)?

 

Have you verified that you actually have MEN implemented on your supply? Check the supply poles, the neutral (the top wire of the 4 LV wires) should be grounded at every third pole.

 

If your supply is MEN and the neutral is getting to 15V above deck than there's a significant diverted current somewhere. Very worrying.

 

If your supply is not MEN (or you are not sure) you should remove the N-E link and "TT" the whole house.

 

As it is now with the shower on a separate rod there's no real hazard but I worry that you are managing to pull your earth up to 15V.

 

  • Like 1
  • Thanks 1
Posted

Thank you for your response and concern.

 

On 8/6/2021 at 10:29 AM, Crossy said:

Have you done the "screwdriver in the lawn" check (measuring voltage, not resistance between the driver, L, N and E)?

Yes, July 22 post.

“OK, screwdriver ground installed and connected directly to the water heater. 224VAC L-E, 14VAC G-E.”

 

Quote

Have you verified that you actually have MEN implemented on your supply? Check the supply poles, the neutral (the top wire of the 4 LV wires) should be grounded at every third pole.

 

If your supply is MEN and the neutral is getting to 15V above deck than there's a significant diverted current somewhere. Very worrying.

MEN confirmed. See photos below. Three poles down the same.

 

Quote

As it is now with the shower on a separate rod there's no real hazard but I worry that you are managing to pull your earth up to 15V.

 

As do I.

 

Investigating further, I went to where the power lines enter our property and disengaged the double pole, knife disconnect switch. On the incoming side, the pen meter showed the same readings as taken in the house, 12+V on N and ~220 on L. I could not use my multi-meter as the probes are too short. (I even had my ol' trusty, not rusty, screwdriver with me ready to jab into the dirt.)  ????

power pole gd-sm .jpg

power pole G-sm2 .jpg

Posted
6 minutes ago, ellobo said:

OK, screwdriver ground installed and connected directly to the water heater. 224VAC L-E, 14VAC G-E.

 

And the important one N-E? Don't assume it's going to be the same as the G-E one (it should be of course but ...).

 

Is N-E constant or does it vary with load or time of day?

 

A MEN N at 14V isn't right, shame you can't check at the meter (is it sealed you you can't remove the terminal cover?).

 

I might still be tempted to remove the MEN link, at least then you know all your grounds are actually at ground.

Posted

 

 

On 8/7/2021 at 3:41 PM, Crossy said:

 

And the important one N-E? Don't assume it's going to be the same as the G-E one (it should be of course but ...).

I was doing so much testing that I may have lost track but I believe that this is a typo as it makes no sense to test G to E, as in the context of our discussions, they are the same. I think it should have read N to E as that is consistent with what I have been reading, and still am.

 

On 8/7/2021 at 3:41 PM, Crossy said:

 

Is N-E constant or does it vary with load or time of day?

Sorry but I did not pay that much attention. It was always 14-15V.

 

On 8/7/2021 at 3:41 PM, Crossy said:

 

A MEN N at 14V isn't right, shame you can't check at the meter (is it sealed you you can't remove the terminal cover?).

I think that we agree that the 14-15V on the N is the real problem. On further investigating, I think that you intuition that it may be in the meter is spot-on. The photo below shows that the power company lines from the pole are split into two lines, one going to my meter and the other to my neighbor's meter. When I cut the power at my knife switch, it essentially isolated the meter and lines to the switch. I think that the lines themselves being the problem are remote, and the problem lies in the meter. As mentioned, I still showed 12+V N at my knife switch, while my neighbor shows 0V at the N in their CU.

 

I do not feel comfortable poking around in the meter but I have just about convinced my wife to call someone who knows what they are doing to take a look at it. I will let you know the results. Thanks again.

split power lines.jpg

Posted

It seems to me that you have a highs resistance path to the mains voltage (220V)  This would give a slight shock that your wife has experienced, but show a low voltage on your probe.  If you could measure with a high input impedance meter, you might get a different, higher voltage reading.   I had this with my toaster, which gave a mild shock when the metalwork was touched.  I got a 50 VAC reading on my meter.  Final diagnosis was that there was leakage in mins wire.  Getting  proper earth to the toaster metal work cure this without any wiring catching fire.

never expect anything to be logical in Thailand, and never ever trust anyone else's wiring.

If you earth the suspect 'live' part, do you get any indication that it has a voltage on it?  ( spark to blown fuse,)  If not is must be a high resistance path to the live, like a leakage in the wiring.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...