Electrical installation of Hitachi WM-P400GX


Recommended Posts

Posted (edited)
External (exposed but OK) location of pump. Appliance cable is 1.5 sq mm 2 core and a separate earth lead ( damn! separate issue.)


What power supply cable size should I run to the power outlet for the pump?

Suggested rating of combination CB and safety cut (combined)?


Approx 12 metres from supply board. Will be dedicated circuit.


Edited by mayview
Posted

Run it as a regular outlet, 2.5mm2 on a 20A breaker.

Use a 20A/30mA RCBO if you're likely to be plugging garden tools into the outlet at any time.

  • 2 weeks later...
Posted (edited)

Thank you for the information. The supply is good!

Of course changing the pump cable myself invalidates the warranty but think that safety is a higher consideration. Contacted the pump manufacturer and they refused to give details stating that Thai Standards don't allow for a three lead cable of 1.5 sq mm wires, two core cable is OK they refused information on the process of replacing the cable stating it was against their policy to give out manual's procedures. The access is hidden under the pump itself. I finally contacted the retailer (bigpump)for instructions and K. Piya was most supportive and made contact with the Thai distributor.

The engineers from the distributor factory arrived within 24 hours and replaced the cable onsite, free of charge, with a Thai molded cable and standard 3 pin plug with 3 x 1.5 sq mm leads all round, EU colour coding. The warranty remains valid.

Edited by mayview

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



ร—
ร—
  • Create New...