Posted

From a long time ago from back home I know RCCBs - residual-current circuit breaker.

I know in Germany they use the so called FI (Fehlerstromschutzschalter) over there with 30mA.

They are installed in the breaker box and the 30mA is a good value to protect and safe life.

 

But how about Thailand?

First, it seems they are not really common here, at least there are lots of breaker boxes without them.

And when I searched in Thai online shops the RCCBs are difficult to find at all (maybe they use another name). And then they use 100mA or even 300mA which, as far as I know, is not a good protection.

 

Here is one which I found with 30mA but I never heard of the brand "CHINT"

NL1-2-40-30AC | CHINT 2 Pole Type AC RCCB, 40A NL1, 30mA | RS Components (rs-online.com)

 

What do you know about RCCBs in Thailand? Do you use them? Which brand?

And are they all the same with the same specs or are there big differences?

 

P.S.: I just found some on Lazada from ABB - I hope the real thing.

 

This is a sample picture

beca1ed840d82262e9e58c1b137f52db

 

 

 

 

Posted

Agree with @Crossy

There is an abundance of RCBO's out there and I have only ever seen either 30ma or the adjustable, up to 30ma, ones.

There are also plenty of individual circuit RCBO devices which can fit in place of an MCB. Not cheap but a very useful idea.

  • Like 1
Posted
Just now, Will B Good said:

Had these fitted just yesterday.........are these okay....the right thing?

 

Looks good to me ???? 

 

Not a manufacturer I'm aware of but if everything feels solid you're good to go.

 

  • Thanks 1
Posted
Just now, Crossy said:

 

Looks good to me ???? 

 

Not a manufacturer I'm aware of but if everything feels solid you're good to go.

 

Thanks......I wonder.....would it be a good idea to find an independent qualified electrician to check everything out?......or can you rely on the PEA to do a class job?

Posted
3 minutes ago, Will B Good said:

Thanks......I wonder.....would it be a good idea to find an independent qualified electrician to check everything out?......or can you rely on the PEA to do a class job?

 

Post a photo with the lid off (care please). We can gleen a lot of idea about the sparks from simply looking. We've used moonlighting PEA chaps in the past with no issues but you really never know.

 

As to finding a qualified / licenced sparks for domestic ...

 

  • Like 1
  • Thanks 1
Posted

As @Crossy said RCCBs/RCBOs are widely available, every big store and electrical supply shop has them, they have been a required fitting to all new supplies for about a decade possibly more. The most advertised brand is Safe-T-Cut, they are also available as a standalone unit for things like AC units and showers 81505A73-B0F5-4948-B3DC-5086890741E6.jpeg.8efbf72664ac0bbf9b8d3639fb3f1c15.jpegB49B62C0-6D3B-4168-9F3C-59FE0FE605A4.thumb.jpeg.709970ccd9777d9efc16fa50f204f498.jpeg

  • Like 2
Posted
14 minutes ago, Will B Good said:

Thanks......I wonder.....would it be a good idea to find an independent qualified electrician to check everything out?......or can you rely on the PEA to do a class job?

You know, if you were to complete your profile with your location it will help in recommending local assistance.

 

I know an excellent, qualified electrician (this is a rare thing here) in my area. He will work further south in Isann if the job is big enough with his team, locally and north for smaller jobs.FC57B3AE-B7AC-4BFD-B63B-6124AF4D63C4.thumb.jpeg.36aadded8b7de9d01c540d6159ddb78d.jpeg

  • Like 1
Posted
15 minutes ago, sometimewoodworker said:

they have been a required fitting to all new supplies for about a decade possibly more.

My house was built 8 years back by a KKN, all MCB.

They also managed to build the house with the incoming live and neutral reversed.

So not required by the PEA in Chiang Mai.

Posted
12 minutes ago, sometimewoodworker said:

You know, if you were to complete your profile with your location it will help in recommending local assistance.

 

I know an excellent, qualified electrician (this is a rare thing here) in my area. He will work further south in Isann if the job is big enough with his team, locally and north for smaller jobs.FC57B3AE-B7AC-4BFD-B63B-6124AF4D63C4.thumb.jpeg.36aadded8b7de9d01c540d6159ddb78d.jpeg

Soz......not sure I have ever looked at my profile???.........Nong Bua Daeng.....Chaiyaphum.

  • Like 1
Posted
12 minutes ago, Will B Good said:

Soz......not sure I have ever looked at my profile???.........Nong Bua Daeng.....Chaiyaphum.

Just look under your profile picture in a computer browser.  If you have filled in the information it will always be there.

.9EAC7DEF-9BA8-4425-9606-28FD608143C1.jpeg.fcb6e57a9f594aac5e9357546c1a833a.jpeg

 

if you haven’t, it won’t.

CDE2875D-BB3A-4483-89BC-D3ABC6A5C94F.jpeg.5dbabc782a48a9ab02ab4732c8d679f3.jpeg

 

I certainly don’t bother looking up 99.9% of members profiles, but the location given on every post is helpful.

  • Thanks 1
Posted
25 minutes ago, BritManToo said:

My house was built 8 years back by a KKN, all MCB.

They also managed to build the house with the incoming live and neutral reversed.

So not required by the PEA in Chiang Mai.

It was required by the PEA at that time, just your local area didn’t follow the requirements. AFIR it came in in the early teen’s 

Posted
24 minutes ago, Will B Good said:

Soz......not sure I have ever looked at my profile???.........Nong Bua Daeng.....Chaiyaphum.

Reed will work in your area if you can’t find a local real electrician, he does charge for travel time and he is not cheap, but then he actually understands what he is doing and has all the equipment that could be required and more.

 

PM me if needed.

  • Like 1
  • Thanks 1
Posted
55 minutes ago, Crossy said:

@OneMoreFarang where are you seeing 100 and 300mA units?

 

They are useful in certain circumstances to provide discrimination but I've not seen them here.

 

Here are 100mA

RCCBs | RS Components (rs-online.com)

I saw 300mA but I don't remember where.

 

The problem with me is that I learned about these things in Germany, obviously with the German names. I can translate them but it seems often there are other words in use compared what I see in the translation.

 

Now I found a supplier with loads of those things.

อุปกรณ์ไฟฟ้า เบรกเกอร์ แมกเนติก สายไฟ ปลั๊ก สวิทซ์ โคมไฟ หลอดไฟ ท่อร้ายสายไฟ รางเดินสายไฟ ทามเมอร์ รีเลย์ หางปลา อุปกรณ์ประกอบตู้คอนโทรล - Sirichai Electric

 

Thanks

 

  • Like 2
Posted
On 4/8/2022 at 8:56 AM, Muhendis said:

Eventually. Yes.

Unfortunately I must respectfully disagree with this. You cannot even rely on the PEA to get things right. I'll post something to illustrate. Recently my sister in law asked me to rewire her house, so I obliged. Within minutes of doing some basic checks, I found the following gross errors. The house has a 3-phase supply. The PEA marked the individual cables to discern the three phases and the neutral, which is good. Unfortunately they marked them incorrectly. The only reason this was missed for years and didn't kill anyone was because the house is all hardwood, was wired as TT and had no ground rod. . . See my video. . .

 

 

 

I also noted this abandoned cable. It's the type used by the PEA to connect meters, so this was from the previous single phase meter, now removed. . . why you should always gives power poles a wide berth. . .

 

 

signal-2022-04-09-164205.thumb.jpeg.d2ed6149192b13f455b8493cc090fe57.jpeg

 

 

 

 

So no, you can't rely on the PEA to do things right. Not by a long, long way.

 

About the topic, I will only use Siemens or ABB residual current devices. I have had many Schneider devices fail. I'm interested to see where you're finding 100+ milliamp devices, hopefully with time delay, I need some of these but haven't found any supplier yet.

  • Like 2
Posted
16 minutes ago, Led Lolly Yellow Lolly said:

About the topic, I will only use Siemens or ABB residual current devices. I have had many Schneider devices fail. I'm interested to see where you're finding 100+ milliamp devices, hopefully with time delay, I need some of these but haven't found any supplier yet.

Here are some 100mA RCCB - but not from ABB or Siemens

RCCBs | RS Components (rs-online.com)

 

I just looked at the ABB supplier from my link above. They have many many devices, all 30mA...

  • 2 weeks later...
Posted
On 4/8/2022 at 7:47 AM, Crossy said:

RCDs (just earth leakage) and RCBOs (earth leakage with over-current) are readily available in all the big-box DIY places (HomePro, Global, ThaiWatsadu etc. etc.), usually 30mA but 10mA are available.

By now I looked a little more about what is available and what it cost.

I found i.e. this ABB supplied on Lazada and they seems to have "everything"

https://www.lazada.co.th/acb-official-store/

 

I am still confused about RCCBs and RCBOs. In theory I understand what they are doing and the difference. But what I don't understand until now is when to use an RCCB with MCBs and when to use RCBOs. Is there a clear rule or recommendations, etc.? Thanks

 

Posted
12 hours ago, OneMoreFarang said:

But what I don't understand until now is when to use an RCCB with MCBs and when to use RCBOs. Is there a clear rule or recommendations, etc.? Thanks

Not sure about "rules" but generally RCBO is used as the main breaker for whole house (all circuit) RCD protection.  Individual circuits can also use RCBO but I suppose if there is room in the CU, an RCCB could be used along with existing MCB.

Posted
4 hours ago, bankruatsteve said:

Not sure about "rules" but generally RCBO is used as the main breaker for whole house (all circuit) RCD protection.  Individual circuits can also use RCBO but I suppose if there is room in the CU, an RCCB could be used along with existing MCB.

New kid on the block is:-

https://shopee.co.th/Abb-RCBO-10A-DSN201-AC-C10-0.03-2CSR255050R1104-i.639623820.11092945035?sp_atk=74712aca-f86c-44e8-a5b0-d04e7a4f6bbf

These are ridiculously expensive but they combine MCB and RCD into the same size as an MCB and would be useful if whole house protection is not required but individual circuits are (as in the case of you still want lighting when it trips) . I don't know if there are any big enough for an electric shower etc.

Posted
5 minutes ago, Muhendis said:

New kid on the block is:-

New?  I have a Schneider box with single pole RCBO for over 12 years and pretty sure available long before that.

Posted
35 minutes ago, Muhendis said:

New kid on the block is:-

https://shopee.co.th/Abb-RCBO-10A-DSN201-AC-C10-0.03-2CSR255050R1104-i.639623820.11092945035?sp_atk=74712aca-f86c-44e8-a5b0-d04e7a4f6bbf

These are ridiculously expensive but they combine MCB and RCD into the same size as an MCB and would be useful if whole house protection is not required but individual circuits are (as in the case of you still want lighting when it trips) . I don't know if there are any big enough for an electric shower etc.

 

Some RCBOs

 

40A, N interrupted

https://www.lazada.co.th/products/abb-ds201-c40-ac30-2csr255040r1404-miniature-circuit-breaker-with-overload-protection-rcbo-type-ac-1pn-40a-6ka-30ma-240v-i2956828793-s10840598433.html

 

32A N not interrupted

https://www.lazada.co.th/products/abb-miniature-circuit-breaker-with-overload-protection-rcbo-type-ac-1p-32a-10ka-30ma-240v-dse201mc32ac30-2csr275051r1324-i3072681441-s11274180970.html

 

Posted
On 4/8/2022 at 5:06 AM, sometimewoodworker said:

 

 

......I know an excellent, qualified electrician (this is a rare thing here) in my area. He will work further south in Isann if the job is big enough with his team, locally and north for smaller jobs......

This is good to know.  We are in Kut Chap.  I will flag this to contact you in future when the time comes.  Thanks!

Posted
1 hour ago, bankruatsteve said:

New?  I have a Schneider box with single pole RCBO for over 12 years and pretty sure available long before that.

New to me ☹️

I could have done with some of these (non Schnieder) about five years ago.

Posted

I spent some time on various websites and YouTube and this is what I learned.

For the record: I helped with electrical installations a long time ago with a professional company but I don't have any certificate and I am not up to date.

Having said that let me know if you know better than the following:

a) having a RCD, RCCB is a lot better than having just a main switch.

b) having one RCCB and a couple of MCBs might work but there is a problem with possible too much leakage 

c) like b but having two RCCBs with each a couple of MCBs is better but depending on the size of the installation there might still be too much leakage 

d) the alternative is using RCBOs instead of MCBs. So i.e. 8 RCBOs instead of 8 MCBs. That is the best protection. It is more expensive but at the end of the day maybe 10k THB wisely spent.

e) See d) with Type A instead of Type AC RCBOs is best.

 

All this, and more, is more or less explained in the following videos. Both together they are almost an hour long. For anybody who likes to know how to do things right I think it's a good investment of your time.

 

 

 

 

 

  • Sad 1

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...